That is a big skylight. That would be a hard alternate for someone to approve 
and get approval with the AHJ.

How far are the sidewalls down from the top, 4.5-feet?

You could use the obstructed construction rule to get the upright sprinklers 
22-inch down from the peak if this was desired. Better for smaller skylights as 
you could end up with two rows.

Steve Welsh, PE  \  Burns & McDonnell
Senior Fire Protection Engineer
M 410-978-3836

From: Fpdcdesign <[email protected]>
Sent: Friday, February 13, 2026 9:05 AM
To: Sprinklerforum <[email protected]>
Subject: [Sprinklerforum] Sprinklers in skylights.

I am fighting, yet again, old sprinkler in the skylight battle. The skylight is 
about 60 ft long, 12 ft wide and 4.5 ft from the bottom of the skylight opening 
to the peak.

I showed a single line at the peak with uprights. Obviously to GC doesn’t like 
that. They have a plan from a building in another state with sidewalls in a 
soffit several feet down from the peak. This was stamped, approved and 
installed.

Is there any justification (Code, fire test, etc) for the sidewall arrangement? 
 If not, why is this still getting approved? This has been going on for a long 
time.

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559