these are the models we use
PULS Power supplies.
24VDC power supplies  240Watt=10Amps QS10.241, 480Watt=20Amps QS20.241

48VDC power supplies 240Watt=5Amps QS10.481, 480Watt=10Amps QS20.481

good stuff...much better then I Don't Meanwell

Jaime Solorza
Wireless Systems Architect
915-861-1390

On Thu, Mar 10, 2016 at 8:06 AM, Josh Baird <[email protected]> wrote:

> From PSUI:
>
> Traco TSP 360-148 (360w/48V) - $233
> Traco TSP-BCM48 - $126
>
> Or, instead of the BCM48, you can use the:
>
> Traco TSP-BCMU360 (single 12V battery, selectable 24/48V output, less
> charging current than the BCM48) for around the same price, I believe.
>
> Josh
>
> On Thu, Mar 10, 2016 at 9:57 AM, Gino Villarini <[email protected]>
> wrote:
>
>> how much are you paying for this combo?
>>
>> On Wed, Mar 9, 2016 at 4:21 PM, George Skorup <[email protected]> wrote:
>>
>>> The AD-155 is 150W max load.
>>>
>>> What I would do is a Traco TSP 48v power supply (180, 240, 360 or 600W),
>>> a TSP-BCMU360 in 48v mode and a Mean Well 48 to 24 RSD. The BCMU360 takes a
>>> 12v SLA and does an internal DC-DC conversion. I haven't had any problems
>>> with them. I have two in the field right now maintaining 37Ah Deka's.
>>>
>>>
>>> On 3/9/2016 2:06 PM, SmarterBroadband wrote:
>>>
>>> That Meanwell sounds right.  I will have to see if they make a more
>>> powerful one?
>>>
>>>
>>>
>>> *From:* Af [mailto:[email protected] <[email protected]>] *On
>>> Behalf Of *Mathew Howard
>>> *Sent:* Wednesday, March 09, 2016 11:39 AM
>>> *To:* af
>>> *Subject:* Re: [AFMUG] Small DC Site
>>>
>>>
>>>
>>> Is there really any advantage to using something like an AD-155B with a
>>> UPS function over just connecting the batteries in parallel with the load
>>> to a normal DC power supply and setting the voltage properly? It seems like
>>> there would be less parts to fail and it'd be easier to add redundancy if
>>> the batteries were just connected in parallel.
>>>
>>>
>>>
>>> On Wed, Mar 9, 2016 at 12:52 PM, Chuck McCown <[email protected]> wrote:
>>>
>>> A pair of power supplies that are capable of pulling the load and
>>> charging the battery.
>>>
>>>
>>>
>>> For example, if you needed 200 watts for your 24 volt loads, you need
>>> 8.3 amps.  Round that up to 10 amps.
>>>
>>> Then you have to decide how long you want this thing to last without
>>> commercial power.  I would think 24 hours is a minimum.  So 10 amps x 24
>>> hours is 240 amp hours of battery.
>>>
>>> It is always a safe figure to charge a battery at .1C or 10% of its
>>> capacity or less.  That would be 24 amps to charge the batts after a power
>>> outage, plus 10 for load = 34 amps of power supply.  You could get by with
>>> 20 amps, just will take a bit longer to charge.
>>>
>>>
>>>
>>> Lots of 20 amp 28VDC power supplies out there.
>>>
>>> Rule of thumb double your load power or more to size the charger.
>>>
>>>
>>>
>>> *From:* SmarterBroadband <[email protected]>
>>>
>>> *Sent:* Wednesday, March 09, 2016 11:45 AM
>>>
>>> *To:* [email protected]
>>>
>>> *Subject:* [AFMUG] Small DC Site
>>>
>>>
>>>
>>> What are people using to power small DC sites.  Option 1 up to 150 - 200
>>> Watts, option 2 up to 300 – 400 Watts.  I’m looking for a DC UPS that can
>>> charge attached batteries.  Need to have 24 and 48 volt.
>>>
>>>
>>>
>>>
>>>
>>
>

Reply via email to