Building Expansion Joints in Seismic Areas

 

“We have a project that contains several expansion joints with a 2-in. gap and 
a 4-in. gap that branch lines will be required to cross multiple times along 
with the feed main in a few locations. Section 9.3.2.3.1(4) indicates that 
flexible couplings shall be installed within 24 in. of expansion joints with 
annex material describing and clarifying the purpose of expansion joints. The 
architectural and structural documents specifically call out and label these 
joints as “expansion” and not “seismic,” along with section details indicating 
rated UL listed joint systems that are to be installed. For expansion joints 
occurring in regions subject to earthquakes, is there a maximum gap for 
expansion joints that when exceeded would require the use of a seismic joint 
assembly rather than the flexible coupling as indicated by 9.3.2.3.1(4)?”

 

 We have reviewed NFPA 13, 2013 edition that you indicated as the applicable 
standard.  Our informal interpretation is that there is not a maximum gap size 
for expansion joints.

 

The standard is explicit that only a flexible coupling is needed within 24 in. 
of building expansion joints per 9.3.2.3.1(4) regardless of the size of the 
gap. A seismic separation assembly is required where sprinkler piping, 
regardless of size, crosses building seismic separation joints at ground level 
and above per 9.3.3. These two joints are not the same and the standard 
addresses these separately. Expansion joints are introduced to accommodate 
building movements caused by shrinkage, creep, or temperature changes. They are 
often one-way joints, meaning they are usually intended to accommodate 
movements in the direction perpendicular to the joint. A seismic separation 
joint will create separate structures. This may be the same building or 
separation of an adjacent building to accommodate story drift. Although it may 
appear as a single structure, seismic separation allows these structures to 
move independently of the adjacent structure. Seismic separation joints have to 
accommodate movement in both orthogonal directions simultaneously and their 
spacing is not typically affected by building length or size. To determine if 
the joint is expansion or seismic separation, structural columns will be 
typically located on each side of a seismic separation. Structural columns may 
not be located on each side of an expansion joint. Seismic separation joints 
typically create a separation between walls, floors, roof, piping, and HVAC 
ducts that have a functional need to cross the joint. The design of seismic 
joints is complex and includes proper sizing, adequately sealed from the 
weather, and it’s safe to walk on. It also provides for adequate movement of 
other systems crossing the joint while maintaining any fire ratings of the 
floor, roof and wall systems.

 

 

=========

Technical Update is prepared by the Technical Services Dept. of the AFSA: 
Roland Huggins, a PE registered in fire protection engineering, Vice President 
of Engineering and Technical Services; and Tom Wellen, a PE registered in fire 
protection engineering and Tom Noble E.T., a Technical Programs Specialist. 
This is provided with the understanding that the AFSA assumes no liability for 
this opinion or actions taken on it and they are not to be considered the 
official position of the NFPA or its technical committees.

 

Copyright 2017, American Fire Sprinkler Association. All Rights Reserved.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.firesprinkler.org/private.cgi/sprinklernotes-firesprinkler.org/attachments/20170501/9a46246c/attachment.htm>

Reply via email to