Hi Jamie,

Looking at the lines:

SNMPv2-SMI::enterprises.16174.1.1.1.3.1.2.0 = STRING: "21.8"
SNMPv2-SMI::enterprises.16174.1.1.1.3.1.3.0 = INTEGER: 22
SNMPv2-SMI::enterprises.16174.1.1.1.3.2.2.0 = STRING: "20.1"
SNMPv2-SMI::enterprises.16174.1.1.1.3.2.3.0 = INTEGER: 20
SNMPv2-SMI::enterprises.16174.1.1.1.3.3.2.0 = STRING: "24.1"
SNMPv2-SMI::enterprises.16174.1.1.1.3.3.3.0 = INTEGER: 24
SNMPv2-SMI::enterprises.16174.1.1.1.3.4.2.0 = STRING: "24.7"
SNMPv2-SMI::enterprises.16174.1.1.1.3.4.3.0 = INTEGER: 25 

It looks like you have 4 probes recording a temperature and providing 2 values 
each, 1 being the temp to 1 decimal place and another rounded to an integer.

It's my understanding that using OIDs as a data source that have more than 1 
value (like the one you have entered) *should* work, but it's currently broken, 
see this forum post:

http://community.zenoss.com/forums/viewtopic.php?t=6387


However, if you add multiple data sources, using the OIDs below you will get a 
single graph showing the 4 temperatures - you can then add a threshold of X 
degrees and any of the 4 above that threshold will give you an alert. Here's 
the OIDs to use:

1.3.6.1.4.1.16174.1.1.1.3.1.2.0
1.3.6.1.4.1.16174.1.1.1.3.2.2.0
1.3.6.1.4.1.16174.1.1.1.3.3.2.0
1.3.6.1.4.1.16174.1.1.1.3.4.2.0

If you click the test button on any one of those you should see a single line 
and a single temperature value.

After remodeling the device, and waiting a few minutes, you should see the 
graph appear correctly. Here's the full process for creating the graph which 
should work:


1 - Navigate to the device you want to monitor -> click the "down arrow" -> 
more -> templates.
2 - Second "down arrow" -> enter a name (e.g "tempProbe") -> OK
3 - Click the new template name (tempProbe) -> enter a description -> save


4 - "Data sources down arrow" -> add data source -> enter a name (e.g: commsLH) 
-> OK
5 - OID = 1.3.6.1.4.1.16174.1.1.1.3.1.2.0 -> save
6 - "Data points down arrow" -> add data point -> enter name (e.g CommsLH) -> 
Add
7 - Type -> Gauge** -> Save
8 - Click the "tempProbe" name in the tree at the top

Repeat steps 4-8 using the values:

OID                                     Name
1.3.6.1.4.1.16174.1.1.1.3.2.2.0         Comms RH
1.3.6.1.4.1.16174.1.1.1.3.3.2.0         Serv LH
1.3.6.1.4.1.16174.1.1.1.3.4.2.0         Serv RH

9 - Click "threshold down arrow" -> enter name (eg: maxTemp) -> OK
10 - Hold ctrl and click all the datapoints to select them -> enter max value 
(e.g: 60) -> select severity -> save
11 - Click the "tempProbe" name in the tree at the top

Repeat steps 9-11 for any other thresholds you want (e.g: 90 maybe critical)

12 - Click "graph definitions down arrow" -> enter name (eg: tempGraph) -> OK
13 - Units = C (or F) -> save
14 - Click "graph points down arrow" -> select all the graph points using ctrl 
click (or shift click) -> make sure threshold is ticked -> OK
15 - Click each graph point (excl the thresholds) -> linetype = line -> save

16 - Remodel the device, go to the perf tab and you should see the graph - 
you'll probably see "nan" for the values for a little while until snmp has 
picked up the values.


** For future reference on the data source types, see here: 
http://www.zenoss.com/community/docs/zenoss-guide/2.2.0/ch12s05.html




-------------------- m2f --------------------

Read this topic online here:
http://community.zenoss.com/forums/viewtopic.php?p=21602#21602

-------------------- m2f --------------------



_______________________________________________
zenoss-users mailing list
[email protected]
http://lists.zenoss.org/mailman/listinfo/zenoss-users

Reply via email to