According to NFPA 13, CPVC pipe and fittings can be used in certain situations, 
but there are limitations. For light-hazard occupancies, CPVC is generally 
allowed. However, in ordinary-hazard rooms within light-hazard occupancies, 
CPVC pipe can be installed if the room doesn't exceed 400 square feet.

Key Considerations for Using CPVC in NFPA 13 Systems:

  *   Room Size Limitation: CPVC pipe can be installed in ordinary-hazard rooms 
up to 400 square feet.
  *   Installation Requirements: CPVC pipe and fittings must be installed 
according to the manufacturer's instructions and listing.
  *   Concealed vs. Exposed: CPVC pipe can be installed concealed or exposed, 
but exposed installations have specific requirements, such as maximum sprinkler 
spacing.
  *   Private Garages: In private garages within dwelling units not exceeding 
1,000 square feet, CPVC pipe can be protected from the garage compartment by 
wall or ceiling sheathing required by the applicable building code ¹ ².

Additional Requirements:

  *   Verify the CPVC product is listed for fire sprinkler service and specific 
use within the system.
  *   Ensure the manufacturer confirms the product's suitability for the 
intended application.
  *   Follow the manufacturer's installation guide for specific requirements on 
spacing, distance from ceiling, and sprinkler temperature.

Regards,
Yasser Amer

From: Ed Kramer <[email protected]>
Sent: Wednesday, May 14, 2025 12:30 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] CPVC and pipe scheduled systems


! External Email, Use Caution !

Oh knowledgeable ones:  Is there anything in NFPA 13 that prohibits the use of 
CPVC pipe/fittings in the remodel of an old pipe schedule system?  The intent 
is to maintain the pipe schedule and not provide calculations.  I'm not aware 
of anything, but I don't want this to bite me later.

Thanks,
Ed K

[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]

[cid:[email protected]]


Ed Kramer
Design Manager | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
M:   785.766.4894
A:   1383 W. North Street  Salina, KS  67401



________________________________



Confidentiality & Disclaimer Note: This e-mail (including any attachments) 
contain protected and confidential information intended for the sole use of the 
individual or organization addressee. If you are not the addressee or an 
authorized agent acting on their behalf, or if you have received this message 
by error, please notify the sender immediately be returning the message. It 
must not be copied, distributed or used in any other way but should be 
immediately deleted from your system.

While Dar and the Dar Group strive to maintain high standards of communication, 
reliability, authenticity and integrity, neither shall be liable for the 
improper or incomplete transmission of the information contained in this 
communication nor for any delay in its receipt or damage to your system. 
Neither Dar nor the Dar Group guarantees that the integrity of this 
communication has been maintained or that this communication is free of 
viruses, interceptions or interference.

Confidentiality & Disclaimer Note: This e-mail (including any attachments) 
contain protected and confidential information intended for the sole use of the 
individual or organization addressee. If you are not the addressee or an 
authorized agent acting on their behalf, or if you have received this message 
by error, please notify the sender immediately be returning the message. It 
must not be copied, distributed or used in any other way but should be 
immediately deleted from your system. While Dar and the Dar Group strive to 
maintain high standards of communication, reliability, authenticity and 
integrity, neither shall be liable for the improper or incomplete transmission 
of the information contained in this communication nor for any delay in its 
receipt or damage to your system. Neither Dar nor the Dar Group guarantees that 
the integrity of this communication has been maintained or that this 
communication is free of viruses, interceptions or interference.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to