I should have noted the abandoned pipe should be identified as having been
abandoned in place as required by NFPA 1 (the Fire Code) as it appears in
multiple sections, including for gas pipe as well as other types.  I thought
we added this requirement to NFPA 13 or 25 but my quick look didn't show
anything.. Still a best practice.  Thanks Shawn 

 

 <https://link.nfpa.org/publications/1/2015/chapters/66#ID000010012563> 

 <https://link.nfpa.org/publications/1/2015/chapters/66#ID000010012563>
Removal from Service of Piping Systems.

 <https://link.nfpa.org/publications/1/2015/chapters/66#ID000010012563>
Piping systems taken out of service or abandoned shall be temporarily or
permanently closed in accordance with 

 

 

 

 


   <https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1> 


Bob Caputo, CFPS


President


American Fire Sprinkler Association

1410 E Renner Rd., Suite 150

Richardson, TX 75082

c:     760-908-7753


p:

214-349-5965 ext124 


w:

 <http://firesprinkler.org/> firesprinkler.org  

        

 

New Year, New Training!
Learn design, hydraulic calculations, and ITM with AFSA's best-in-class
training! Click here <https://firesprinkler.org/education-training/>  to
learn more and register now for Beginning Design School, Sprinkler
Hydraulics Calculations Course, NFPA 25 Essentials Workshop, and Advanced
Hydraulics Calculations Course.

 

From: Shepherd, Shawn SS <[email protected]> 
Sent: Thursday, February 5, 2026 1:27 PM
To: 'Discussion list on issues relating to automatic fire sprinklers'
<[email protected]>
Subject: [Sprinklerforum] Re: Removing Mechanical water motor bell 

 

I can agree with Bob's perspective, but working for an AHJ of a 175 year old
city, when a capped pipe of sprinkler system that lead to a WMG is found, it
can often lead to a rabbit hole of research on why it was capped.   Happened
to me far more than once.  You don't know who will find the issue or on what
path it will lead.  But often I have found the overall cost the owner to be
more in the end than that upfront cost when the equipment was not completely
removed.  I will add that I would not consider such work to be need of such
a "major" permit.

 

Shawn Shepherd, PE

Fire Protection Engineer

Seattle Fire Department

  _____  

From: [email protected] <[email protected]>
Sent: Thursday, February 5, 2026 11:09 AM
To: 'Discussion list on issues relating to automatic fire sprinklers'
<[email protected]>
Subject: [Sprinklerforum] Re: Removing Mechanical water motor bell 

 

CAUTION: External Email

Don't remove the pipe, just the bell.  Cap the pipe and leave it in place.
Just a thought.

 

 


 


Bob Caputo, CFPS


President


American Fire Sprinkler Association

1410 E Renner Rd., Suite 150

Richardson, TX 75082

c:     760-908-7753


p:

214-349-5965 ext124 


w:

 
<https://protect2.fireeye.com/v1/url?k=31323334-50bba2bf-31321b84-4544474f56
31-007f0811dc0b3c39&q=1&e=482605c8-a915-4e8f-9c95-b52d83d49c72&u=http%3A%2F%
2Ffiresprinkler.org%2F> firesprinkler.org  

        

 

New Year, New Training!
Learn design, hydraulic calculations, and ITM with AFSA's best-in-class
training! Click here
<https://protect2.fireeye.com/v1/url?k=31323334-50bba2bf-31321b84-4544474f56
31-7be89be2169abb42&q=1&e=482605c8-a915-4e8f-9c95-b52d83d49c72&u=https%3A%2F
%2Ffiresprinkler.org%2Feducation-training%2F>  to learn more and register
now for Beginning Design School, Sprinkler Hydraulics Calculations Course,
NFPA 25 Essentials Workshop, and Advanced Hydraulics Calculations Course.

 

From: Brandon Bridgford <[email protected]> 
Sent: Thursday, February 5, 2026 12:19 PM
To: Discussion list on issues relating to automatic fire sprinklers
<[email protected]>
Subject: [Sprinklerforum] Removing Mechanical water motor bell 

 

Good Afternoon,

 

I am trying to remove a mechanical fire sprinkler alarm bell that frequently
plugs up. The facility already has an external horn/strobe in the same
location. The city is requiring a major building permit because it includes
the removal of pipe. Does this sound right? Any thoughts or suggestions?  

  

 

Brandon Bridgford