The jacket might be rated for it, but if it's a commercial operation, it's against code to route it around without protection. This would also apply to your house, you can't run Romex vertically or horizontally against walls where a human might crash into it, or damage it. The fear being bumping into the exposed Romex with sharp metal object (tool) and cutting the insulation which would present an electrocution hazard. Overhead in the ceiling joists is OK, but lower that head height, NG. If it's against the wall, it should be conduit, if it's floating like a connection to your boiler, then BX is acceptable.

Bob




----- Original Message ----- From: "jimlux" <jim...@earthlink.net> To: "Discussion of precise time and frequency measurement" <time-nuts@febo.com>
Sent: Friday, June 18, 2010 1:46 PM
Subject: Re: [time-nuts] Galvanic decoupling of GPS antenna


Robert Benward wrote:
Rated for 1400V from CENTER conductor to shield, not shield to the
outside. If you choose to use RG-58 with 250V on the shield then you
will need to put the entire cable inside conduit.  It is not acceptable
to have any type of exposed mounting.

Bob


Yeah... I've been looking for the jacket rating...  As a practical
matter, I've used solid dielectric RG-58 (both A and C flavors) to carry
10kVrms AC (neon sign transformer type voltages).  Usually, you don't
get breakdown between center/shield.

However, considering that ordinary PVC insulated hookup wire is rated at
300V, I suspect it's ok.

Obviously, we're talking a transient here.. if you're floating the
shield at 200V above surrounding objects/ground, a better solution is
called for.


Interestingly, looking at MIL-C-17 (which covers coax)

There are several requirements for RG-58 (MIL-C-17-28)
Spark test: 5000V rms +10%/-0%
Voltage Withstanding: 5000Vrms +10%/-0%
Corona extinction voltage 1900Vrms minimum

Then, looking at the test procedures in Sec 4.8 of MIL-C-17G

Spark test (4.8.3) A test voltage at a frequency...shall be applied
between the outermost braid or shield and the outer surface of the jacket.

Voltage withstanding (4.8.4) (a) For coaxial cables. The test voltage
shall be applied between the inner and the outer conductor, with the
outer conductor grounded.


Overall.. MIL-C-17 is a great reference on how to test coax (or to ask
your coax supplier about how they test...)

_______________________________________________
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.


--------------------------------------------------------------------------------



No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.829 / Virus Database: 271.1.1/2946 - Release Date: 06/18/10 02:35:00


_______________________________________________
time-nuts mailing list -- time-nuts@febo.com
To unsubscribe, go to https://www.febo.com/cgi-bin/mailman/listinfo/time-nuts
and follow the instructions there.

Reply via email to