Walls Terminate Less Than 18 in. Below the Deflector

"I am designing a sprinkler system for a self storage building that has been 
specified
as an ordinary hazard Group 1 classification.  There are rooms that are only 16 
sq. ft. (4 ft x 4 ft).  They have walls that are 8 ft above the finished floor 
and
1-1/2 in. wide.  The deck is 9 ft - 3 in. above the finished floor.  The 
sprinkler
deflector will be approximately 15 in. above the top of the wall.  Table 
8.6.5.2.2
indicates it can only be used for light hazard situations.  Can the table be 
used
for ordinary hazard applications?"

We have reviewed NFPA 13, 2013 edition as the applicable standard. Our informal 
interpretation is Table 8.6.5.2.2 cannot be used.

Table 8.6.5.2.2 allows sprinkler to be installed above the 18-inch plane below 
the
sprinkler deflector. This allows a greater degree of shadowing (water not 
reaching
a portion of the floor) so it is limited to the less demanding fire presented by
 the light hazard classification. With other classifications, you have to place 
the sprinkler such that water is adequately discharged on both sides of the wall
 obstruction. There are two means to achieve adequate floor coverage.  One means
 is to place sprinklers on both sides of the obstructing wall. With such closely
 spaced walls this approach can be excessively conservative.  Another means is 
to
follow the obstruction rules for sprinkler located above solid structural 
members
(such as the bottom chord of a joist or a beam).  These structural members can 
be
up to 8 inches wide (over 4 times wider than the wall) and presents the same 
impact
on the discharge pattern as created by the top of your wall. As dictated by 
Section
8.6.5.2.1.7, the sprinkler must be located directly over the top of the wall and
 the deflector must be at least 6 inches over the top of the wall.  This way 
adequate
water is discharged to both sides of the wall.
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

NFPA 25 Open for Public Comments

The first draft report for the next edition of NFPA 25, Standard for the 
Inspection,
Testing, and Maintenance of Water-Based Fire Protection Systems, is open for 
public
comments.

Public Comment Closing Date for Online Submission: 5/15/2015

Public Comment Closing Date for Paper Submittal: 4/10/2015

http://www.nfpa.org/25 [http://www.nfpa.org/25]

2017 edition:

Posted under Next Edition tab:
First Draft Report - open for public comment 
[http://r20.rs6.net/tn.jsp?f=001s_3ms41jD28sktTRW1NCcsUpkgd_gebNBRW6wJqb3dVQJCtPKBywDUWugjs6-PCAG0sq79_2Glo-lCenZA1pFRc6VdRt8j_fn1t27fdkiPmYlMOHvM5N_5snvWZmiuc3ERD100AIS4PE1ox6m2xCl17FJ6gp3QiuJmTBE2p4Y2gz2jkFueK5nAk5JmzRz1V1dS_jSi6FgMac7hbE35QUiMY8fCv-4Iuqmq5ALOY0hoHl6YabDIn-MbrlEJBw84Cz5ol_804Nuxf_IBAig2pSzvtEiJP0cz-O&c=xPf2_GSYX-3a8I17M6ITid6S29SewReqq3w4BTmVLciyp_9K8oOLqQ==&ch=aOt51kXD79Uu6-2B1YMObWb_tnFil8adcbyBMgFosn3-pv7irtZ33Q==]
First Draft Ballot Final 
[http://r20.rs6.net/tn.jsp?f=001s_3ms41jD28sktTRW1NCcsUpkgd_gebNBRW6wJqb3dVQJCtPKBywDe57b-ZcnRYWmIkGF39MdViHnFUwQiPwHtGXL3sb9RtOC8gPjwAXVMGVqU3OALgNLYNqIAXg-sltaJJX19_D4lmNDztI_9k2421PXEJ6I2NEg3KCdGXsdWe7ty3ElkO1Eeg85EUlKZ4dQGr6UMgzIsj0mQSlteQonlXdk__3h26hLUvUTZuRLhlTH8Pr4nyZTAV6e9UOMHteX5vbQ1EDhAI=&c=xPf2_GSYX-3a8I17M6ITid6S29SewReqq3w4BTmVLciyp_9K8oOLqQ==&ch=aOt51kXD79Uu6-2B1YMObWb_tnFil8adcbyBMgFosn3-pv7irtZ33Q==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

firesprinkler.org 
[http://r20.rs6.net/tn.jsp?f=001s_3ms41jD28sktTRW1NCcsUpkgd_gebNBRW6wJqb3dVQJCtPKBywDQepKyGOXrG26rpY9MfYBc7VH-Bj-43G5ZA-1wSXlV9Sk791u_VTqwEI3wpbHxveseaXS2lfH-D3tbOHPWA4LjcMb66gbAzPMTvlSjwxeA3l6bko7e-5p1c9kzqeQBcEDg==&c=xPf2_GSYX-3a8I17M6ITid6S29SewReqq3w4BTmVLciyp_9K8oOLqQ==&ch=aOt51kXD79Uu6-2B1YMObWb_tnFil8adcbyBMgFosn3-pv7irtZ33Q==]

Hosted by the American Fire Sprinkler Association
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Technical Update is prepared by the Technical Services Dept. of the AFSA: Vice 
President
of Engineering and Technical Services Roland Huggins, a PE registered in fire 
protection
engineering; Phill Brown, a NICET IV certified automatic sprinkler technician 
and
NFPA Certified Fire Protection Specialist (CFPS) and Tom Wellen, a PE registered
 in fire protection engineering. This is provided with the understanding that 
the
AFSA assumes no liability for this opinion or actions taken on it and they are 
not
to be considered the official position of the NFPA or its technical committees.
Copyright 2015, American Fire Sprinkler Association. All Rights Reserved
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quick Links
Firesprinkler.org [http://www.firesprinkler.org]    Join AFSA 
[http://www.firesprinkler.org/membership/purchase-membership/]
   National 
[http://r20.rs6.net/tn.jsp?f=001s_3ms41jD28sktTRW1NCcsUpkgd_gebNBRW6wJqb3dVQJCtPKBywDbxHHsPc0FNgAXpiD6Lm4NtKYI1pYBBIswWHSQRuV72sbZ8TMkYIZc8senMJdjR09pnzVr1MHb1hoJjXWAvEs57ft1pZM5wnaqhcnZl_FJ7IPI3WQISvfTMom_9YnfFUoQ==&c=xPf2_GSYX-3a8I17M6ITid6S29SewReqq3w4BTmVLciyp_9K8oOLqQ==&ch=aOt51kXD79Uu6-2B1YMObWb_tnFil8adcbyBMgFosn3-pv7irtZ33Q==]
Scholarship Contest 
[http://r20.rs6.net/tn.jsp?f=001s_3ms41jD28sktTRW1NCcsUpkgd_gebNBRW6wJqb3dVQJCtPKBywDbxHHsPc0FNgAXpiD6Lm4NtKYI1pYBBIswWHSQRuV72sbZ8TMkYIZc8senMJdjR09pnzVr1MHb1hoJjXWAvEs57ft1pZM5wnaqhcnZl_FJ7IPI3WQISvfTMom_9YnfFUoQ==&c=xPf2_GSYX-3a8I17M6ITid6S29SewReqq3w4BTmVLciyp_9K8oOLqQ==&ch=aOt51kXD79Uu6-2B1YMObWb_tnFil8adcbyBMgFosn3-pv7irtZ33Q==]
Safety Training 
[http://r20.rs6.net/tn.jsp?f=001s_3ms41jD28sktTRW1NCcsUpkgd_gebNBRW6wJqb3dVQJCtPKBywDfVuqTFhU7zhbaRAisljAehsl-FyP5ISFA3_zX3BWiO1IqrRbx2ADqqCL0XGq6AVK2t4pkRj137EvSA6v6d7QVfNIKQtJeZj_pXsI-A-To3BXze79BYtadqRYuiiIuIxmVm82q1MmXahjxCA5XAEnm-S-E97pwOsifpYDD5hw-iDkWMel63QrxY=&c=xPf2_GSYX-3a8I17M6ITid6S29SewReqq3w4BTmVLciyp_9K8oOLqQ==&ch=aOt51kXD79Uu6-2B1YMObWb_tnFil8adcbyBMgFosn3-pv7irtZ33Q==]
    Technical Services 
[http://r20.rs6.net/tn.jsp?f=001s_3ms41jD28sktTRW1NCcsUpkgd_gebNBRW6wJqb3dVQJCtPKBywDRHhH69t2WCmG2iv9kfSpSxD0B81brs__CxpduZoUZYMs8PNrDOROuPIbthDLUIqsyImHhdl5H-QMp_HhbCmL4REfTqrPZepN6Rfs8fecY7Hjsse8B3fwKpsV6nQ5zicikEHkrC2uWhqpiGDcJBLq9xunhZzo0vXlg==&c=xPf2_GSYX-3a8I17M6ITid6S29SewReqq3w4BTmVLciyp_9K8oOLqQ==&ch=aOt51kXD79Uu6-2B1YMObWb_tnFil8adcbyBMgFosn3-pv7irtZ33Q==]
    Informal Interpretation Request 
[http://r20.rs6.net/tn.jsp?f=001s_3ms41jD28sktTRW1NCcsUpkgd_gebNBRW6wJqb3dVQJCtPKBywDRHhH69t2WCm_eg_aAnj3RV-tvklYa80YTFNK-0eyInTDDKFHtl6FZeHqoenj9mwo9Nu7UfnHTN76xKh9Rb0PSZQSpIAzPgZJWtTc2gksz0NfaVNLqIpa6HB6OQQmN_GxrbC-QuJI_ty_bLqBXOt1VeSeHuil0btBoK_uYWIfMFaOan3skcyfRutQqtHDsH5YA==&c=xPf2_GSYX-3a8I17M6ITid6S29SewReqq3w4BTmVLciyp_9K8oOLqQ==&ch=aOt51kXD79Uu6-2B1YMObWb_tnFil8adcbyBMgFosn3-pv7irtZ33Q==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

PDF Version
PDF Link 
[http://r20.rs6.net/tn.jsp?f=001s_3ms41jD28sktTRW1NCcsUpkgd_gebNBRW6wJqb3dVQJCtPKBywDf0C53COalSvAeNJZYDYjG3RKtATBMLTvRVYI0uLBf34lNT5yxVxOFLQnFdD0qPA5TRzKZNYHEps0rUo0jWyde5L8g25lYLSqaf8pUQLzis-abqtZvOYRY6BQoF4VcA4XQJewruFPw-p4twmr_Z9A2uRaYCWamfcye7it0Fb14yZcbfvLqEBE3MTVRUzawZBSw==&c=xPf2_GSYX-3a8I17M6ITid6S29SewReqq3w4BTmVLciyp_9K8oOLqQ==&ch=aOt51kXD79Uu6-2B1YMObWb_tnFil8adcbyBMgFosn3-pv7irtZ33Q==]
Archives 
[http://r20.rs6.net/tn.jsp?f=001s_3ms41jD28sktTRW1NCcsUpkgd_gebNBRW6wJqb3dVQJCtPKBywDamHGYBTcPmT2BsELM50u882eiUFXtUKRxJsdoPIq4vzI3yIpM89kDp8BMP1kh9bJNitg0IidKWNcSYjEm-BhmODt2jErC2k69CL91va7dfyCr4ddBYmVua46Ag3HKVqxfabzHXOJAoNOPl_CqjsRN3r5_3Z5aA0w5C4dEcDT8EM5vfpB-qjBgo30tz03gqzCA==&c=xPf2_GSYX-3a8I17M6ITid6S29SewReqq3w4BTmVLciyp_9K8oOLqQ==&ch=aOt51kXD79Uu6-2B1YMObWb_tnFil8adcbyBMgFosn3-pv7irtZ33Q==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Training Calendar
AFSA Beginning
Fire Sprinkler System
Planning School
More Information 
[http://r20.rs6.net/tn.jsp?f=001s_3ms41jD28sktTRW1NCcsUpkgd_gebNBRW6wJqb3dVQJCtPKBywDamHGYBTcPmT7va5bo4jr-lLpTZcEGsxE3fJgiAkn-GAkJ3Z4go89ZAm9Xs-vlIpyjOxNU7QGSsljCPsZcMhnIIi44vSkjsOKt8ix_QLESiynStp9x-V41fnxgFOByLvAss0Plflv-tV&c=xPf2_GSYX-3a8I17M6ITid6S29SewReqq3w4BTmVLciyp_9K8oOLqQ==&ch=aOt51kXD79Uu6-2B1YMObWb_tnFil8adcbyBMgFosn3-pv7irtZ33Q==]
May 11 - 22, 2015
July 20 - 31, 2015

Check our calendar to view upcoming training.

For details and/or to register, visit the AFSA Calendar 
[http://www.firesprinkler.org/events/].

e-campus_logo 
[http://r20.rs6.net/tn.jsp?f=001s_3ms41jD28sktTRW1NCcsUpkgd_gebNBRW6wJqb3dVQJCtPKBywDRofp3t9AkTIf9sYkLQZi7EM-bxc6ByxzOFI1YqQXfVcP7aqOvsCXPucJCBSAiRfcj__QSX1Jool7GIVnRK-YxqbGNmWvTMEks6qz7xc13M6bw0BB_ui3kCwzpMHiByruQ==&c=xPf2_GSYX-3a8I17M6ITid6S29SewReqq3w4BTmVLciyp_9K8oOLqQ==&ch=aOt51kXD79Uu6-2B1YMObWb_tnFil8adcbyBMgFosn3-pv7irtZ33Q==]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Free Subscription to Sprinkler Age 
[http://www.firesprinkler.org/sprinklerage/subscribe/]
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~

Quality Contractor 
[http://www.firesprinkler.org/member-center/afsa-quality-contractor-recognition/]

~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Forward email
http://ui.constantcontact.com/sa/fwtf.jsp?llr=gdnaptcab&m=1102312387686&[email protected]$&a=1120544701438

This email was sent to [email protected] by 
[email protected].

Update Profile/Email Address
http://visitor.constantcontact.com/do?p=oo&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=6bda41e6-7882-41a7-bf4e-e8cd487f0914


Instant removal with SafeUnsubscribe(TM)
http://visitor.constantcontact.com/do?p=un&m=001GQO31O13sDTrK9y8bEn5_A%3D%3D&ch=d1293a80-f8c6-11e3-9a97-d4ae527b8c41&ca=6bda41e6-7882-41a7-bf4e-e8cd487f0914


Privacy Policy:
http://ui.constantcontact.com/roving/CCPrivacyPolicy.jsp

Online Marketing by
Constant Contact(R)
www.constantcontact.com



American Fire Sprinkler Association | 12750 Merit Drive, Suite 350 | Dallas | 
TX | 75251
_______________________________________________
Sprinklernotes mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklernotes-firesprinkler.org

Reply via email to