Back when I was a telco lineman, the Oregon PUC gave us the clearances and they 
would actually send out an inspector to measure them once in a while.
We had to cross all roadways at 16 feet.  We had to be below the bottom of a 
secondary drip loop by 18 inches.   Sometimes that was tough to do.  I remember 
rail road tracks were something like 26 feet.  Cannot remember the rest.  That 
was 38 years ago.  

From: Jason McKemie 
Sent: Saturday, June 24, 2017 12:57 PM
To: af@afmug.com 
Subject: Re: [AFMUG] Avoid 'make ready' by using my own poles

Code is 15'6" above most roads and driveways. It is a bit less over yards, I 
can't remember off hand. Obviously the more clearance the better.

On Saturday, June 24, 2017, <ch...@wbmfg.com> wrote:

  Well, with max truck height of 14 feet, you sure want to be above that.  

  From: Adam Moffett 
  Sent: Saturday, June 24, 2017 10:02 AM
  To: af@afmug.com 
  Subject: Re: [AFMUG] Avoid 'make ready' by using my own poles

  I just saw some about that short yesterday with telephone drop cables on 
them, so mabe.  You also have to consider the terrain changes.  Often the road 
is slightly elevated for drainage, and the line may be running down hill for 
instance.  With a 35' pole we can maintain good clearance in most 
circumstances, and it's not too expensive.

  I need to be 16 feet above state roads.  Other circumstances could allow as 
low as 14'.  So far I've given those numbers a wide margin because I don't want 
to assume that the wire won't stretch or have something leaning on it to bring 
it down.


  ------ Original Message ------
  From: "Kurt Fankhauser" <lists.wavel...@gmail.com>
  To: af@afmug.com
  Sent: 6/24/2017 10:01:22 AM
  Subject: Re: [AFMUG] Avoid 'make ready' by using my own poles

    What is minimal pole size and cost for a small pole for communications 
wire? 25 foot pole? 5 foot in ground and 20 foot above ground? That would get 
you roughly 5 feet of sag allowance between poles since I was told 15 feet is 
the lowest your wire can be to the road.

    Also is there any ROW laws that give a county/municipality the right to 
deny you an application to set another row of poles on the opposite side of the 
road from electric poles when you obviously could place more wires on the 
electric poles?

    On Sat, Jun 24, 2017 at 1:26 AM, Jason McKemie 
<j.mcke...@veloxinetbroadband.com> wrote:

      The NEC that the local power coop goes by is 40" below neutral for a 
conductive cable, and 30" for non-conductive. 


      On Friday, June 23, 2017, Chuck McCown <ch...@wbmfg.com> wrote:

        The zone around primary conductors that you have to keep out of.  Rule 
of thumb is 10 feet, but there are legal specs.  Actually secondary too but 
that is normally 12-18 inches.  

        From: Adam Moffett 
        Sent: Friday, June 23, 2017 11:43 AM
        To: af@afmug.com 
        Subject: Re: [AFMUG] Avoid 'make ready' by using my own poles

        This is going to be an ignorant question, but what is the clearance 
zone?  


        ------ Original Message ------
        From: ch...@wbmfg.com
        To: af@afmug.com
        Sent: 6/23/2017 1:16:21 PM
        Subject: Re: [AFMUG] Avoid 'make ready' by using my own poles

          You can’t force them to use your pole.
          Your pole cannot encroach on the clearance zone.

          You can always put your own poles in ROW that is clear from other 
pole lines.  
          Across the street is probably fine depending on easements.  

          You can always go underground for a span or two.  That will be less 
expensive.  

          From: Adam Moffett 
          Sent: Friday, June 23, 2017 11:09 AM
          To: af@afmug.com 
          Subject: [AFMUG] Avoid 'make ready' by using my own poles

          So, our most common make ready issue so far has been old poles that 
are relatively short and we can't stay the required distance from the power 
equipment and also be far enough above the existing phone line.  Sometimes we 
can use a standoff or other solutions to avoid the issue, but sometimes the 
pole needs to be replaced.  It's never less than $5,000, could be as much as 
$10,000.   

          What I'm wondering is this:  We can get a new 35' pole for $800.  We 
can get a new 50' pole for $1500.  Is there any reason I couldn't just avoid 
make ready expense by setting our own pole instead of using theirs?  Even with 
guy wires, permit, and easements it's almost guaranteed to be less expensive.  
Maybe I would put a 35 footer on the opposite side of the road, for example.  
Or maybe we set the new 50 footer right next to theirs and even let them move 
onto our pole if they want to.  It seems too easy and I'm wondering if there's 
a catch I'm not thinking of.


Reply via email to