Hydrostatic Testing of Tenant Improvements

The following information was provided: We have a local AHJ that always 
requires us to pump up tenant improvement projects to 200 psi if they are over 
20 sprinklers. We have a waiver/release form we always get signed from the 
owner and/or GC. It always results in delays and change orders for additional 
testing time as well as repairs to areas that were not in our scope.
 
You asked the following question: Does NFPA 13 require an existing system to be 
pressurized to 200 psi when modifications in excess of 20 sprinklers cannot be 
isolated?
 
In response to your question(s), we have reviewed NFPA 13, Standard for the 
Installation of Sprinkler Systems, 2019 edition.
 
Our informal interpretation: Our informal interpretation is that NFPA 13 does 
not require an existing system that cannot be isolated, regardless of the 
number of sprinklers modified, to be pressurized to 200 psi. A hydrostatic test 
is required, but only at the system working pressure.
 
When installing portions of the system that can be isolated AND consist of more 
than 20 sprinklers in the individual portion, that portion shall be tested 
using the standard hydrostatic test per section 29.7.1.1:
 
29.7.1.1 Where modification is made to an existing system affecting more than 
20 sprinklers, the new portion shall be isolated and tested at not less than 
200 psi (13.8 bar) for 2 hours.
 
If that section cannot be isolated, then section 29.7.1.2 applies:
 
29.7.1.2 Modifications that cannot be isolated, such as relocated drops, shall 
require testing at system working pressure.
 
While the intent is not directly stated in the body of the standard, the 
handbook commentary clarifies the intent behind the sections:
 
The requirements of 29.7.1, 29.7.1.1, and 29.7.1.2 address additions and 
modifications and specify when new piping installations are to be isolated and 
tested. In many cases, segregating new work from existing work is difficult. To 
require the entire system to undergo another hydrostatic test when only 
relatively minor changes have been made is unreasonable and not required by 
NFPA 13.
 
Where system modifications are made and the piping cannot be isolated, such as 
relocated drops, NFPA 13 provides some flexibility and permits hydrostatic 
tests to be conducted at the system’s normal static pressure. In general, 
existing portions of the system do not need to be subjected to a new 
hydrostatic test. In general, existing portions of the system do not need to be 
subjected to an additional hydrostatic test above system working pressure. 
There is no limit on the number of sprinklers modified throughout the building 
when they cannot be isolated. This relieves the requirement to subject the 
existing portions of the system from a new hydrostatic test of 200 psi for 2 
hours. A hydrostatic test is still completed but not in excess of the system 
working pressure.
 
It’s important to understand and be familiar with the definition of “system 
working pressure,” as it will affect the pressures at which we are required to 
test the system.
 
3.3.216. System Working Pressure. The maximum anticipated static (nonflowing) 
or flowing pressure applied to sprinkler system components exclusive of surge 
pressures and exclusive of pressure from the fire department connection
 
In addition to the definition of system working pressure, there is handbook 
commentary that helps clear up any confusion.
 
The term system working pressure applies to the maximum pressure that the 
system is expected to be exposed to under normal circumstances. All components 
of the sprinkler system should be rated for operating pressures at or above the 
system working pressure. Transient pressure spikes (surge pressure) and 
elevated pressure pumped into the system during fire department operations are 
not taken into consideration for the purposes of defining the system working 
pressure.
 
In closing, section 29.7.1.2 is not stating that only relocated drops are 
exempt from testing at 200 psi. The committee is merely providing an example 
where testing at system pressure is acceptable. It is impossible for the 
standard to cover every possible situation that would be exempt, which is why 
the wording “such as” was used in the section.