I know Cotek makes a 1U sinewave inverter with automatic transfer switch, you would need a separate battery charger. I had trouble with the Cotek units though, the transfer switch will stay on line power if the voltage is low, plus I think I had a fan fail. Generally, everything is less reliable when crammed into a 1U size.
-----Original Message----- From: Af [mailto:[email protected]] On Behalf Of Matt Sent: Tuesday, November 29, 2016 9:03 AM To: [email protected] Subject: Re: [AFMUG] Rack Mount UPS This site has a generator already. Is there something I can have wired into the electrical panel to act as a UPS for certain outlets tell the generator starts? On Tue, Nov 22, 2016 at 5:51 PM, Jaime Solorza <[email protected]> wrote: > Doesn't Falcon make 1 and 2 U versions? > > > On Nov 22, 2016 4:44 PM, "Eric Kuhnke" <[email protected]> wrote: >> >> Never seen one. I suppose you could hack it but those things are >> 12VDC internally (composed of two flat 6V AGM cells) , so you'll be >> spending a lot of money on 0 or 2 gauge copper across the room to >> avoid significant voltage drop if you're putting batteries remote from where >> the UPS is. >> >> >> On Tue, Nov 22, 2016 at 3:36 PM, Matt <[email protected]> wrote: >>> >>> Anyone know of a 1u rack mount UPS that uses external batteries? >>> Thinking of running cord across room instead. I have limited rack >>> space. >>> >>> On Tue, Nov 22, 2016 at 4:51 PM, Matt <[email protected]> >>> wrote: >>> > Anyone know of a small wall mount UPS? I need something to hold >>> > the Ciena 3903x fiber transceiver the telco provided until the >>> > generator starts. It actually runs off a 12v wall transformer. >> >> >