JD, that k you for the information. When is says “…pressure doesn’t exceed 15 
psi…”, does that mean air pressure, water pressure or both?
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Mar 3, 2026 at 11:32 AM,  <JD Gamble (mailto:[email protected])>  
> wrote:
>   
>   
>           
>   
>   
>
>    Consider a Low Pressure Dry Pipe System
>
>   
>
>   Unlike wet systems, dry pipe systems aren’t prone to freezing because the 
> pipe is not filled with water. Instead, it’s filled with pressurized air or 
> nitrogen that keeps the valve to the water supply closed. When a sprinkler 
> head activates, the air pressure in the system drops, causing the valve to 
> open and releasing water into the pipes to be delivered to the fire sprinkler 
> heads.
>
>   
>
>   Tyco (Johnson Controls) and Viking BlazeMaster pipe is UL listed for use in 
> Light Hazard and Residential dry pipe sprinkler systems where the pressure 
> doesn’t exceed 15 psi and the ambient temperature is above -20ºF (-29ºC). A 
> dry pipe system utilizing BlazeMaster CPVC must be designed to provide 
> pressure relief when the system pressure exceeds 15 psi. Alternatively, the 
> system may be equipped with an alarm that sounds when the pressure exceeds 15 
> psi. Other design and installation parameters are outlined in the 
> manufacturer’s installation guide. A link to Tyco’s is   here 
> (https://docs.johnsoncontrols.com/tycofire/api/khub/documents/Y7NN9_1q7PoIN9081~sZ9Q/content),
>  and Viking’s is   here 
> (https://www.vikinggroupinc.com/sites/default/files/documents/080712.pdf?__hstc=120511383.ac16f0333100f67a732406dc8ddd60c5.1668094726860.1700233678466.1700494728935.153&__hssc=120511383.1.1701212585389&__hsfp=1999393944&hsCtaTracking=b491017c-9540-4865-90).
>    
>
>   
>
>   A key benefit to using BlazeMaster pipe in a low pressure dry system is 
> that BlazeMaster CPVC is naturally resistant to corrosion and 
> microbiologically influenced corrosion (MIC), completely eliminating the 
> corrosion concerns, and the associated maintenance costs, that plague 
> metallic dry systems.
>
>   
>   
>
>   
>
>   
>
> From the BlazeMaster Website
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>   
>
> From:   Patrick Tomaszewski  <[email protected]>
>   Sent:  Tuesday, March 3, 2026 9:28 AM
>   To:  Discussion list on issues relating to automatic fire sprinklers  
> <[email protected]>
>   Subject:  [Sprinklerforum] Re: CPVC in dry system
>
>   
>   
>   
>
>   
>
>   
>
> Never heard of this.
>
>   
>
> Ive only ever seen standards and manufacturers documentation saying that CPVC 
> products are approved for wet systems only.
>
>   
>
>   
>
>   
>
> Maybe instead of telling him no, you can ask client to produce the 
> documentation saying it is acceptable – we can do whatever the client wants 
> as long as it complies with codes, standards, manufacturer’s docs, and AHJ 
> approval.
>
>   
>
>   
>
>   
>
> That way you don’t have to risk being wrong, while maintaining compliance 
> based on your own knowledge.
>
>   
>
>   
>
>   
>   
>   
>   
>   
>   
>
>
>
>   
>   
>   
>
>  Patrick tomaszewski |Estimator
>
>   
>
>   www.valiantfireco.com (http://www.valiantfireco.comorg)   
>
>   
>
>   [email protected]   (mailto:[email protected]%C2%A0)
>
>   
>
>  📍3910 Howe rd. Wayne, MI 48184   
>
>   
>
>  “Every Second Matters.”   
>
>   
>
> IG (https://www.instagram.com/valiantsec.mi/)   •   FB 
> (https://www.facebook.com/valiantsec.mi)   •   LINKED IN 
> (https://www.linkedin.com/company/valiant-security-llc)   
>
>   
>   
>   
>   
>   
>
>   
>
>   
>   
>
>   
>
>   
>   
>   
>
> From:   Fpdcdesign  <[email protected] (mailto:[email protected])>
>   Sent:  Tuesday, March 3, 2026 11:21 AM
>   To:  Sprinklerforum  <[email protected] 
> (mailto:[email protected])>
>   Subject:  [Sprinklerforum] CPVC in dry system
>
>   
>   
>   
>
>   
>
>   
>   
>
> I had a client tell me this morning that there was something about CPVC being 
> approved for residential dry systems where low pressure dry valves were used. 
> I have never heard of it and can’t find any references about it. Before I 
> tell him no, is there something that I am missing?
>
>   
>   
>
>   
>
>   
>   
>   
>
> Todd G Williams, PE
>
>   
>   
>
> Fire Protection Design/Consulting
>
>   
>   
>   
>
> Stonington, CT
>
>   
>   
>   
>
> 860-535-2080 (tel:860-535-2080)  (ofc)
>
>   
>   
>   
>
> 860-554-7054 (tel:860-554-7054)     (fax)
>
>   
>   
>   
>
> 860-608-4559 (tel:860-608-4559)  (cell)
>
>   
>   
>   
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to