For the 100AH ones we just put them on a battery shelf mounted at the
bottom of our telco rack.  For the 60AH ones we put them in a
separate battery enclosure in the cabinet.

On Wed, Feb 3, 2021 at 3:00 PM Josh Baird <joshba...@gmail.com> wrote:

> No, they go in dedicated battery enclosures and/or sit on mats in larger
> buildings.
>
> On Wed, Feb 3, 2021 at 3:53 PM Josh Luthman <j...@imaginenetworksllc.com>
> wrote:
>
>> Specifically for ICT, you need to adjust the LVD to be higher than the
>> BMS's cut off.  If you let it drop with the BMS, it's 0v and then the
>> battery is basically gone until you reset it (like drive out there and
>> physically push a button).  Float voltage I'm told you need to change, too.
>>
>> Looking at the NSB100FT RED, these are nearly a foot tall.  Are you
>> mounting them in the rack?  That's 7U of space, which I suppose isn't
>> massive (I was previously looking at lithium ion before learning about the
>> complications, that was 6U).
>>
>> Josh Luthman
>> 24/7 Help Desk: 937-552-2340
>> Direct: 937-552-2343
>> 1100 Wayne St
>> Suite 1337
>> Troy, OH 45373
>>
>>
>> On Wed, Feb 3, 2021 at 3:01 PM Chuck McCown via AF <af@af.afmug.com>
>> wrote:
>>
>>> I presume if the float voltages are the same you could.  But not if they
>>> are different.
>>>
>>> *From:* SmarterBroadband
>>> *Sent:* Wednesday, February 3, 2021 11:52 AM
>>> *To:* 'AnimalFarm Microwave Users Group'
>>> *Subject:* Re: [AFMUG] Battery recommendations at fiber hut
>>>
>>>
>>> Can you connect batteries like this, with built in BMS, directly into a
>>> system like ICT made for SLA/AGM?
>>>
>>> Adam
>>>
>>>
>>>
>>> *From:* AF [mailto:af-boun...@af.afmug.com] *On Behalf Of *Louis
>>> Arsenault
>>> *Sent:* Wednesday, February 3, 2021 4:48 AM
>>> *To:* AnimalFarm Microwave Users Group <af@af.afmug.com>
>>> *Subject:* Re: [AFMUG] Battery recommendations at fiber hut
>>>
>>>
>>>
>>> We have been using PowerTec Solutions
>>>
>>>
>>> https://www.powertecsolutions.net/solutions/#psi-micro-vision-48v-rackmount-battery-series
>>>
>>> We have 4 of them setup in the fiber hut.
>>>
>>> They have a BMS to protect the batteries from overcharging /
>>> overcurrenting
>>>
>>>
>>>
>>> On Tue, Feb 2, 2021 at 3:33 PM Josh Luthman <j...@imaginenetworksllc.com>
>>> wrote:
>>>
>>> I'm looking at a 1200 watt load and would like to see 2 or 3 hours of
>>> run time.  Everything's 48vdc.
>>>
>>>
>>>
>>> I'm kind of leary about using lithium ion since I'm using an ICT power
>>> supply and their system is designed for SLA/AGM.
>>>
>>>
>>>
>>> What kind of things should I be looking for?  I thought these looked
>>> pretty good:
>>>
>>>
>>> https://www.batteriesplus.com/productdetails/battery/sla-sealed-lead-acid/12/wkdc12=80pus
>>>
>>>
>>>
>>> 12v*80a=960whr
>>>
>>> 4 of these = 3840whr
>>>
>>> Runtime upwards of 3.2 hours (obviously there will be loss, but
>>> shouldn't I expect 2+ hours)?
>>>
>>>
>>>
>>> Josh Luthman
>>> 24/7 Help Desk: 937-552-2340
>>> Direct: 937-552-2343
>>> 1100 Wayne St
>>> Suite 1337
>>> Troy, OH 45373
>>>
>>> --
>>> AF mailing list
>>> AF@af.afmug.com
>>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>>>
>>> ------------------------------
>>> --
>>> AF mailing list
>>> AF@af.afmug.com
>>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>>>
>>> --
>>> AF mailing list
>>> AF@af.afmug.com
>>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>>>
>> --
>> AF mailing list
>> AF@af.afmug.com
>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>>
> --
> AF mailing list
> AF@af.afmug.com
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>


-- 

Carl Peterson

*PORT NETWORKS*

401 E Pratt St, Ste 2553

Baltimore, MD 21202

(410) 637-3707
-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to