I mixed + and - 48 in a off grid solar system. I had one battery bank with the positive to the common point/ ground. The other battery bank was negative to the common point. From one battery to the other it was 96 volts when went to the load.

But I had two 48 volt solar systems and charge controllers and they charged each half of the total battery independently. One of the charge controllers had to be mounted on an insulating board because its chassis was hot.

The whole -48, +48 thing is all about what is connected to the ground, common point, return etc. If you ground the negative side of a battery you have a positive voltage hot wire system. If you ground the positive side of a battery you have a negative voltage hot wire. The battery itself does not care.

If you load does not have an electrical connection to a grounded chassis, it will not car either.

However if you have a device that is designed to be powered from -48 and internally its positive 48 connections are all bonded to its metallic chassis, it really needs to be powered from a floating supply or a -48 supply.

There is no good reason to ground either side of a DC supply in a system these days. Originally telcos went with positive grounding so that if you had an insulation fault in an underground cable, the -48 volt ring side (hot side) of the phone line would tend to attract metallic ions from the surrounding soil. If it was reversed the wire would donate copper ions to the soil and quickly plate itself away to nothingness.




-----Original Message----- From: Mark - Myakka Technologies
Sent: Monday, January 8, 2024 9:25 AM
To: af@af.afmug.com
Subject: [AFMUG] -48V kicking the dead horse

I know we have been though this many times and I thought I understood it.

-48VDC is the Negative side being HOT, correct?

It is BAD to try to mix -48VDC and 48VDC

There is no such thing as a -48V battery.  A battery is a battery, correct?

How about the ICT Platinum power supplies. They show as 48VDC, can they be used on -48VDC equipment?

I remember Check saying something about a way to test to see if a piece of equipment that is Neg 48VDC is truly grounded as Neg 48VDC.


--

Thanks,
Mark                          mailto:m...@mailmt.com