The SQLite website is back up after being down
all day due to a power supply failure at a data
center.  Sorry for the inconvenience.  For those
who are curious, the a detailed description of
the data center's problem is reproduced below:


> Location: DLLSTX2 
> Severity: Level 5 
> Description: 
> At 4:09AM CST, a power failure occurred in a redundant pair of Powerware UPS 
> units feeding power to section B of the DLLSTX2 datacenter. The power failure
> was caused by a faulty fuse in UPS unit B-1. As the load transferred to UPS 
> unit B-2, the spike in the load created an overloaded breaker and UPS B2 also 
> lost power. This resulted in a power outage to the main power distribution 
> unit feeding section B of the datacenter floor. Emergency teams were notified 
> and the power was restored within 20 minutes. The power continued to cycle 
> until 6:45AM due to the faulty fuse and the inability of the redundant UPS 
> units to remain in bypass mode. Customers may have noticed several power 
> cycles during this time period. Powerware, JT Packard, and electricians found 
> the problem and replaced the faulty hardware and fuses. At 6:45AM, all 
> electrical 
> service was restored to normal and the NOC team began to bring all servers 
> back online. The technical staff is currently placing a console on all 
> servers 
> to verify server restarts. Customers with operating systems that require a 
> file 
> check may have experienced extended downtime during the file check. Powerware 
> and JT Packard will continue to monitor the UPS systems for the next 24 to 48 
> hours. The Planet does not anticipate any further outages.
> 

Note that even though the management at The Planet claims
that all power was restored by 6:45 AM, in fact the server
that hosts www.sqlite.org did not receive power until about
12:30 PM.  
-- 
D. Richard Hipp <[EMAIL PROTECTED]>

Reply via email to