7/5=1.4 hours at full load.  

Batts are about 30 cents per watt hour for AGM, half that for flooded cells.
Inverters are about 25 cents per watt.  

7kWh battery == $1125 –$2250
5 kW inverter == $1250
Put it on your critical loads.   Charge the batts with a rectifier that is fed 
from commercial power.
You can run the inverter all the time, or use a smaller charger and put in a 
transfer switch.
Transfer switches/contactors are not very expensive.  One single relay will do 
the job.  

From: Eric Kuhnke 
Sent: Wednesday, March 23, 2016 7:45 PM
To: [email protected] 
Subject: [AFMUG] Tesla 7kWh powerwall as UPS?

$3000 is not so bad for something that can deliver up to 5kW for multiple 
hours...

http://arstechnica.com/business/2015/09/tesla-powerwall-home-installations-are-starting-for-pilot-customers/


I am interested to see the results of integrating two of these in parallel with 
an off grid solar array. At first glance it appears a great deal less expensive 
than buying a dozen 12V 200Ah lead acid AGM batteries to make a string. And 
should last a lot longer in 60% cycle depth daily cyclic use.




Interesting they've cancelled the 10kWh model ($3500) which had a much shorter 
lifespan, the 7kW model is rated at 5000 cycles. 

Reply via email to