Ok - so this is what I was thinking.  I thought my breakers were rated for
much more current, but it looks like they are only rated for 5A (both AC
[1] and BATT [2]).

In short - I need a breaker that can handle more current, correct?  I have
these breakers at a ton of sites.. can't believe I just noticed they were
only rated for 5A. :(  In the meantime, I may need to use an external
charger to get these batteries charged back up.

[1] http://www.alliedelec.com/altech-corp-2c5um/70076204/
[2] http://www.alliedelec.com/altech-corp-1c5um/70076445/

On Sun, May 28, 2017 at 1:36 PM, Chuck McCown <ch...@wbmfg.com> wrote:

> 360 recommends a 16 amp or greater circuit for the AC.
> And it will only make 7.5 amps.  Almost any batter discharged that much
> will take 100% of that 7.5 amps when starting to charge.  I would set the
> battery circuit breaker to be higher than 7.5 amps to prevent this
> problem.
>
> *From:* Josh Baird
> *Sent:* Sunday, May 28, 2017 11:30 AM
> *To:* af@afmug.com
> *Subject:* Re: [AFMUG] Traco TSP+BCM Question
>
> This site has about 180-200W of load.  The TSP power supply is 360W.  I
> know the BCM has about a ~55W overhead for charging, so that should still
> leave plenty of headroom, wouldn't you think?
>
> On Sun, May 28, 2017 at 1:19 PM, Bill Prince <part15...@gmail.com> wrote:
>
>> Might be as simple as your AC circuit is too small for the whole load.
>> The key questions are (1) What is the load of your equipment?, and (2) What
>> is the bulk charge load on your controller?
>>
>> Add those two together to understand what the total load should be.
>>
>>
>> bp
>> <part15sbs{at}gmail{dot}com>
>>
>>
>> On 5/28/2017 9:19 AM, Josh Baird wrote:
>>
>>> I have a site with a TSP+BCM 48V combo.  Last night, something caused
>>> the AC breaker to trip, putting the site on battery.  We didn't see the
>>> alert until about 12 hours later.  At this point, the batteries were down
>>> to ~42V.  When our guy arrived on site, he reset the AC breaker, and AC
>>> power was restored.  Immediately, the battery breaker (breaker between
>>> positive side of the batteries and the BCM) tripped.
>>>
>>> Now, each time that we reset the battery breaker, it causes the AC
>>> breaker to immediately trip.  At this point, the site is up on AC with no
>>> battery.  Any ideas what would be causing this?  Do you think the batteries
>>> are causing the BCM to draw too much current?  Could one (or more) of the
>>> batteries be dead/bad?  The site *did* run successfully on battery for
>>> nearly 12 hours.
>>>
>>> Josh
>>>
>>
>>
>