I agree. I don’t see what information you’re really wanting to get. Considering 
it’s a restricted orifice. There is a process like this that you need to do on 
a deluge. You would choose the Inspector‘s test or the furthest most accessible 
point and get your readings while doing a full flow test. I guess that test 
would be more understandable with the idea that paddle water flow switches 
require a minimum GPM to activate so if you get a waterflow alarm, that's not 
activating this could possibly be a foreseeable way to diagnosed.

Get Outlook for iOS<https://aka.ms/o0ukef>
________________________________
From: Fpdcdesign <[email protected]>
Sent: Wednesday, March 11, 2026 7:34:19 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: inspector test connection

The intent of the ITC is to simulate the flow of one sprinkler in order to test 
the alarm activation. The fire pump has nothing to do with it. There is no 
measuring the flow from it. However, if you colleague is going to pitot an ITC, 
call me. I want to watch.

Todd Williams
Fire Protection Design/Consulting
Stonington, CT
860-608-4559


On Mar 11, 2026 at 5:54 AM, <Teaster1974<mailto:[email protected]>> wrote:


I have a colleague that says must use fire pump rated pressure to determine 
flow from inspector’s test connection. I said its a restricted orifice to 
represent a sprinkler head flowing. Therefore pump pressure is negligible. Who 
is right?

_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To 
unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to