AFSA Technical Update
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

A newsletter dealing with codes and other technical issues

January 11, 2013
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Sprinkler Penetrating a Fire-rated Membrane

"We have completed the installation of a wet pipe sprinkler system in a nursing 
home. The attic space is wood truss construction and is heated so we have 
installed
a wet pipe system with 200 F quick-response sprinkler. Attached to the bottom of
 the wood trusses is 5/8-inch drywall that forms the ceiling of the occupied 
space.
This ceiling assembly has a 1-hour fire rating. The occupied space is protection
 by 155 F quick-response concealed sprinklers with 135 F cover plates. The fire 
inspector is requiring that the area around the concealed sprinklers where it 
penetrates
the ceiling to be fire caulked to maintain the 1-hour ceiling assembly.  Can you
 clarify this matter?"

In response to your question we have reviewed NFPA 13, 2013 edition as the 
applicable
standard as well as the 2012 editions of the International Building Code (IBC), 
NFPA 5000, and NFPA 101 Life Safety Code (LSC). Our informal interpretation is 
that
NFPA 13 does not address pipe penetrations but the IBC, NFPA 5000, and the LSC 
does
allow penetration of rated partitions.

Section 8.3.5.6.2 of the NFPA 101 LSC lays the foundation by requiring all 
membrane
penetrations be protected by a fire stop system (fire caulking is one such 
system).
There are four scenarios that allow other arrangements to satisfy the 
requirement.
One of the four is when a metal escutcheon plate covers the annular space 
created
by the penetration of a fire sprinkler. Section 8.5.6.4 also states, "Where 
sprinklers
penetrate a single membrane of a fire resistance-rated assembly in buildings 
equipped
throughout with an approved automatic fire sprinkler system, noncombustible 
escutcheon
plates shall be permitted, provided that the space around each sprinkler 
penetration
does not exceed 1/2-inch, measured between the edge of the membrane and the 
sprinkler."The
IBC (Section 714.3.2 exception 5) and NFPA 5000 (Section 8.8.7.1) both have 
similar
wording.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWdeA6Gu7zT46cPKfwCSAVfScTVba9iGH-glBiYjdvWeR61jX9caqfCzVHcTsg4L1urNCZmJ_9vbgq95riLuVLQpN1kHXRL0wwgLuG6-bwnUDQ==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWcxTfOKpWeY3HofwqRSKH_-zgP3iaIHfOznyWdYNWJrJWLA6N4Cs5fJpbiMNsOmMdSyAoXH0vIAI1nkBPrstD2ZcTtHCX6F3P1x0Vd1ekqAySEzJM_epYTYvPV-tH5O4w_dn0vYhLtorvt6RjDMkdRgC_X0Hrqge8u5pnXktAILaR_hoZyf9aA4ectD8uHmvq4=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
February 25 - March 8, 2013

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWcrX5nhAsuR5DKQntSItSMeW1pkNfkRSkxr_RTlIRTEbfn-N_XDOM6ng_Mzf_gC4-neM96p56tFapJrqwaqknrJ7h73eIMBxFQ6fr50tLr7Bhn4KF7R2zr5GRUZT7Jkptec2XsXVC1wkT2g9oP6LaoVxCQk2QIx0RywyICAIHiFHG1aypGSKhODI92gHjcJheS1gqZ4OmB2j29pEd2aOBWJx53_B6cTzeGz35lVcQyKXWKqetJNcLHuP5Honj-DeklsCw7SLhRiPnfFTsbYK0Od].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWcpoNEGNPv4XRmX3dEZtjt_YUX2ZVYsSZ8cNNGAfp0NCHI0drJuE6HVtOB9-vk6-Lph901y4VKucf2Ik7eVYpC_2spMwb-xD2mOFMtVX1v_aCSXYlfNUkyM]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWfznjIazreiJMDPbG-MB6RewaIuEkn2gyGdXngwTmf4e4v88VGTXJ0S9lJqQ2j0SuZ1Deeh2bKoHwk8rNyx53N9sxCseliwzWbX2LaYOSvH6BDvmByoE06-zFR1csovQD7yGXLZPJiKLx0fHneqdnjXMo43popd4o8=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWfH64UKOQokpGS7Q9V7EHTLmHOvCNA1Qp3UPtS7YMa1jHLcLGTnNsjDPqkeafD5NqfSjKP48oOlHd1SQDTFAI4J49-klZYE1Z4pmwT_S8DefgUG9PRtG6q93xFlMHhV8HnQHadA9eQZfKVZjQ0odOwW2wbgkxq-TZo=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWdeA6Gu7zT46cPKfwCSAVfScTVba9iGH-glBiYjdvWeR61jX9caqfCzVHcTsg4L1urNCZmJ_9vbgq95riLuVLQpN1kHXRL0wwgLuG6-bwnUDQ==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWcrX5nhAsuR5DKQntSItSMeW1pkNfkRSkxr_RTlIRTEbfn-N_XDOM6ng_Mzf_gC4-neM96p56tFapJrqwaqknrJ7h73eIMBxFQ6fr50tLr7Bhn4KF7R2zr5GRUZT7Jkptec2XsXVC1wkT2g9oP6LaoVxCQk2QIx0RywyICAIHiFHG1aypGSKhODI92gHjcJheS1gqZ4OmB2j29pEd2aOBWJx53_B6cTzeGz35lVcQyKXWKqetJNcLHuP5Honj-DeklsCw7SLhRiPnfFTsbYK0Od]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWehPKLy2tpMMR_0BJY37PK-nBgGhtR0u1Oa5Mzoze4dOm-vlLK8KtH7iZQIr38UFeAsUUnz7OMnXsDV_OtBLQGeCpVuK0b0i6gHgnTn0VlaDGWIHAfUW7iFTvm8f-fJXpHm6wnJUPvmFQ==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWcyahOkRJ5tf6EGOIedi03FcBMLXQ9Vz5obh6jXNon6wWyvGHT7URhYTxLhJaLaRVjPwG4szQ35iZaJXHyv0wqBRtB210Z_KFZygUON6Fiz_IKWZ4MYMbGjOu4Xwfxinf0Io0yWWvmQTPtdN4MKcvJM]
National  
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWc7jdI4rMPUxT0CQeEDiC7gCwQzq5_CC51gVRJNlFClbGqb_Lbnk-RkDkq70F-oFwhUg2uNL6oY7kbeWaxajPh4Hxecbcv5qKWJd3vAoVgQVA==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWc7jdI4rMPUxT0CQeEDiC7gCwQzq5_CC51gVRJNlFClbGqb_Lbnk-RkDkq70F-oFwhUg2uNL6oY7kbeWaxajPh4Hxecbcv5qKWJd3vAoVgQVA==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWfEtIHMPaFrEigJr4RC54IJ5yFP8WqFf9-WFZTsPVunFq00T8VYYC6cwRNXfSaVFo72mcnwO4YZv--IUS2HbmlYrWldOsInVpJt5CGYB5TaWwfR-EBdOiRukX6izd8okyEqSdc35orvG-u7wH7b48qh]
Technical Services 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWcZ1-RKyD3hoF1W3nqB5obZFvskrWnXoxA_EcqlJPe8Ae-9Fy1h9yqz8hsfOKAR-bhsk2llXZgB6wnErSe3xsVmoILI8Wzr4ZwXdyU-j8wRs7XOTXojFoSa2Dtckv9fXhY=]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWf8vv79i5FCiBtiyqONhokn3PRByVuGoY5IJkG2P0PEL63L5HMV6OpmrDRVBZXsYrBTv7B-SKO--QBmKk8yNnnmIoPu3bJyZAAujtAAj58i9SSlC-GIvrTTmqAy-VurCH3zW46jo2Ztu58Kjgq-NV-39rXW4zRyHJA=]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1112119058460


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=0013F0sOFF_sYH3w_TpRpkTuA%3D%3D&llr=gdnaptcab


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=0013F0sOFF_sYH3w_TpRpkTuA%3D%3D&llr=gdnaptcab


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://firesprinkler.org/mailman/listinfo/sprinklernotes

Reply via email to