http://www.nerc.com/files/BAL-005-0.pdf
http://www.nerc.com/files/BAL-005-1.pdf

It would appear these documents are just talking about annual
calibration requirements of the *transducer* (the control room
test equipment used to measure line frequency) and do not
imply a specification of line frequency itself.

Does anyone know which NERC document specifies power line
phase or frequency? (and note that a frequency measurement
implies an averaging time).

See http://leapsecond.com/pages/mains/ for the ADEV of power
line frequency. It's ~2e-5 at one day. So does NERC owe me a
million bucks or not?

/tvb

----- Original Message ----- 
From: "Bill Hawkins" <[EMAIL PROTECTED]>
To: "'Discussion of precise time and frequency measurement'" 
<time-nuts@febo.com>
Sent: Friday, November 21, 2008 12:16 PM
Subject: Re: [time-nuts] Do any regulations or laws require time tobeaccurate 
within 'x' seconds?


> That's an interesting reference. Google finds it.
> 
> Assuming that the digital frequency transducer measures the 60 Hz line
> frequency, the required accuracy is somewhat less than 2 parts in 10E-5.
> 
> Analog transducers, like Watts, Volts, and VARs, require 0.25% of scale
> accuracy. Calibration is annual.
> 
> This is nothing like the 10E-15 sought by time nuts.
> 
> Bill Hawkins
> 
> 
> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On
> Behalf Of Mike Clapp
> Sent: Friday, November 21, 2008 1:04 PM
> To: Discussion of precise time and frequency measurement
> Subject: Re: [time-nuts] Do any regulations or laws require time to
> beaccurate within 'x' seconds?
> 
> The North American Electric Reliability Corporation (NERC) under federal
> law can fine of up to $1 million a day.
> 
> Standard BAL-005-0 - Automatic Generation Control Requirement 17. Each
> Balancing Authority shall at least annually check and calibrate its time
> error and frequency devices against a common reference. The Balancing
> Authority shall adhere to the minimum values for measuring devices as
> listed below:
> 
> Device Accuracy
> 
> Digital frequency transducer ? 0.001 Hz



_______________________________________________
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Reply via email to