Without actually digging out a NEC code book…

Inside a panel pretty much anything goes - the theory being that if it’s inside 
the box it’s protected from physical damage.  THHN in wire loom is a little 
different but I don’t think it violates code.  They could have run it through a 
chase nipple and thrown some wire ties on it and been fine.   This is a little 
cleaner.

For the knockout on the side of the box the 3/4 knockout is just where you put 
the punch through for whatever size conduit you want.  

For the bottom of the box - yeah, I’ll give you that’s a little odd.

Mark

> On Feb 13, 2026, at 6:47 PM, Adam Moffett <[email protected]> wrote:
> 
> This post is part question and part whining.
> 
> Yesterday I got a look at a manufactured network enclosure from a fairly 
> large company.  They have a load center built in, and the feeds to the 
> rectifier are THHN in wire loom.  They bring that into the load center with 
> NM box connectors.  
> 
> I want to believe that they wouldn't sell something to us for $30,000 that 
> wasn't up to electrical code, but 
> I have never seen that done before, and neither has our electrician
> It doesn't make me feel like I got $30,000 worth
> 
> Does anyone know if this is actually square with the NEC?
> 
> Even if it's legally ok, how does it make any sense?
> 
> <image.png>
> 
> <image.png>
> 
> 
> Weird thing #2:
> 
> The installation guide says to bring our incoming utility power through the 
> knockout shown here under the load center.  The one next to it with the 
> rubber passthrough is for a ground to the equipment MGB.  It's a ¾ knockout, 
> and I added a picture of the bottom side to show that it's not one of the 
> expandable ones.  The main breaker in the load center is 100A. Normally you'd 
> want a 1-1/4 knockout for a 100A service.  I struggled to think of some 
> creative way to get 100A through a ¾ conduit and still be compliant, but I 
> got nothing.  I think we'll have to remove the factory breaker and install a 
> 50A.  It's either that or bore a 1.7" dia hole somewhere, and while I do 
> enjoy cutting up metal I don't think I should have to.
> 
> <image.png>
> 
> <image.png>
> 
> -- 
> AF mailing list
> [email protected] <mailto:[email protected]>
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com

-- 
AF mailing list
[email protected]
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to