>From PSUI:

Traco TSP 360-148 (360w/48V) - $233
Traco TSP-BCM48 - $126

Or, instead of the BCM48, you can use the:

Traco TSP-BCMU360 (single 12V battery, selectable 24/48V output, less
charging current than the BCM48) for around the same price, I believe.

Josh

On Thu, Mar 10, 2016 at 9:57 AM, Gino Villarini <[email protected]> wrote:

> how much are you paying for this combo?
>
> On Wed, Mar 9, 2016 at 4:21 PM, George Skorup <[email protected]> wrote:
>
>> The AD-155 is 150W max load.
>>
>> What I would do is a Traco TSP 48v power supply (180, 240, 360 or 600W),
>> a TSP-BCMU360 in 48v mode and a Mean Well 48 to 24 RSD. The BCMU360 takes a
>> 12v SLA and does an internal DC-DC conversion. I haven't had any problems
>> with them. I have two in the field right now maintaining 37Ah Deka's.
>>
>>
>> On 3/9/2016 2:06 PM, SmarterBroadband wrote:
>>
>> That Meanwell sounds right.  I will have to see if they make a more
>> powerful one?
>>
>>
>>
>> *From:* Af [mailto:[email protected] <[email protected]>] *On
>> Behalf Of *Mathew Howard
>> *Sent:* Wednesday, March 09, 2016 11:39 AM
>> *To:* af
>> *Subject:* Re: [AFMUG] Small DC Site
>>
>>
>>
>> Is there really any advantage to using something like an AD-155B with a
>> UPS function over just connecting the batteries in parallel with the load
>> to a normal DC power supply and setting the voltage properly? It seems like
>> there would be less parts to fail and it'd be easier to add redundancy if
>> the batteries were just connected in parallel.
>>
>>
>>
>> On Wed, Mar 9, 2016 at 12:52 PM, Chuck McCown <[email protected]> wrote:
>>
>> A pair of power supplies that are capable of pulling the load and
>> charging the battery.
>>
>>
>>
>> For example, if you needed 200 watts for your 24 volt loads, you need 8.3
>> amps.  Round that up to 10 amps.
>>
>> Then you have to decide how long you want this thing to last without
>> commercial power.  I would think 24 hours is a minimum.  So 10 amps x 24
>> hours is 240 amp hours of battery.
>>
>> It is always a safe figure to charge a battery at .1C or 10% of its
>> capacity or less.  That would be 24 amps to charge the batts after a power
>> outage, plus 10 for load = 34 amps of power supply.  You could get by with
>> 20 amps, just will take a bit longer to charge.
>>
>>
>>
>> Lots of 20 amp 28VDC power supplies out there.
>>
>> Rule of thumb double your load power or more to size the charger.
>>
>>
>>
>> *From:* SmarterBroadband <[email protected]>
>>
>> *Sent:* Wednesday, March 09, 2016 11:45 AM
>>
>> *To:* [email protected]
>>
>> *Subject:* [AFMUG] Small DC Site
>>
>>
>>
>> What are people using to power small DC sites.  Option 1 up to 150 - 200
>> Watts, option 2 up to 300 – 400 Watts.  I’m looking for a DC UPS that can
>> charge attached batteries.  Need to have 24 and 48 volt.
>>
>>
>>
>>
>>
>