There are Factory Mutual design schemes as well, but they also stop at 55 feet.

I think that you are going to be stuck with in-rack protection of some sort.

-Kyle M @ Aero

From: Greg Held <[email protected]>
Sent: Thursday, November 27, 2025 12:34 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [External][Sprinklerforum] Re: Design for buildings greater than 50ft

You don't often get email from [email protected]<mailto:[email protected]>. 
Learn why this is important<https://aka.ms/LearnAboutSenderIdentification>
Unfortunately, the ceiling is higher than 55ft

________________________________
From: Brett Peters <[email protected]<mailto:[email protected]>>
Sent: Thursday, November 27, 2025 11:31:18 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Design for buildings greater than 50ft

The Tyco ESFR34 is designed for 50'-0 of storage with maximum ceiling height of 
55'-0 and I think the Reliable M336 is the same

I don't know of any other sprinklers that will go that high or higher. The only 
other protection schemes I am aware of include providing ESFR in rack 
sprinklers (ESFR in racks can be placed with larger height intervals than 
traditional in rack sprinklers)




Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
[email protected]<mailto:[email protected]>
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at 
www.proudline.ca<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.proudline.ca%2f&c=E,1,IIB6fBvb4dpIffFjJBKjmfGYZ5Zf0vgRULiUlKZUyeSjUEtwP4FlolZt7kjDDZAqSFXMho1wOlUTSErKzDWV6dyrLrfqsYJ-5NYcmUgaPQT-&typo=1>


On Thu, Nov 27, 2025 at 12:00 PM Greg Held 
<[email protected]<mailto:[email protected]>> wrote:
I am curious if anyone can direct me on how to design ceiling only protection 
for a building with a roof greater than 50ft.  The building will eventually 
have storage, but there is no information about the racking at this time.  What 
is known is that it will have Class I-IV commodities.

Thank you,


Greg Held

[email protected]<mailto:[email protected]>

Delta Fire, Inc.



[cid:[email protected]]





14795 SW 72nd Avenue

Portland, Oregon 97224

503.620.4020 X 113

www.deltafire.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fna01.safelinks.protection.outlook.com%2f%3furl%3dwww.deltafire.com%26data%3d02%257C01%257Ckathy.marino%2540am.jll.com%257C600ab234ae2d4d2b00c508d678109cba%257Cbfef2b06d2564f8ebd038d3687987063%257C0%257C0%257C636828410093238795%26sdata%3dx1%252BYPL61aI20rvrTQFvlKeMIhihsy6Nl1iA09WKzy%252Bo%253D%26reserved%3d0&c=E,1,rb7C4lGy0hyBGI8mYFNvU2fvf-9s8Ixcp5bxlrEKKBpxoQl_mpaMrDN-rQKKzIxisb640B165slEuNBsxrlk8ocq3KWm7C0AZUlsuHWd2Q,,&typo=1>


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,fNY6OnDcAmTS40jZb5yrvgCJJgzbczzQE5iMOvOr9vO9i1_Rv-Z7CcH0vDjL1cZBqahcB_34qWnM7TPsY0N7FSxJJs46NGOahc6MzP8HLERbJPw,&typo=1>