AFSA Technical Update ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ A newsletter dealing with codes and other technical issues October 11, 2013 ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ NFPA 25 Inspection, Test and Maintenance (ITM) Frequencies The 2014 edition of NFPA 25 provided new material on ITM task frequencies. The new material defines a minimum and maximum time range of when the task is required to be completed. The new text is similar to NFPA 72 to define an acceptable range of the time for the required task frequency. 3.7 ITM Task Frequencies. 3.7.1* Frequency. Minimum and maximum time between events. A.3.7.1 Frequency. The frequencies in NFPA 25 are intended to establish an optimal time between tasks that are required by this document. When scheduling conflicts or other conditions do not allow the tasks to be performed on a strict calendar schedule, it is important that the required task frequencies be identified and complied with according to the variances described in the frequency definitions. When the required task frequencies have not been followed, it should be noted on the inspection report, the task should be performed, and the task frequencies should be followed for all future tasks. The variances should not be used to "skip" tasks or to perform fewer tasks than called for in this document. 3.7.1.1 Daily Frequency. Occurring every day. 3.7.1.2 Weekly Frequency. Occurring once per calendar week. 3.7.1.3 Monthly Frequency. Occurring once per calendar month. 3.7.1.4 Quarterly Frequency. Occurring four times per year with a minimum of 2 months and a maximum of 4 months. 3.7.1.5 Semiannual Frequency. Occurring twice per year with a minimum of 4 months and a maximum of 8 months. 3.7.1.6 Annual Frequency. Occurring once per year with a minimum of 9 months and a maximum of 15 months. 3.7.1.7 Three Years Frequency. Occurring once every 36 months with a minimum of 30 months and a maximum of 40 months. 3.7.1.8 Five Years Frequency. Occurring once every 60 months with 3.7.1.8 Five Years Frequency. Occurring once every 60 months with a minimum of 54 months and a maximum of 66 months. ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ NFPA Document Revisions Below is a partial list of documents under revision. NFPA Documents currently accepting public input: NFPA 14 [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88Alt7TaIx1n-9TWzaPuOI2BOvcHpCC70OSzdAsMz1EizjzibAFWvFqDQv_g0fYit7DrS7EySJ8kZ0o2m2HNPCJyngRDJCZL69Gph_A6URFr0A==] Standard for the Installation of Standpipe and Hose Systems NFPA 15 [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88D0hND1EyTPsg-W0TYJFgkoHHSs8TdykOfNrUPj2s1M2GCMAKrg39rIPtCMa7lItTgi1vHd4aEBVMqq6kHhwVHFE6dr9WdQO4YCnOu8FfeWSA==] Standard for Water Spray Fixed Systems for Fire Protection NFPA 214 [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88DGnoPuKhMINE2-NZ-XDAyJ24qqmddHya9msfPMaTRmPEA8anLil69JpJnIa6qXQ3_oAcg59v9B6fjHoz8ryzdm3yCTmwLZABHircmJEjkwYQ==] Standard on Water-Cooling Towers NFPA 232 [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88Cod-IUvHmxW9_0oWJmah0AzDNDK8XgQ5sh9yDh8m9YC5Ps2J9fpRMidoZHHdEMA6VXRXrZ6aHrDJzNusYAjcLFly6XQea8fHOYJ8zF2XAWLA==] Standard for the Protection of Records Documents currently accepting public comment: NFPA 11 [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88A2iBiMvs9O07LB3UYctAE5FoybAXfn1A9cPdTHkarauI3SqIKpcM-YR56no2p2K30f8SbyiVyPBAFe7l8oRJL8IBY9tVsucSPBWiD-HliKlg==] Standard for Low-, Medium-, and High-Expansion Foam NFPA 13E [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88DAFnTEdx402U2v2M0GHBqu0oye7cslRcztIOXvuRMs1KM3CsuTLQVmsVPudaBuZlGivfnZ3VZdiS6GVyTGMEwNH6Dvv7QIXbQtOhKIdZaoYQ==] Recommended Practice for Fire Department Operations in Properties Protected by Sprinkler and Standpipe Systems NFPA 16 [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88DNsKCHztpmq9Xw3Hz9kbpi3WbbH6JB2KIS1gbo--xOUK0V78-8OcY6Efdo0sJ81EgX_jo9DRO44uklAGr3NKx_HP9WEJ9rjfGDr4Cs4F8Ahw==] Standard for the Installation of Foam-Water Sprinkler and Foam-Water Spray Systems NFPA 33 [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88D1DIJok1V6JdZehPB6FSIoUoyAvwz7-6EtmtQp82UMmB1ywnVb5QHHlyhKjcXncXLSo9yb5LqFT7FmxvfC-biO5ZKK9-j1LjJ3kUWKqBt06w==] Standard for Spray Application Using Flammable or Combustible Materials NFPA 45 [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88AylSRgI4kwkxb7d7BtJyF8AZB79z15syeYgHM4VPevKgq1E8kVbj6OPZP_Nl1E9SLhOU1w9VT_nXQxWw_EINu80zKpu6sQR1Nsm6LyUgJtPw==] Standard on Fire Protection for Laboratories Using Chemicals Not a member of NFPA? See nfpa.org/freeaccess [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88DxY1PoHNBs8II0usAp6uQWA9naMxpXDbhD0wcwowcwQzibF6cp5L2V-jEZhO4VaPAkW6LI9MTbret3oq7xov2p7nP_F8s8XBviJOxktb4Z0-iaCnFmh0f1] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ firesprinkler.org [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88BW6KXLslmsvip8H_FhIzIczTyL9bZNKvGVmonLvqWEs9tDdAFerL6300xHha6Iw7fLWr-b64cV08IYp2QNKBbzb_kOaFzAm-RvUnBtAgpxT9feoY7b5YNK] Hosted by the American Fire Sprinkler Association ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice President of Engineering and Technical Services Roland Huggins, a PE registered in fire protection engineering; Phill Brown, a NICET IV certified automatic sprinkler technician and NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered in fire protection engineering. This is provided with the understanding that the AFSA assumes no liability for this opinion or actions taken on it and they are not to be considered the official position of the NFPA or its technical committees. Copyright 2012, American Fire Sprinkler Association. All Rights Reserved ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ PDF Version PDF Link [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88AtE5X9YkxFRd743mG8vapOoz0IRvdXeSSdMs_rU9S0KJKOv0wyszaisB9FDrgAP8angqtmWNA5wX-WBsKMlKbdCAs3Q2UXTd97awdUu73SK0mpDE07gb31w2Sjjz-UoYNgzXg5OQhb7D89PY8vlZ8iQ9QkVw7JHg7EvISlW8UL-rVI9y9uihgmhYeSa1IwSUvOUjITW0-M7g==] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Training Calendar AFSA Beginning Fire Sprinkler System Planning School Oct. 28 - Nov. 8, 2013 Check our calendar to view upcoming training. For details and/or to register, visit the AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88AyF84YKSaqiv0KOxedNJb51dll3twzwHfvZqjmQOaockbcC8SHUrBmzVFTfe9jUDTNaO1SvLJKPXvadFt3a49plNI1L-JS11_FmT6Jo7zEojrcaNntqbKW_KnAFkRm759osnF0BhiF7ml4PmTPl4FrHqwHAzkhHj5hjD6Tr5_gh60NhyaIeWaEgUdieevAsLlJ6Z4iopqFXC6L3frf7NXRTVMo6himYz8yngWkRROM-kOhlWNSS0MxZ5eMDeqtpIPyr03qO1x_-UOGqURD9Wc6]. e-campus_logo [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88Bj8LZz9XfSOj-UoTVQuFILTKVynlFkTxAi1Qd81vZaOkn5zP-b6O26DtH_V2cf-9w1HBJTv0Rmaaw5ZiOZSxYvcBiQo_KmufLsyXLyaINi8xStghbYrHzR] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Webinar NFPA 20 2013 Update Nov. 20, 2013 11 am - 12:30 pm Central Time $15 fee for 1.5 CPDs or 0.15 CEUs Non-members $140 Register at Webinars [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88BqiDUE1aNdxBL5xXqRPR9JyN62fOffa29Kh6e47AE8JCVk6IyOAc9_ECrfbFV6wdrBEGYo0DbXlsT_bjPOTvosP2t310W5fLyiu634i5dZzqBBZVRSxfID__NhEeMmFwwTiFnV5GP6qeN9rPttz76eMqzvwQIBBMw=] Check our calendar to view upcoming training. For details and/or to register, visit the AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88AyF84YKSaqiv0KOxedNJb51dll3twzwHfvZqjmQOaockbcC8SHUrBmzVFTfe9jUDTNaO1SvLJKPXvadFt3a49plNI1L-JS11_FmT6Jo7zEojrcaNntqbKW_KnAFkRm759osnF0BhiF7ml4PmTPl4FrHqwHAzkhHj5hjD6Tr5_gh60NhyaIeWaEgUdieevAsLlJ6Z4iopqFXC6L3frf7NXRTVMo6himYz8yngWkRROM-kOhlWNSS0MxZ5eMDeqtpIPyr03qO1x_-UOGqURD9Wc6]. ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Free Subscription to Sprinkler Age [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88BELRmpQT5uKjDHS7p5JvyCugC6WFT0acQrxP8hzgW09RIFcivyfiEwiFcxdVH05f0QhWj3Lqb4e_iY8711K9PIMkjxYnbf_H1IV8pvxlRt0s-NrhD5oBtsJa9iEM4wfBoSykPZGblAoyUKSlRFnHdV4iwL8qimJt4=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Quality Contractor [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88DyUYRpk7Q38EHlZh9E87pQ0qRESNCP5f2FH8jBZYvp001M9YbV6zhUkHd6RHyAWE8fma901RXnR0WS0LKR2cBKIHQlUBajwD3S3fb_ldv3zXVAUw16IHouf3cbhG2g7Gu6Xc7mCzuiDCOWfQDZ-MVOEygb9PCo1Mo=] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Quick Links Firesprinkler.org [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88BW6KXLslmsvip8H_FhIzIczTyL9bZNKvGVmonLvqWEs9tDdAFerL6300xHha6Iw7fLWr-b64cV08IYp2QNKBbzb_kOaFzAm-RvUnBtAgpxT9feoY7b5YNK] AFSA Calendar [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88AyF84YKSaqiv0KOxedNJb51dll3twzwHfvZqjmQOaockbcC8SHUrBmzVFTfe9jUDTNaO1SvLJKPXvadFt3a49plNI1L-JS11_FmT6Jo7zEojrcaNntqbKW_KnAFkRm759osnF0BhiF7ml4PmTPl4FrHqwHAzkhHj5hjD6Tr5_gh60NhyaIeWaEgUdieevAsLlJ6Z4iopqFXC6L3frf7NXRTVMo6himYz8yngWkRROM-kOhlWNSS0MxZ5eMDeqtpIPyr03qO1x_-UOGqURD9Wc6] Buyer's Guide [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88ATGLRuMksWLXC7GsJZPn6CLv0zEspFqWy5q_GRP6RvCBrFkOpVg-fh5FXztc3jYJT7DxgI4l4ww6-t_A7Hujhu-VfCJGV62qBylmDIvwM53OV0SnmJshmpdyMt8NhKjoCzwqoPcogjO9IkEGt7z3Ec] Join AFSA Video [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88BA07cgAg22bubo-rvOcd-7QgTHsQhDY_IOTK3dV9QGSnDFjVUSB8SphVIW-QvZe3sgaoSzs_sac_jDiCarMUqDMZ_zA7bWOK4QVwOW_wycBjxRe0z23r1cmKdpa_JLbdV2Y2CPEZ3C9EiZ1_YA9uHXCCAyoRmuKs0=] National [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88A5Vag8hAsJ_QsP_HIlCsYChukTFMDOETUfM6w8gD_8uPVzqbrRIjD3K9nmUoK7xfPdl5Kjj5C2sathJbpL0BDkCCdz4ZcaOMEIO7kvFX7IWizLo3sNU-SN] Scholarship Contest [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88A5Vag8hAsJ_QsP_HIlCsYChukTFMDOETUfM6w8gD_8uPVzqbrRIjD3K9nmUoK7xfPdl5Kjj5C2sathJbpL0BDkCCdz4ZcaOMEIO7kvFX7IWizLo3sNU-SN] OSHA Alliance [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88D3Cwl6wsKcZqx9GAGBmWjqm2dkqd2onA9Jfjtw4SFDw2-LVAJ3WE_y2hW9WE3szW6wMwvkZQ48FXeEcU-fPkPjRbUShTOVpuqcGaGJyEXp70PPJENDK77PZFQQnUbjXeZKPhMnBz_4oVwnjJ3paTZa] Technical Services [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88DzxNLfLqu2UkcIkPJnEtRKeVCbx3agPgOkv8gT0Lu8cL4RQ3focSd6mQnqlSy7KwMKtidYnocWIslCbAQ7LumVO159MpYmARjO1JJfVoZSHt_tVxFbOSSOYIc_bcEizBxUDSxR69kV1w==] Informal Interpretation Request Form [http://r20.rs6.net/tn.jsp?e=001nTV7OLev88DRhHNJ2HpO8gObKDzUjWrkOj0PGP7VeVZ0tWazXolOejJymrJKmxOBtfvi13EwR1wybx-0GuNrqwQwT25QGR8EGGeA7EE99xJC2F5NeCkXq3-xhCYzOxUiUP5hF7aFy-Z2x1oOMYSOqcN53WStJ-4tlJkWY3tDN58cm8ETZDbLdg==] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Join Our Mailing List [http://visitor.constantcontact.com/email.jsp?m=1102312387686] ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ Forward email http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1115243395816 This email was sent to [email protected] by [email protected]. Update Profile/Email Address http://visitor.constantcontact.com/do?p=oo&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001f_YWuQLZHuRNPJwXWOVajg%3D%3D&llr=gdnaptcab Instant removal with SafeUnsubscribe(TM) http://visitor.constantcontact.com/do?p=un&mse=001bAhAGGXw8y_kvRx4AvcwfUNM_21h39IjcFrSc-92BSk%3D&t=001f_YWuQLZHuRNPJwXWOVajg%3D%3D&llr=gdnaptcab Privacy Policy: http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp Online Marketing by Constant Contact(R) www.constantcontact.com American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | TX | 75251 _______________________________________________ Sprinklernotes mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org