American Fire Sprinkler Association [http://www.firesprinkler.org/] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ AFSA Technical Update ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ A newsletter dealing with codes and other technical issues January 11, 2013 ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Sprinkler Penetrating a Fire-rated Membrane "We have completed the installation of a wet pipe sprinkler system in a nursing home. The attic space is wood truss construction and is heated so we have installed a wet pipe system with 200 F quick-response sprinkler. Attached to the bottom of the wood trusses is 5/8-inch drywall that forms the ceiling of the occupied space. This ceiling assembly has a 1-hour fire rating. The occupied space is protection by 155 F quick-response concealed sprinklers with 135 F cover plates. The fire inspector is requiring that the area around the concealed sprinklers where it penetrates the ceiling to be fire caulked to maintain the 1-hour ceiling assembly. Can you clarify this matter?" In response to your question we have reviewed NFPA 13, 2013 edition as the applicable standard as well as the 2012 editions of the International Building Code (IBC), NFPA 5000, and NFPA 101 Life Safety Code (LSC). Our informal interpretation is that NFPA 13 does not address pipe penetrations but the IBC, NFPA 5000, and the LSC does allow penetration of rated partitions. Section 8.3.5.6.2 of the NFPA 101 LSC lays the foundation by requiring all membrane penetrations be protected by a fire stop system (fire caulking is one such system). There are four scenarios that allow other arrangements to satisfy the requirement. One of the four is when a metal escutcheon plate covers the annular space created by the penetration of a fire sprinkler. Section 8.5.6.4 also states, "Where sprinklers penetrate a single membrane of a fire resistance-rated assembly in buildings equipped throughout with an approved automatic fire sprinkler system, noncombustible escutcheon plates shall be permitted, provided that the space around each sprinkler penetration does not exceed 1/2-inch, measured between the edge of the membrane and the sprinkler."The IBC (Section 714.3.2 exception 5) and NFPA 5000 (Section 8.8.7.1) both have similar wording. ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ firesprinkler.org [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWdeA6Gu7zT46cPKfwCSAVfScTVba9iGH-glBiYjdvWeR61jX9caqfCzVHcTsg4L1urNCZmJ_9vbgq95riLuVLQpN1kHXRL0wwgLuG6-bwnUDQ==] Hosted by the American Fire Sprinkler Association ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered in fire protection engineering. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees. Copyright 2012, American Fire Sprinkler Association. All Rights Reserved ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ PDF Version PDF Link [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWcxTfOKpWeY3HofwqRSKH_-zgP3iaIHfOznyWdYNWJrJWLA6N4Cs5fJpbiMNsOmMdSyAoXH0vIAI1nkBPrstD2ZcTtHCX6F3P1x0Vd1ekqAySEzJM_epYTYvPV-tH5O4w_dn0vYhLtorvt6RjDMkdRgC_X0Hrqge8u5pnXktAILaR_hoZyf9aA4ectD8uHmvq4=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Training Calendar AFSA Beginning Fire Sprinkler System Planning School February 25 - March 8, 2013 Check our calendar to view upcoming training. For details and/or to register, visit the AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWcrX5nhAsuR5DKQntSItSMeW1pkNfkRSkxr_RTlIRTEbfn-N_XDOM6ng_Mzf_gC4-neM96p56tFapJrqwaqknrJ7h73eIMBxFQ6fr50tLr7Bhn4KF7R2zr5GRUZT7Jkptec2XsXVC1wkT2g9oP6LaoVxCQk2QIx0RywyICAIHiFHG1aypGSKhODI92gHjcJheS1gqZ4OmB2j29pEd2aOBWJx53_B6cTzeGz35lVcQyKXWKqetJNcLHuP5Honj-DeklsCw7SLhRiPnfFTsbYK0Od]. e-campus_logo [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWcpoNEGNPv4XRmX3dEZtjt_YUX2ZVYsSZ8cNNGAfp0NCHI0drJuE6HVtOB9-vk6-Lph901y4VKucf2Ik7eVYpC_2spMwb-xD2mOFMtVX1v_aCSXYlfNUkyM] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Free Subscription to Sprinkler Age [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWfznjIazreiJMDPbG-MB6RewaIuEkn2gyGdXngwTmf4e4v88VGTXJ0S9lJqQ2j0SuZ1Deeh2bKoHwk8rNyx53N9sxCseliwzWbX2LaYOSvH6BDvmByoE06-zFR1csovQD7yGXLZPJiKLx0fHneqdnjXMo43popd4o8=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Quality Contractor [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWfH64UKOQokpGS7Q9V7EHTLmHOvCNA1Qp3UPtS7YMa1jHLcLGTnNsjDPqkeafD5NqfSjKP48oOlHd1SQDTFAI4J49-klZYE1Z4pmwT_S8DefgUG9PRtG6q93xFlMHhV8HnQHadA9eQZfKVZjQ0odOwW2wbgkxq-TZo=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Quick Links Firesprinkler.org [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWdeA6Gu7zT46cPKfwCSAVfScTVba9iGH-glBiYjdvWeR61jX9caqfCzVHcTsg4L1urNCZmJ_9vbgq95riLuVLQpN1kHXRL0wwgLuG6-bwnUDQ==] AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWcrX5nhAsuR5DKQntSItSMeW1pkNfkRSkxr_RTlIRTEbfn-N_XDOM6ng_Mzf_gC4-neM96p56tFapJrqwaqknrJ7h73eIMBxFQ6fr50tLr7Bhn4KF7R2zr5GRUZT7Jkptec2XsXVC1wkT2g9oP6LaoVxCQk2QIx0RywyICAIHiFHG1aypGSKhODI92gHjcJheS1gqZ4OmB2j29pEd2aOBWJx53_B6cTzeGz35lVcQyKXWKqetJNcLHuP5Honj-DeklsCw7SLhRiPnfFTsbYK0Od] Buyer's Guide [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWehPKLy2tpMMR_0BJY37PK-nBgGhtR0u1Oa5Mzoze4dOm-vlLK8KtH7iZQIr38UFeAsUUnz7OMnXsDV_OtBLQGeCpVuK0b0i6gHgnTn0VlaDGWIHAfUW7iFTvm8f-fJXpHm6wnJUPvmFQ==] Join AFSA Video [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWcyahOkRJ5tf6EGOIedi03FcBMLXQ9Vz5obh6jXNon6wWyvGHT7URhYTxLhJaLaRVjPwG4szQ35iZaJXHyv0wqBRtB210Z_KFZygUON6Fiz_IKWZ4MYMbGjOu4Xwfxinf0Io0yWWvmQTPtdN4MKcvJM] National [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWc7jdI4rMPUxT0CQeEDiC7gCwQzq5_CC51gVRJNlFClbGqb_Lbnk-RkDkq70F-oFwhUg2uNL6oY7kbeWaxajPh4Hxecbcv5qKWJd3vAoVgQVA==] Scholarship Contest [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWc7jdI4rMPUxT0CQeEDiC7gCwQzq5_CC51gVRJNlFClbGqb_Lbnk-RkDkq70F-oFwhUg2uNL6oY7kbeWaxajPh4Hxecbcv5qKWJd3vAoVgQVA==] OSHA Alliance [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWfEtIHMPaFrEigJr4RC54IJ5yFP8WqFf9-WFZTsPVunFq00T8VYYC6cwRNXfSaVFo72mcnwO4YZv--IUS2HbmlYrWldOsInVpJt5CGYB5TaWwfR-EBdOiRukX6izd8okyEqSdc35orvG-u7wH7b48qh] Technical Services [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWcZ1-RKyD3hoF1W3nqB5obZFvskrWnXoxA_EcqlJPe8Ae-9Fy1h9yqz8hsfOKAR-bhsk2llXZgB6wnErSe3xsVmoILI8Wzr4ZwXdyU-j8wRs7XOTXojFoSa2Dtckv9fXhY=] Informal Interpretation Request Form [http://r20.rs6.net/tn.jsp?e=001gUrxftnBvWf8vv79i5FCiBtiyqONhokn3PRByVuGoY5IJkG2P0PEL63L5HMV6OpmrDRVBZXsYrBTv7B-SKO--QBmKk8yNnnmIoPu3bJyZAAujtAAj58i9SSlC-GIvrTTmqAy-VurCH3zW46jo2Ztu58Kjgq-NV-39rXW4zRyHJA=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Join Our Mailing List [http://visitor.constantcontact.com/email.jsp?m=1102312387686] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Forward email http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1112119058460 This email was sent to [email protected] by [email protected]. Update Profile/Email Address http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=0013F0sOFF_sYH3w_TpRpkTuA%3D%3D&llr=gdnaptcab Instant removal with SafeUnsubscribe(TM) http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=0013F0sOFF_sYH3w_TpRpkTuA%3D%3D&llr=gdnaptcab Privacy Policy: http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp Online Marketing by Constant Contact(R) www.constantcontact.com American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | TX | 75251 _______________________________________________ Sprinklernotes mailing list [email protected] http://firesprinkler.org/mailman/listinfo/sprinklernotes