sprinklernotes
Pressure-Regulating Devices in Suction Piping

 You asked the following question: “Are pressure-reducing valves allowed in the 
suction pipe of a fire pump?”

In response to your question, we have reviewed NFPA 20, Standard for the 
Installation of Stationary Pumps for Fire Protection, 2019 edition. Our 
informal interpretation is that pressure-reducing valves are not permitted to 
be installed in fire pump installations. 

NFPA 20 does not permit the use of pressure-regulating devices, which includes 
pressure-reducing valves, to be installed in fire pump piping as a means to 
reduce the system pressure below the maximum-rated pressure.

4.7.7.2* Pressure relief valves and pressure-regulating devices in the fire 
pump installation shall not be used as a means to meet the requirements of 
4.7.7.1.

This limitation is restricted to the pipe under the scope of NFPA 20 which 
includes all pipe, fittings, and appurtenances from the connection to the water 
supply to the system side of the discharge control valve.

4.16.1.1 The suction components shall consist of all pipe, valves, and fittings 
from the pump suction flange to the connection to the public or private water 
service main, storage tank, or reservoir, and so forth, that feeds water to the 
pump.

4.17.1 The discharge components shall consist of pipe, valves, and fittings 
extending from the pump discharge flange to the system side of the discharge 
valve.

Anything downstream of the discharge control valve would be under the 
jurisdiction of the installation standard for the fire protection system that 
the fire pump is supplying and anything upstream of the connection to the 
source would be under the jurisdiction of the applicable installation standard 
and/or water purveyor.

 

 