A ceiling cloud obstruction attached to a wall is provided over an entry door 
that
measures 15 ft by 3 ft 11 in. When the measurement is taken from the doorjamb, 
the
distance is 4 ft 1 in. where the AHJ is requiring a sprinkler under the cloud. 
Do
we measure the width of the obstruction from the wall or the door jamb?

We have reviewed 13, 2007 Edition as the applicable standard.  Our informal 
interpretation
is that when architectural features such as windows and doors create additional 
floor area, the distance is measured to the door or window surface.
This issue was clarified in the 2007 Edition in Section 8.5.3.2.4 where it 
states,
"The distance from the wall to the sprinkler shall be measured to the wall when 
sprinklers are spaced near windows and no additional floor space is created." 
Since
the door jamb creates an additional floor space, the distance is measured from 
the
side of the obstruction (ceiling cloud) to the side of the door jamb. Thus an 
additional
sprinkler is required by Section 8.5.5.3.1 since the obstruction width is 
greater
than 4 ft. This is supported by the NFPA 13 Handbook text that states, 
Paragraph 8.5.3.2.4 
applies when the  wall  is represented by a window.

Where the window in the wall is set back from the inside surface of the wall, 
the
distance is measured to the wall, and not to the glass surface of the window 
where
no additional floor area is created by the window. Where additional floor area 
is
created by the window, the distance is measured to the glass surface of the 
window.

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Hydraulic Calculations - Part 3 is Here
Part 3 of the Hydraulic Calculations series on eCampus! This 2-hour interactive 
online course is the third in a series covering the topic of hydraulic 
calculations
for fire sprinkler systems. For more information, click
here 
[http://r20.rs6.net/tn.jsp?llr=gdnaptcab&et=1104125138547&s=13010&e=001-UCENKj7JgewGASLt5f2al2DWeW5U7DIZlZUpF4qYIJysuYEvUy9LX0RHDZkXgpkFLPeglWin2ku_lP5K3j_WcbSaanGJzaxzLuwQq9DkDsDbgwNB4Ry10YuxuvUpBdKtH0t_9jbL3LZrWYhty3k7g==]to
 explore the Fire Sprinkler e-Campus.

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Vice President of Engineering and Technical Services Roland Huggins, 
a PE registered in fire protection engineering; Phill Brown, a NICET IV 
certified 
automatic sprinkler technician and NFPA Certified Fire Protection Specialist 
(CFPS) and Tom Wellen, a degreed fire protection engineering technologist. 
This is provided with the understanding that the AFSA assumes no liability for 
this opinion or actions taken on it and they are not to be considered the 
official position of the NFPA or its technical committees. 

Copyright (c) 2008, American Fire Sprinkler Association, 12750 Merit
Drive, Ste 350, Dallas, TX 75251.   Voice (214) 349-5965 ext 124 or
Fax (214) 276-0908.  All rights reserved.

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Mark Your Calendar!
Changes to NFPA 13
Thursday, Dec. 18, 2008
Phone seminar
For details and/or to register, visit the AFSA
Calendar 
[http://r20.rs6.net/tn.jsp?llr=gdnaptcab&et=1104125138547&s=13010&e=001-UCENKj7JgeWGJ1IqiZ1JsT7iFlnszbk8sFkPT-9llTiB1LDZIH3JzkE9xuMa-IdEs9aEHBzqUPSMMIErfROAsdq_atMT1uj3B5MKk297yoFcuWuKKiwYff_IpeNurS3MBbQeFzqBnCwMSLOc6ozxJySXRDTV-JSqKMnv2n3WGPqaQb5AhLJ91dZzLt50SZnzggPAZLWtRFBw1yvBxP5P7VqjVDL-4Z0c4RV8T_9TZqlJ3KdiwR6nmzFQce08K7aCgtFFnDIuw5p1VrcZ0aV_ipZLItt-M0E].

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~Join
 Our Mailing
List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1104125138547


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&se=001WBC-c5DgHn0%3D&t=001qDzYDBoMm4QLgI7-13CXrQ%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&se=001WBC-c5DgHn0%3D&t=001qDzYDBoMm4QLgI7-13CXrQ%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Email Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to