Brett,

When ever I see something moved in -13, I look to the online NFPA-link for an explanation or other references.  Here's what I found as enhanced data for the '25 edition:

Automobile parking garages were moved from the list in A.4.3.3.2 for ordinary hazard (Group 1) (OH1) to ordinary hazard (Group 2) (OH2) for the 2022 edition. Automobile materials have changed substantially, because parking garages were originally considered OH1. Even though there is gasoline in the automobiles, the loss history for these occupancies demonstrates that fires in standard-type parking garages are typically limited to one car and do not pose an excessive challenge for the sprinkler system to control.

More recent fires in these structures have proven difficult to extinguish in large part due to the materials used in cars. A recent Fire Protection Research Report, Modern Vehicle Hazards in Parking Structures and Vehicle Carriers, reviewed the problems and stated: “The evaluation of modern vehicle fire hazards and current code requirements found that for enclosed parking garages and marine vessels the existing requirement for active protection systems appears adequate to control a vehicle fire until the fire department arrives, based on historical fires and laboratory testing. Open parking structures emerge as the main area of concern regarding fires in modern vehicles.” The findings around enclosed structures, which are the ones that require sprinkler protection, would indicate that the OH1 classification was justified. The committee ultimately decided to make the change to OH2 and noted that further research in this area is needed.

It is important to note that this does not apply to parking garages that use a car stacking system. As indicated in A.4.3.5, parking garages using a car stacking or car lift system with maximum two automobiles high are classified as Extra Hazard Group 2 occupancies. If the number of automobiles stored vertically exceeds two, then such an occupancy classification is outside the scope of NFPA 13. Additional consideration should be given where a larger number of electric cars are stored or where car chargers are present.

Always a good idea to check for the "why" when something moves in -13.

sincerely,

Ken Wagoner, SET
Parsley Consulting
3002 Younger Drive
Harrisonville, Missouri 64701-3909

Phone: (760) 745-6181
Visit the website



On 1/14/2026 9:01 AM, Brett Peters wrote:
I believe that changed in the '22 edition but we are still working on the '19 edition here.
I lot of projects actually specify sprinkler design to be done by the most current code book though



Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca


On Wed, Jan 14, 2026 at 7:58 AM daren welborn <[email protected]> wrote:
Brett,
Its funny you say that because ive been told to use Ordinary Group II for all garages from the engineering plans ive been getting.  Code still says Group I in 2019.

From: Brett Peters <[email protected]>
Sent: Wednesday, January 14, 2026 9:55 AM
To: Jay Google <[email protected]>; Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: EV Charging
 
The only things that I am aware of is that NFPA 13 changed parking garages from OHI to OHII and FM changed from HC2 to HC3



Thanks

Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca


On Wed, Jan 14, 2026 at 7:19 AM Jay Google <[email protected]> wrote:
I heard that in NFPA 13 (2025) there is something about charging stations being designed to EH2, but cannot find it.  Anyone know where it is?

Jay Stough
NICET IV LAYOUT
NICET III ITM

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to