Sprinklers Inside of Equipment

We are involved with a company that makes large modular computer facilities 
where
we install the sprinkler systems in the factory.  They will ship the units to 
customers
around the country.  A large air-handling unit is approximately 15 ft x 15 ft 
and
the height is from floor to ceiling.  It has doors on it for servicing but the 
only
combustibles inside are filters.  The AHJ thinks it is a combustible concealed 
space
with doors and wants it protected.  Is this required?

We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal 
interpretation is that sprinklers within the air-handling unit are not required.

This issue is specifically addressed in the 2013 edition in Section 8.1.1(8)*. 
This
section indicates that sprinklers shall not be required to be installed within 
electrical
equipment, mechanical equipment, or air handling units not intended for 
occupancy.
The annex for this section also says that equipment having access for routine 
maintenance
should not be considered as intended for occupancy.

The Handbook provides additional commentary on this subject. This states, "It is
 not the intent of 8.1.1(8) to require sprinklers to be installed in air 
handling
units (AHUs) or in similar mechanical or electrical equipment. AHUs for large 
buildings
and building complexes can be so large that it brings into question whether or 
not
sprinklers should be installed inside them. Providing sprinkler protection in 
these
units is not practical and would not be overly effective based on the limited 
hazard
present.

AHUs that have access panels or "man doors" are not necessarily intended for 
occupancy
and should not be treated as such when applying these requirements. Often the 
presence
of an access hatch or other means to allow for equipment maintenance is 
misconstrued
as allowing occupancy of such a space."
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk3CUPY6VzKB44Ni9C7bqA0BrCfPiOqfjm0ng2JJ4vR871NFDeLXmvaAr0S3Uw2LceX4PjjYOUg8JzCNgEYO7Ty45HvPEXM8jC0DPl0J6Yiv9zUGZxNVlAlnPdp-m0y8Ctw==&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2014, American Fire Sprinkler Association.
All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqkxULnjUlOiqbAR-3TSVoyPjTVUqIiK7CycZhJVWPuLNDrTAL7gtB9zedU5PTWMbp-TeuAb7dOPkuMi3dQCHjBYrfhm7yWrhFJ1cZA6orduKi4SMK3xopjCdQ4SLb0eHsyAQzMNffu17igUVkE3qdzqujoFY5X_RdA86cqqgR25IinHyPfKhxpPnoXKs8vePYrLnmv2bmnEoQgA8BmdWgJVw=&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

AFSA Webinar
by

Josh Tihen

"Corrosion Inhibition of Dry and Preaction Fire Suppression Systems Using 
Nitrogen
Gas"

Wednesday

April 9, 2014

Free to AFSA members!

11:00 a.m. - 12:30 p.m. Central Time

1.5-hours
Register Button 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk1kK7xqcCTmjWiSQj8u1hgHPNAMigHX9Qg9LSAMMLHESpJuSkttUYMnUHoR68MhcrU7ylG_iQjC_eeP4WfVfhz7C7HYGpQX8e8CY3jxLUJwaYdWJmbFqE0BqteqVcZo5arctBIRdwGyl7DEd7bLLZHvUoz827Tz-AHnin37tlldh&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
Register for
July 14 - 25, 2014

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk7Ru1qAq_MmH0dWdpsNPiJ_TOBGybW0CbgjO-plpwHPNVO6FEV7yrMBcG31BDwBil2PGCddeim-YD3zwEs0KFvPA-96tw0pUvXLpsCx84Y1W3fd0KKh8wehNCBo5Guxnhlf7fVZyS8fQ3Egbg2AsEs7n-WmV7HrJjo5n60rAExf6ui3PS3YRrz9i1ZzzFnvknFLgi_P9yDUhylIHqD3V5nEDFu6JU_FTp651_f3vYoh4eH1e3m9D800XVVvySbcbokttRnLZryTinjglmKtEpJMIybVIZs9dJQ==&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk1vXA-dvG3KVGFJex8KgzO9waNh7vAxqie0hg8oQQ_teo6tK8gAcwgkDlT6hWPLHu3TYAm7M2nq83jXWCRTu-uT7B097uNMzesszFWxPYrhVLQSN0PTBSy4gkObqa4SUjQ==&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk2AsFN5NuUrxsONgLGPYdGSnB5oGOHtWp72rv1KW3jC6QMoYspZN0SZCM3ESNXIaCZzDmLNP3PWYkDOzE3SBEQg_gp2Njn6tgONHRfz7Kf5m5w6Ng7UYzTYlar5xCpHqIXmQXtAqk31KBJv8b6YkW8Ks6eDc3jS8tzBa2eXd65az&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk2oN9oIYJzwpdBf-Pq3ki1Qqi6F_e0U3MCkpDJGmc4sHXmhBpIcgwLd_cXr9eZXeBhxMXNYKKbYADL7YnAXSIT-926eYkpd4ediUdFUe5zeTR10aqbVFUa0bBiNyKJBKb2LiJZCun7sbc8qdreqxBYBJDeeBkCHtdHkYfTXIvG2t&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk3CUPY6VzKB44Ni9C7bqA0BrCfPiOqfjm0ng2JJ4vR871NFDeLXmvaAr0S3Uw2LceX4PjjYOUg8JzCNgEYO7Ty45HvPEXM8jC0DPl0J6Yiv9zUGZxNVlAlnPdp-m0y8Ctw==&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
AFSA Calendar 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk7Ru1qAq_MmH0dWdpsNPiJ_TOBGybW0CbgjO-plpwHPNVO6FEV7yrMBcG31BDwBil2PGCddeim-YD3zwEs0KFvPA-96tw0pUvXLpsCx84Y1W3fd0KKh8wehNCBo5Guxnhlf7fVZyS8fQ3Egbg2AsEs7n-WmV7HrJjo5n60rAExf6ui3PS3YRrz9i1ZzzFnvknFLgi_P9yDUhylIHqD3V5nEDFu6JU_FTp651_f3vYoh4eH1e3m9D800XVVvySbcbokttRnLZryTinjglmKtEpJMIybVIZs9dJQ==&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
Buyer's Guide 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk3CUPY6VzKB4ztX21eHO7LA_H22cxqcPPua8LXxMhLj4aVZ2m4qjTOD8Mnxflo2tBYO4e5-VGdrJ68xQE_lq7DfJOjioYAqxzEsWBiOsuz-WFGDyyHfOan6aRb-JiAaqZ4G_okVYZP7VYPGmTBwSMXeAzSn7GRt34w==&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
Join AFSA Video 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk3CUPY6VzKB4i8JnH1WEvQ94Wno7F8XO_puGKrUdLkz9nShRXBSPQ03Jatk_yiZu68co1pbzEKByeIWAaYNFE_7xaj2rV5_lcliISx4KmVuJlhDs7sXZOZ6-KLA66zx64EzMwiCv_7t9H32IK3Siq8qKMZLyh-BjFg==&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
National  
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk01kVJWuKzdS2g2mzcboUwUlqjQytH5bV3fkg8yJeJFW2Wp7sJdOM987FhURqoMMhDfLCjfX6JoV93bwmWhn799Brb1XhBtb4lpgXb5PtAHVDu6U8wB1-8ncAuRvA1QigQ==&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk01kVJWuKzdS2g2mzcboUwUlqjQytH5bV3fkg8yJeJFW2Wp7sJdOM987FhURqoMMhDfLCjfX6JoV93bwmWhn799Brb1XhBtb4lpgXb5PtAHVDu6U8wB1-8ncAuRvA1QigQ==&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
OSHA Alliance 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk3CUPY6VzKB4QWAM67948c-NekHwvh-6DEQkJ9mWKV9P3XNFWXm6Ggw6KVoc9dAkTbWwhIw3ZhRawWsdRxEn4BjSXfQYtXlSidVhLtJ_DRaoNfwrg9ZOnTVlwCvPAYdJ2MptM5yjIUjUW9K5-868LHsUEm3x_DVxYA==&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
Technical Services 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqk7ryrse3MFMJ_y79fmk8AqR_sOn0kMR78aWDgyZQimhAj7fnbT6EpCM47c2rKE53hI2Huk-9UjXOqic5-aUHz5zyPTE3hyBdmbGxObU5hbAJA_drV_DLIK1m5ES63ypWA2Lr2AJqsBCY&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
Informal Interpretation Request Form 
[http://r20.rs6.net/tn.jsp?f=001zyDb7srZld-H9cEVggRcbB6xkkBA-TS9UWm3HTwev1Q7ibPb2KBqkxPfdszFxPHg631WauMfS83P7DMPU4mnGxaTXmuCXNsc94Eipa6oYwfq_sR30aauokb7jBocizd8br65mXp_6brK_DMCV0ANQ1pjEmwbbgsmHwjItVXOwyltcFP7bQ4tLO4907unWDA_Rmiw4WPPNPAJEf-fWFGuX9_bDXIp_-Ua&c=52qiZrLBeMJov1xa6mDQsiQH4ImhqmW_HHYEMTXRfCSnIbm3BJ4r7g==&ch=XiZOzs2SUyuBF0xawqH9lDUEDpWj54b9qj8AAiX44JaufAzKunqipQ==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Join Our Mailing List 
[http://visitor.constantcontact.com/email.jsp?m=1102312387686]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]&a=1116680487589


This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=0229c230-354a-11e3-852c-d4ae527b8c41&ca=4394ec7c-07f9-4f77-a03a-4897105d10ce


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=0229c230-354a-11e3-852c-d4ae527b8c41&ca=4394ec7c-07f9-4f77-a03a-4897105d10ce


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp


Online Marketing by
Constant Contact(R)
www.constantcontact.com


American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to