There are a few issues this brings up with using nitrogen on a wet system.
As far as I am aware, the maximum maintenance pressure for nitrogen generators 
(provided you’re using a generator and not a nitrogen cylinder) is around 80 
psi.
Purging the system of oxygen is typically done by a remote purge valve, left 
open for up to 1 month, or an automated purge valve.  These valves do not purge 
when water is located at this purge valve.
So you have two possibilities to inert the system.

  *   Leave the system down (not automatic) in nature for up to 1 month to 
purge the oxygen?
  *   Are you using a nitrogen cylinder to fill the system with nitrogen prior 
to introducing water?
There may be a way to install a dry system to keep the system automatic, set it 
up, and when purged turn it to a wet system but this seems overly complicated.
Jamie Seidl NICET SET #107472
Century Fire Protection<http://www.centuryfp.com/> | General Manager
3600 Woodpark Blvd. Suite G Charlotte, NC 28206
____________________________________________________________________
p  704 888 3473 |  m  704 650 0033

From: Tim Easter <[email protected]>
Sent: Tuesday, October 29, 2024 6:22 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Help with nitrogen pressure

External Email: ONLY open links/attachments from known safe sources
If a wet pipe system is inerted with nitrogen what does nitrogen pressure need 
to be?
Thanks