Yes sir. Saw that and thank you.

So reading that, as long as a 4" main serves an ajacent 4" main, I am in 
compliance. "?"

I was just curios, if we ARE to add the additional loading, then size would not 
matter.

Wondering why the commitee would not just have added wording like, "The brace 
can serve as the other as long as the combined loads are good." Worded a bit 
btter of course.. 🙂

If we follow the hard line and ignore the annex, then.. ?

Thanks again for guiding me these many times!

R/
Matt




Matthew J. Willis, C.E.T.

Ferguson Fire Design, LLC

D: (602) 337-0721<(602)%20337-0721> C: (307) 236-8249<(307)%20236-8249>

[email protected]<mailto:[email protected]>



________________________________
From: Ken Wagoner <[email protected]>
Sent: Tuesday, December 24, 2024 12:18 PM
To: [email protected] 
<[email protected]>
Subject: [Sprinklerforum] Re: To add or not to Add That is the question

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
Matthew,

I looked back into the 2016 edition of the handbook where it discusses the use 
of a lateral brace within 24" of a change in direction to serve as a 
longitudinal brace, and found the following just below §9.3.5.5.8:
Where a lateral brace also acts as a longitudinal brace, care must be given to 
address the combined total
seismic load from both lateral and longitudinal pipe being braced. The lateral 
braces on smaller diameter
mains should not be expected to serve as longitudinal bracing for adjacent 
mains of larger diameter. This
could create too much load on the smaller diameter sway brace assembly
And there is relatively identical text below §9.3.5.6.2 regarding longitudinal 
bracing:
Where a longitudinal brace also acts as a lateral brace, care must be given to 
address the combined total
seismic load from both longitudinal and lateral pipe being braced. As in 
9.3.5.5.8, the longitudinal brace
should be on a pipe of equal or greater size than the pipe being braced 
laterally. A longitudinal brace on
a smaller diameter main should not be expected to serve as lateral brace for an 
adjacent main of larger
diameter. This arrangement could create too much load on a smaller diameter 
sway brace assembly.
As I am a member of the hanging and bracing committee of NFPA 13, please see 
the disclaimer below.

sincerely,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.parsleyconsulting.com%2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1>

IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued 
pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of 
the author and does not necessarily represent the official position of the NFPA 
or its Technical Committees. In addition, this correspondence is neither 
intended, nor should it be relied upon, to provide professional consultation or 
services. It should be noted that the above is my opinion as a member of the 
NFPA Automatic Sprinkler System Hanging and Bracing Committee and the Hanging 
and Bracing for Fire Suppression Systems Committee in accordance with the NFPA 
Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the NFPA or its 
Committees
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to