Holes in Wood Joists as Piping Supports
The NFPA 13 standard does allow for holes through solid structural members to
serve
as hangers for the support of system piping in Section 9.1.1.6.3. The spacing of
the supports has to meet spacing and support of Section 9.2.2.1. The location
and
size of the holes permitted are according to applicable building codes.
The International Building Code (IBC) addresses this for solid wood joists in
Section
2308.8.2. Holes bored in joists shall not be within 2 inches of the top or
bottom
of the joist, and the diameter of any such hole shall not exceed one-third the
depth
of the joist. Notches in the top or bottom of joists shall not exceed one-sixth
the depth and shall not be located in the middle third of the span.
The notching and boring allowances that are permitted for solid sawn joist
framing
cannot be applied to engineered wood products. Section 2308.8.2.1 indicates that
cuts, notches and holes bored in engineered wood products such as trusses,
structural
composite lumber, structural glue-laminated members or I-joists are not
permitted.
Exceptions are where permitted by the manufacturer's recommendations or where
the
effects of such alterations are specifically considered in the design of the
member
by a registered design professional. Each manufacturer typically publishes
guidelines
to establish safe notching and boring limitations.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHMVa-7vQWdvPeza-EF3za9LpSsgpuKMsgaRsZ-Vl0OiC1gcd9ZFVIZxVPKQvxKseBMg9_jO3DvZnZKeLGEXE4jwVyEHcWoj76VwTOky5f0jOal9Whik9XLsgo8eAy1WaXg==&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
in fire protection engineering. This is provided with the understanding that
the
AFSA assumes no liability for this opinion or actions taken on it and they are
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2012, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
PDF Version
PDF Link
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHMZeNSXCqOb5Qrpptb05gllvBtR0l5zU2naAED2v8LDOgwaMU2xXJeIgtfbMTq8PkVU59VIO6NBitfd0EOMDRZ5r7EgplGImXnHQr9bOc3sMu5xVrpmVFMsVOeTKwQpDMrL-r0XOB0kGbczczNgsNpeEK_TQsUMUY-s6pBh14mjHC4ZxqBhH6X_XLCSP-PeLG_3WWjLu5CHFCUbELMb0jDU=&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Register for
July 14 - 25, 2014
Check our calendar to view upcoming training.
For details and/or to register, visit the AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHAfdaBzFHgqIDfXS5cmvXDqZiKtgg7CqNnfzQZ6sTRPCVPLSbcDPRfyu4PzAE8B0JEMQqMXf-MWjGKV0Y4zsBTVLDzXqwakUv7f47FSxQrINaiNt-mp83AfH-W6XCACsQM4gPnwpeR08WiPyXzotV4muJoHyaXMX_4_qt43HSs-WuEungEujJK9R5UIwwu74mF-nzN3qUNPXSpKDpG99AhXfUaf8slEV_45lIpE54hSGYeareiUbqyrpMlTPTGLTdu35N6yqQgLtbtSM5RGOnoOofi7-5qFObw==&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==].
e-campus_logo
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHM0kNc31ZAqsKsOFwzKHsMjFwNTQGrfuZlOnRNyy6H4wsK388OOKqnEvT6yMB362PzlPjQ-qee68zmMW_a8tr_SMIkKm-6iq68xDkj5thBokZLYuuJMpW8xchYx7MdZaMw==&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Free Subscription to Sprinkler Age
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHA7avTePlgwwztbaEApzLQ3OqUMdqfBLRgdXtw_YW1sq9DLFp2-lpIbWTBaZinT6dS7OvassUxF_Va-nvp3WxrUQOZLhvP9L-wy7a6YTTYmqhYJ9Rk965nEAW6cYFjsdmJ3B16doy1Sp5r2G5Snxsu8WczvOWbXCc0iMcOrtQ6ls&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quality Contractor
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHOzP3psCyygxcNrqqrjE6XF7EBlvVksmtcktf-YvbcIrcefF76u5_MTfL07H02DgCqZdvBg3Y0Juh694yGcQYEcJ9zdtLK4LzIQrSbKs5_n6tp2G_MNYqmsBZbzz3KkSA0qKy0Q-_DxlqdXiJEPRmS0x8n2oppRErOWZqG7PGEvr&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Quick Links
Firesprinkler.org
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHMVa-7vQWdvPeza-EF3za9LpSsgpuKMsgaRsZ-Vl0OiC1gcd9ZFVIZxVPKQvxKseBMg9_jO3DvZnZKeLGEXE4jwVyEHcWoj76VwTOky5f0jOal9Whik9XLsgo8eAy1WaXg==&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
AFSA Calendar
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHAfdaBzFHgqIDfXS5cmvXDqZiKtgg7CqNnfzQZ6sTRPCVPLSbcDPRfyu4PzAE8B0JEMQqMXf-MWjGKV0Y4zsBTVLDzXqwakUv7f47FSxQrINaiNt-mp83AfH-W6XCACsQM4gPnwpeR08WiPyXzotV4muJoHyaXMX_4_qt43HSs-WuEungEujJK9R5UIwwu74mF-nzN3qUNPXSpKDpG99AhXfUaf8slEV_45lIpE54hSGYeareiUbqyrpMlTPTGLTdu35N6yqQgLtbtSM5RGOnoOofi7-5qFObw==&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
Buyer's Guide
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHMVa-7vQWdvPFAJQ38LzsTZsfzYS3nyCRfPTea5jzBqxZByaQcr1JjF2m80cYZL2WBFMpJtjqASNroHKXkeIRTPpo8OL5-dDQTVYJedOugH3q6BTVD61Dflum9YMq_LUv2mFiuzSnuJS1hfmLbqgEQ0kJPQM_ZGxLg==&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
Join AFSA Video
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHMVa-7vQWdvPAlPnTdhAFnfqnWLE1JnzVL4y0NHDmUZ4hLtqSQK1ERmPM0EKfHGcz3D8QA2hPnQqL9ejHcBQoatFzAIE-6FRtGWN6jn3pUAMC58BNxY9DOSfVsp3MC90rbpKnIq2UdqFJYv7Z0YdeKeM1hszOVhAKA==&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
National
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHCavVAUibGEsv0XLcvbwPA-g8QxXBK9343WGp1bhjrovTalOQUuvogWrLd1z6k4krk0ZBle7Pv47R7OfCaUJnd9BukT-xPvsn1IlCSmQ8LdIyvczbbYk8DNgSClktlGl3w==&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
Scholarship Contest
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHCavVAUibGEsv0XLcvbwPA-g8QxXBK9343WGp1bhjrovTalOQUuvogWrLd1z6k4krk0ZBle7Pv47R7OfCaUJnd9BukT-xPvsn1IlCSmQ8LdIyvczbbYk8DNgSClktlGl3w==&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
OSHA Alliance
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHMVa-7vQWdvP29hCgW0DYk0bLLcdrIVwYkdyK_BWBXXvhiLAIyyTC5OQ85dVT4PMBv9cqCxPohj3FChHse5ERdEXBFsEmSjyEh1F07EIqK7gG3sqx05Hwd8jAQiKqDPfRqxDik4CjKEQ3IMTLb5LUnloBYVk7fbg4Q==&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
Technical Services
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHI2nzsxQX1NkDRuea8tAd2jpqxFWJbm-T6OcUO6VbATvzQJP0AaJiQMtI3cb80cb_4xOtgr-V67aFbEC7GImykN4wN8_gY04jkFAWvDOxQ9RhQiVNgbXu8wd-tnxhyQE3mW4mTd17hFE&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
Informal Interpretation Request Form
[http://r20.rs6.net/tn.jsp?f=001-g3gFeOG5iPGxXeRKaf5dsQSgw9FovWOAtYMMw9RzpdNSOMdxapIHNw1MtmP7kOayM2jZFAyyjzORtHBKrD6HIyvUVB7t1u6VTcsyFhcnaQPCSzbTIOgwMLM6ej9j0Tx7qMRaAgo-gvndWVzoV0HDnItycbWnnXzdNv8IsmBPAbFtRkwWaAMHSw0LT1gpqqhD6o375mu14P78YY_2q60N1wknO1kgQ3a&c=o3A2vej1LlpuN0cEvU8uQnlAzpiNAZJH-6yk5fn2GlqQWQHFCEWesQ==&ch=VP5mVaNedUX5bECfBbDli5rQt-PU-Tg6zBoRhbGkZ1GFmGDIDh0BHQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Join Our Mailing List
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1116558383787
This email was sent to [email protected] by
[email protected].
Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=0229c230-354a-11e3-852c-d4ae527b8c41&ca=f699cf07-a124-47f4-9d38-e36dd890b2bf
Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=0229c230-354a-11e3-852c-d4ae527b8c41&ca=f699cf07-a124-47f4-9d38-e36dd890b2bf
Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp
Online Marketing by
Constant Contact(R)
www.constantcontact.com
American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas |
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org