Kyle, As I mentioned, there are several issues with this site I didn’t 
mention. One is approximately 1000 ft of 80 year old, severely tuberculated 8” 
main (estimate C=30) that feeds the site. The first thing is that this needs to 
be replaced. Once that is done, the 825 is very possible.
  

  
CW, I have all of that info. I have been working on this since 2021 and it just 
came back to life after a year away. 825 gpm is the sprinkler demand only. 
There is a raw water supply that would be used for hose streams.   
  

  
I hesitate to post many specifics of the project here as what is going on could 
result in litigation.   
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Oct 6, 2025 at 11:26 AM,  <Kyle.Montgomery 
> (mailto:[email protected])>  wrote:
>   
>   
>         
>   
>
> “Neither pump has ever passed its initial test due to the water supply”. So, 
> the water supply can’t even provide 600 GPM to the little pump? If that’s the 
> case, there is no workaround other than adding a water tank. You can 
> commission the pump without reaching 150% of the rated capacity, but you have 
> to at least meet the demand flow and pressure. If you can’t get to 600 GPM, 
> you certainly aren’t getting to 825 GPM.
>
>   
>
>   
>
>   
>
> -Kyle M at Aero
>
>   
>
>   
>
>   
>   
>   
>
> From:   Fpdcdesign  <[email protected]>
>   Sent:  Monday, October 6, 2025 7:24 AM
>   To:  Sprinklerforum  <[email protected]>
>   Subject:  [External][Sprinklerforum] Multiple undersized pumps.
>
>   
>   
>   
>
>   
>
>   
>   
>
> I am working on a project for a facility with several small and medium sized 
> buildings. Only some of the buildings are sprinklered. This location has a 
> plethora of problems but I only have one that i will bring here.   
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> The facility has a very bad water supply and a new building was constructed, 
> complete with fire pump, to meet a demand of 825 gpm. Also on this site is a 
> fire pump house with a 400 gpm at 75 psi pump that takes suction from the 
> main. I was told this pump only feeds a dedicated main to 3 buildings. 
> However, I subsequently found that the pump actually ties into the 
> underground feeding the entire site, including the new building. Now I have a 
> main fed by a pump with a maximum flow of 600 gpm feeding a 750 gpm pump. Is 
> there any way to get this to work? There is no by-pass around the 400 gpm 
> pump. Not sure if that would make a difference. I would appreciate input from 
> those mightier than I.   
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> Neither pump has ever passed its   initial test due to the water supply.
>
>   
>   
>
>   
>
>   
>   
>   
>
> Todd G Williams, PE
>
>   
>   
>
> Fire Protection Design/Consulting
>
>   
>   
>   
>
> Stonington, CT
>
>   
>   
>   
>
> 860-535-2080 (tel:860-535-2080)  (ofc)
>
>   
>   
>   
>
> 860-554-7054 (tel:860-554-7054)     (fax)
>
>   
>   
>   
>
> 860-608-4559 (tel:860-608-4559)  (cell)
>
>   
>   
>   
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     