On 5/28/17 1:11 PM, Josh Baird wrote:
R Series [1] should be fine for the AC side though, right?

[1] http://www.alliedelec.com/altech-corp-2du25r/70075748/


Yes, fine for AC. You could probably use a smaller breaker in D curve since it's 100ms trip is 20 times rated current. That means a 25A breaker should take <100ms inrush of 500A without tripping.

Of course, if you pick a breaker larger than whatever is upstream feeding it then it's just an expensive switch.

~Seth