Obstructions Below Residential Sprinklers

 

 

 

You have asked the following question: "We are installing a NFPA 13D system.  
In the bedroom, there is a peaked ceiling with collar ties that are 8 inches X 
8 inches.  They are not beams (tight to the ceiling) but are located 51in. 
below the ceiling peak (similar to the bottom chord of a pitched truss).  There 
are four collar ties with a separation of 4 ft. and 5 in. (measured to the 
side).  There are four sprinklers in the room.  They are located midway between 
the collar ties so 2 ft. 2-1/2 in. horizontally from their side and 1 ft. 2 in. 
vertical above the top of the collar ties.  This creates a radial separation of 
33 in.  With this being a continuous obstruction, am I required to comply with 
the beam rule (13D:8.2.5.4.2)?" 

 

In response to your question, we have reviewed the 2010 edition of NFPA 13D as 
the applicable standard.  Our informal interpretation is that the installation 
meets the intent of NFPA 13D.

 

This is a very interesting problem for a couple of reasons.  Let's start with 
the issue of continuous obstructions in section 8.2.5.4.2.  A continuous 
obstruction is one that affects two or more adjacent sprinklers (this 
definition is not yet in NFPA 13D and was added to NFPA 13 in the 2013 
edition).   Such obstructions can be above or below the sprinkler. The location 
in relation to the sprinkler deflector is a critical parameter since different 
rules apply depending on said location.  This is well addressed in NFPA 13 but 
poorly addressed in NFPA 13D (as discussed in the second paragraph).  As for 
section 8.2.5.4.2 (also referred to as the beam rule), as Figure 8.2.5.4.2 
portrays, this only applies to obstructions that are close to (and usually 
tight to) the ceiling.  In other words, it is when the top of the obstruction 
is at, or above, the plane of the deflector.  This is explicitly identified in 
NFPA 13, but you'll have to look at section 13:8.6.5.2.1.2 of a 2013 or later 
edition.  As discussed in NFPA 13: A.8.6.5.2.1.3 in regards to the three-times 
rule, it states: "This works for small non-continuous obstructions and for 
continuous obstructions where the sprinkler can throw water over and under the 
obstruction,.."  However, when a beam is above the deflector, you have to be 
able to adequately throw water beneath it.  It's interesting that the 
discussion keys on the ability to throw water over the obstruction which really 
won't happen if the defector is only slightly above the top of the obstruction, 
but the physical relationship has been explicitly defined.  Nonetheless, the 
beam rule is intended to be for obstructions close to, or tight to, the 
ceiling.  This is the same criteria as provided in NFPA 13:8.5.6.1, which 
explicitly identifies the location of the obstruction.

 

What makes this issue really interesting is that all of the rules in NFPA 13 D 
for pendent sprinklers, other than for fans, address obstructions tight to the 
ceiling.  The only other rule for obstructions below the sprinkler is the 
cabinet rule for sidewall sprinklers.  The standard is written around the 
normal situation where obstructions, like ducts, seldom exist.  For all intents 
and purposes, the collar tie impacts the sprinkler the same as a duct. 
Effectively, there are no rules for obstructions below the sprinklers.  As 
such, a literal application is that there are no requirements for such 
obstructions.

 

Until the technical committee recognizes that obstructions below the deflector 
do occasionally occur and adds rules to address them, it’s reasonable to apply 
the criteria from NFPA 13.  The four-times rule for residential sprinklers 
provides appropriate separation.  Keeping in mind that NFPA 13 is a more 
demanding document than NFPA 13D, this meets or exceeds the intent of NFPA 13D.

 

There is one small issue that must be resolved.  Section 8.10.6.2.1.2 still 
states: “Regardless of the rules of this section, solid continuous obstructions 
shall meet the applicable requirements of 8.10.6.1.2.”  This is the same text 
that section 8.6.5.2.1.2 used in the 2010 edition.  The proposal for 2013 asked 
that a change be made to section 8.6.5 and no other sections were considered.  
The philosophy of how to treat the location of an obstruction is the same 
regardless of the type of sprinkler.  From a sprinkler activation and discharge 
perspective, it is clear that the beam rule should be applied in the same 
manner for a residential sprinkler as it is for a spray sprinkler.  The problem 
is that the committee has not yet been asked to look at it.  This will be 
addressed in the next cycle.