Comments Sought on Proposed TIAs for NFPA 13R and NFPA 25
NFPA13R, 2013 Edition

Standard for the Installation of Sprinkler Systems in Low-Rise Residential 
Occupancies

TIA Log No.: 1081 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcNSxMZzubEYRsfUVtGPZYIO4-tHJY7oHAiK4cUzECYCzyu5lPRW_ZqleP_TBelKzHREVJpnl7_3OtKfHNmJKgWY0jglcJEI7xr16ezqN4Z25vmCSWXIbUzm1n_yf2IZb7wXUezojl1FcDAuFgg9fy0efJTxuGby8eo=],
Reference: A.1.1, Comment Closing Date: January 25, 2013

The proposed change revises the fourth paragraph by deleting text in A.1.1. This
 text addressed the issue of whether a single building could use both a full 13 
NFPA 13 and a 13R system in different portions of the building. As the deleted 
text
states, the Technical Committee's position was that they couldn't be mixed 
unless
the building is separated and classified as two buildings. In the 2013 cycle, 
there
were multiple proposals and comments to explicitly state that both system types 
could not be used within a single building. See proposals 13R-5 and 6 and 
comments
13R - 5 / 6 / 7 / 51. All were rejected. The committee statements explicitly 
stated
that a single building (either a separated, mixed- occupancy or a 
podium/pedestal
facility) is allowed by the building codes to use a NFPA 13R system in the 
residential
portions of the building and a NFPA 13 system in other portions of the building.
 This was a reversal of the previous position in recognition that for some 
situations,
the building codes do allow using both systems within a single building. The 
problem
is that the previous text was not deleted. Although new text is warranted, it 
seems
that both NFPA 13 and NFPA 13R should address this issue as a coordinated 
effort.
As such, the cleanest approach was simply to delete the identified text.

The TIA can be accessed here 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcNSxMZzubEYRsfUVtGPZYIO4-tHJY7oHAiK4cUzECYCzyu5lPRW_ZqleP_TBelKzHREVJpnl7_3OtKfHNmJKgWY0jglcJEI7xr16ezqN4Z25vmCSWXIbUzm1n_yf2IZb7wXUezojl1FcDAuFgg9fy0efJTxuGby8eo=].

NFPA 25, 2011 Edition

Standard for the Inspection, Testing, and Maintenance of Water-Based Fire 
Protection
Systems

TIA Log No. 1082 
[http://www.nfpa.org/aboutthecodes/AboutTheCodes.asp?DocNum=25],
Reference: 8.3.2, Comment Closing Date: January 25, 2013

Approximately 25,000 pressure transducers used on fire pumps were recently 
recalled
because of failures.  Several thousand of the recalled transducers were used in 
fire pumps.  Pressure transducers that stick or fail with a high-pressure 
reading
can prevent a fire pump from starting when needed.  The transducers may stick or
 fail and prevent the fire pump from responding when needed.  The proposed 
language
intends help identify pressure transducers that have developed abnormalities.  
Controller
modifications that could identify many failures and when they occur were deemed 
to be impracticable.  The proposed changes will not identify transducer failures
 when they occur, but will make it more likely to identify abnormal transducers 
during fire pump testing.

The TIA can be accessed here 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcPHxThWQAn9pNAKkATr-_9W_9nbO5EpsN3aK8BfOCSuji0KPkvQooFMVb_uROvms4w7ms5-GOi0jSK3rmf-GNeqRQAbxx7inkdzhxMtcGWQip2DVaDbaFp8kwEZtyVaFuh_Lm63vo83fl4gh1ysSzwLR2Vrke8GHPk=].

Anyone may submit a comment by the closing date indicated above. To submit a 
comment,
please identify the number of the TIA and forward to the Secretary, Standards 
Council,
1 Batterymarch Park, Quincy, MA 02169-7471.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

The Technical Update dated December 14, 2012 was in error as presented.  I 
failed
to provide some background information regarding this question.  The question 
was
in regard to an existing installation where the inspector found the fire 
department
connection connected to the cross mains on the opposite side of the building 
away
from the riser.  I failed to acknowledge in the Technical Update the base 
requirement
regarding fire department connections connected to a manifold arrangement for 
multiple
systems.  Section 8.17.2.4.3 states, "For multiple systems, the fire department 
connection shall be connected between the supply control valves and the system 
control
valves."   Please replace the incorrect Technical Update with this revised 
version.
 I apologize for any inconvenience this may have caused.
Tom Wellen, AFSA Technical Services
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

FDC Connected to Main Piping

"We have a nursing home with two wet systems. There is a remote FDC on the 
opposite
side building away from the fire sprinkler risers. The FDC piping connects to 
the
end of the mains on the two systems with check valves. Is it an acceptable 
practice
to connect to the end of a main on each of the two systems with check valves 
(one
for each system) to supply the FDC?"

In response to your question we have reviewed NFPA 13, 2010 edition as the 
applicable
standard. Our informal interpretation is that the FDC can connect to the end of 
a main on each of the two systems if approved by the AHJ.

The base requirement of NFPA 13 in Section 8.17.2.4.3 is that for multiple 
systems,
the fire department connection shall be connected between the supply control 
valves
and the system control valves. The arrangement found does not meet the NFPA 13 
standard
and would need AHJ approval. With that said, an exemption to this requirement 
may
have been provided by the local AHJ based on the following information. The fire
 department connection shall be permitted to be connected to main piping on the 
system it serves according to Section 8.17.2.4.1.2. There are times when the 
riser
for the sprinkler system is located remote from the fire department access. As 
such,
this section allows the fire department connection to be located on main piping.
 The handbook commentary under Section 8.17.2.4.2 for single systems indicates 
that
for wet pipe systems, the fire department connection can be connected to any 
portion
of the feed main, not just at the system riser, if using another location makes 
more sense. The commentary does not mention connecting to cross-mains but that 
should
be considered acceptable. The inlet pressure from the responding fire department
 pumper should be 150 psi and the minimum size of the pipe for the FDC is 4 
inches
as indicated by Section 8.17.2.3. A size smaller than 4 inches would not be 
permitted
since the exception in 8.17.2.3(3) applies to a single riser. The standard also 
points out that the fire department connection cannot be attached to branch line
 piping in Section 8.17.2.4.1.1. As for connecting remotely to two systems, this
 would be no different than connecting to two systems at the riser so it also is
 acceptable. This type of arrangement should not be attempted on new 
installations
unless approved by the AHJ.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcM5Mj5MCk2sAMT3xrNYjOh6HxyYCAv2RqfLS_8XKLQ0srNxtkIE8NV1xVddABWwj6bhuG_Ozt2yu-ot6Ka_cv7v0YXBSjZHMMcz1x3mQ3cvFw==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Download the PDF Version of
Technical Update
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcMkF0okqrFDeNG-iteigttisV1TEj9xFfh3yIr3EFXBKP91KkoQzioxokr_2UxMnIrFV4AU4OahKJnCQZbKYpEyk2WO1X7EW4bL_PvPnt7Xm03bDQ_Y2JmVb144DsITnwwnXc8De6Q4BwkugxpU4K53dhAXmJ1o9CCvg8LQG0HKkY9x1K1ApMxYhQZbBSwZRZk=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

TIA 1081 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcNcFIXDXOLAZIGhOdSyzUaOmS0zUDfcYmkZfIQP7NCS924a2yP6Q6n7r6CNtTg84rGd5zHQfyjJVfTw3X8XmDuBCZZWq38LCdQ3tYi9pFH0z01bOL5AT0K2RsHUkbrCPvONkOX01NvR5loq_MW6sMLoCnuyfGrkO-Z1yavlHElIb0b2V-NkhFZVBazavdJV8dA=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

TIA 1082 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcPRLWF-dJDG0NQTGobtQD-cVZzH-_iPCzsV33n9YUZmaK6H8GT1V10U6ELGdjdaYr_wzq4o-2qFfpTJG25NZ1TgHtet4xW0uzkAT0oDgtAu-6OFlaMw4Sbfc7wz5rkNt5lg1v-qMLdbmJJjJge6JXQzCM_BRHhdNgHpr_kj76vdmB4JngshA0VYm7u5Ma-sXG8=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Download the PDF Version of
Technical Update
December 14, 2012
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcPbrf7EjpzU8tLuqgZtVNZLxT1-Cm255MmiRrgDO-eTSTunRZAas8S8LWGysOCEMQNSzbfNDXcXCRDq0C0PHnqAviqqYk4s2RJjqOofICv659jVP8LUCj7Rc0n_RPl5ox4GfgKEk8lCBz6puZpDgLmwzFQv5LguQatyUfEWS0R1PoEw4RBy4DI5F0gvI7J5be4=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
January 14 - 25, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcOcqywY_Bjf8ScdfazbKV4vbUbz_Rhudun1__ALO8bKhr7SXBIHuAIXLNVmgCwbKVMvSU6RanmnMtPxjliiYOc1U9PPCOeoIjDXYXUmZEGtVkfDLjutX-lfEV8kwEor04FArnywmVp0dywVdfWYdF_A6Y268RZMYYyFlb1bXFh9NdmneoW4huVBoegDF6oRP6X8Nb7TBWZYUwLDCx4XheXsm3JRSNJ-laOq3uATmR8AvVa0YgC4FaMQ7o8SW2V7EV_x6wKP2ALJjEhJ6UUzZ6nI].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcM54fJ9gW8UYgzV5U7XNliMJiLU4ZyR9Bf9TqmkCdnuYxgnw-Ip7M6valguhXPAiHmvZvuTj-4hUd_gc7xRjC9Zemea_wBVJLEBZUOCB0CqbmNGWRSNAXV_]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcNa-uwVxziUcbp7536S9ZXmI1GVVoBk5zVtm-qqLrLlHkUHNOsVXGlDDyZrk5XIK12XA198Hoj3djqi_8cv2qNoJtF9TTqyrADAK2q8w1FcLeqi_QkuJF-LhdgIAz6dqzQ-fTCxugccBZTLf6eKe0IOe9qJMGlWyvw=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcPrjUe7o7s525CiGPjwkTWQlPxUXAJzzNnriQ5PvapxjNCI-Pvm5yvckqDxbDHbqDHJdD4rj0q7HBp7vep5aUj51o_DFxSt7CZBSuBKmW8z68u9UkoHZkXFLKp9XTR0F3nC6hXotkKUhwwPTjcFT7e-lrhBBfOcEFo=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcM5Mj5MCk2sAMT3xrNYjOh6HxyYCAv2RqfLS_8XKLQ0srNxtkIE8NV1xVddABWwj6bhuG_Ozt2yu-ot6Ka_cv7v0YXBSjZHMMcz1x3mQ3cvFw==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcOcqywY_Bjf8ScdfazbKV4vbUbz_Rhudun1__ALO8bKhr7SXBIHuAIXLNVmgCwbKVMvSU6RanmnMtPxjliiYOc1U9PPCOeoIjDXYXUmZEGtVkfDLjutX-lfEV8kwEor04FArnywmVp0dywVdfWYdF_A6Y268RZMYYyFlb1bXFh9NdmneoW4huVBoegDF6oRP6X8Nb7TBWZYUwLDCx4XheXsm3JRSNJ-laOq3uATmR8AvVa0YgC4FaMQ7o8SW2V7EV_x6wKP2ALJjEhJ6UUzZ6nI]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcPrBWcFf1h6rypP4uJMsKs7WABZRxl23Po1OVQYGu6nIQ2fpRILl5TTjcq4dK7Bm3OznCquo5YgWR0cvTWXHpwlF1EfG0ixGEBTdf4Bx0TsnjPtPj2w_jO2K0L_S2sVgU87vtPNTWFxOQ==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcNQuDEW4x4o16r0dA6S--jzzkGgGsjzsALl7HDYTLVAxKH-R8hBrEQY5U-rcHweVmolNsjorbfIPvTnHpbY6knj1upX7M5ffQfC3tU8DPUn_tF86_vjuHL3EzNskvakSrqtoRnqpGAJeom653hgdzqu]
National  
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcMbr9JE-MfUqkUI3Dwk1QM7NVhZGI5MeeZC2CD_6B3igS7nL8oaa3QYVfeXPa6EA0vRVFhgSziyHftJzR7bNLYB-HoaVwj4P2F_5D8H2pXLcw==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcMbr9JE-MfUqkUI3Dwk1QM7NVhZGI5MeeZC2CD_6B3igS7nL8oaa3QYVfeXPa6EA0vRVFhgSziyHftJzR7bNLYB-HoaVwj4P2F_5D8H2pXLcw==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcNI6T12-KC8auuHo0wBpPGVJQUbzINIpUfUuKFArlBzf3-Ze9wZL5atHmgCPdHvkChGMZ9v11LexO1N1GC6FocbSZWIYBIxAMqPPqnRnYsG4lIHQB-CS0LyvbwOFKCbmSEXxsI61IwoOP-Z-smhYUi5]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcNKp3ulN4JGUUEv7oZNyJadkkrknoetPXk4RGlN-aMY5Hamzsu1Reczc-PVaqxiLXQKszm_UfIQ8E-aFGkrUlgYBfmxVLvWUJlKaXN8mYZWslKgxXqWFLTQYpmWce64uaU=]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001RYJEllMWpcNS_g5ffrfSSQBv6-Abn1ytb2x5NhTclH2LychF4JRp_wGwoTZk5o6w69gJgJQwTWeiQgDlN6BKv8spMIKgeQIZmGg6G8gEALXpLH7T0qBPVkxrE6TWfsiSH_h1TM3Wr_xMfm_zb4dh0QmmtC4jDdLRTW53Pni398I=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1111924578251


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001D38oCGMDemMgl-ebdaeBtg%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001D38oCGMDemMgl-ebdaeBtg%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to