Craig, Not sure if this was your question too. "An approved seismic separation assembly shall be installed where sprinkler piping, regardless of size, crosses building seismic separation joints at ground level and above." Normally, you do not need a separation at the building foundation slab as the slab moves with the ground. However as you are going through a building exterior wall, the wall could move differently than the ground. Thus, the extra separation is required.
Notes: There are clearance requirements at the foundation slab. There will also be clearance requirements at the exterior wall. You will some type of flexible weather seal. Steve Welsh, PE \ Burns & McDonnell Senior Fire Protection Engineer M 410-978-3836 From: Mike Watts <[email protected]> Sent: Monday, March 9, 2026 5:52 PM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]> Subject: [Sprinklerforum] Re: Flexible assembly on pump discharge in seismic cat D area https://www.metraflex.com/products/fire-protection-division/?matchtype=e&network=g&device=c&keyword=metraflex%2520fireloop&campaign=1880371110&adgroup=72795587649&matchtype=&network=g&device=m&keyword=&campaign=1879994101&adgroup=67581073182&gad_source=1&gad_campaignid=1879994101&gclid=Cj0KCQjw37nNBhDkARIsAEBGI8NDEzU6QG8GfbpPNfSPMWigac-U8CJvEPSnVW2RWo1KlqAmv4AklogaAifAEALw_wcB Mike Watts RME-G-3218231 Sprinkler Service Manager [Image removed by sender. image] Firetrol Protection Systems, Inc. 4616 W. Howard Lane, Building 7, Suite 700 Austin, Texas 78728 [email protected]<mailto:[email protected]> Office 512-687-0115<tel:+15126870115> Cell 512-660-4411<tel:+15126604411> ________________________________ From: Prahl, Craig <[email protected]> Sent: Tuesday, February 10, 2026 9:28:47 AM To: Sprinklerforum <[email protected]> Subject: [Sprinklerforum] Flexible assembly on pump discharge in seismic cat D area I have a packaged fire pumphouse, discharge exists horizontally through the wall and then turns down to connect to the underground outside of the bldg. The seismic design category SDC) is "D". I am being told by the project ME that we should I have a packaged fire pumphouse, discharge exists horizontally through the wall and then turns down to connect to the underground outside of the bldg. The seismic design category SDC) is "D". I am being told by the project ME that we should have a flexible connection on the discharge side outside the bldg. to accommodate the potential of 8-inches of movement between the pumphouse and underground piping system. I've looked around to try and find such an assembly for 8" pipe suitable for an outdoor installation and so far haven't found such a device. So, my question for those out there in seismically active areas, is this standard practice and who makes such an assembly? Craig Prahl | Jacobs | Fire Protection SME - EV, AM, DC, Special Hazards [email protected]<mailto:[email protected]> | www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$> 1041 East Butler Road Greenville, South Carolina 29606 CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS ________________________________ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]