I have a situation that's unique to me and am looking for some guidance.

I have a 7-story building.  The first level contains a parking garage with a 
demand of 635 GPM @ 61 PSI.  The municipal supply can meet this demand.

The 7th floor has a remote area with a demand of 285 GPM @ 66 PSI, which the 
municipal supply cannot meet.

NFPA 20 says to size a fire pump to meet the greatest demand.  If I can meet 
the level 1 demand without a pump, why would I need to size a fire pump for it? 
 There would be a drastic size reduction if I only had to meet the 7th floor 
demand.

I have reached out to a couple other people, and they have all said I need to 
size the pump to the garage demand, I am just curious as to why.

If the contractor were to tee the underground and bring up a second supply for 
the first floor only would that be acceptable to then not use a pump?  Maybe 
there is something I'm not considering or thinking of since this is new to me.

Any advice, comments welcome, thank you.