Craig, The FD will need to truck in water for hose, plus there is a nearby 
river they can draft from.   
  

  
This is a very difficult site as there is a lot of ledge and they want the 
tanks underground. They are trying to avoid having to blast. There area other 
issues, but would take too long to describe.
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Sep 23, 2025 at 10:18 AM,  <Craig Prahl (mailto:[email protected])>  
> wrote:
>   
>   
>         
>   
>
> One question, if there is no public water supply, what will the fire 
> department use for firefighting?    Will they truck it in?   
>
>   
>
>   
>
>   
>
> Are these concrete tanks above ground?    What is the reason for this 
> arrangement in lieu of one single tank?   
>
>   
>
>   
>
>   
>
>   
>
>   
>
>  Craig Prahl    |Jacobs     | Fire Protection SME – EV, AM, DC, Special 
> Hazards
>
>   
>
>  [email protected] (mailto:[email protected])|www.jacobs.com 
> (https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$)
>
>   
>
> 1041 East Butler Road      Greenville, South Carolina    29606     
>
>   
>
> CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>
> From:   Fpdcdesign  <[email protected]>
>   Sent:  Tuesday, September 23, 2025 7:45 AM
>   To:  Sprinklerforum  <[email protected]>
>   Subject:  [EXTERNAL] [Sprinklerforum] Multiple tank pump suction
>
>   
>   
>
>   
>
>   
>   
>
> I have a client that is building a retail store in an area with no public 
> water supply. Sprinkler water will be supplied by pump and tank. My estimate 
> is for 20000 gallons. The client want to use 4 - 5500 gallon concrete tanks 
> connected in series. 
>
>   
>   
>   
>
>
>
>   
>   
>   
>
> I have a client that is building a retail store in an area with no public 
> water supply. Sprinkler water will be supplied by pump and tank. My estimate 
> is for 20000 gallons. The client want to use 4 - 5500 gallon concrete tanks 
> connected in series. My question is what size connections between the tanks 
> will be required? NFPA 22 doesn’t address this (that I found). An old copy of 
> the Hydraulic Institute Standards I have states that for piping to suction 
> pits, keep the velocity below 2 ft/sec. Would this be a reasonable number?   
>
>   
>   
>
>   
>
>   
>   
>   
>
> Todd G Williams, PE
>
>   
>   
>
> Fire Protection Design/Consulting
>
>   
>   
>   
>
> Stonington, CT
>
>   
>   
>   
>
>  860-535-2080 (tel:860-535-2080)  (ofc)
>
>   
>   
>   
>
>  860-554-7054 (tel:860-554-7054)     (fax)
>
>   
>   
>   
>
>  860-608-4559 (tel:860-608-4559)  (cell)
>
>   
>   
>   
>   
>   
>     
>  NOTICE - This communication may contain confidential and privileged 
> information that is for the sole use of the intended recipient. Any viewing, 
> copying or distribution of, or reliance on this message by unintended 
> recipients is strictly prohibited. If you have received this message in 
> error, please notify us immediately by replying to the message and deleting 
> it from your computer.
>            