Gotta make sure to zero those DC clamp on units before you use them.  Seems 
like every time I use one it takes me a bit of time to get it to measure 
correctly.  

From: George Skorup 
Sent: Thursday, January 25, 2018 9:45 AM
To: [email protected] 
Subject: Re: [AFMUG] Watts and VA on DC vs AC

Yeah. I guessed about 33 amps based on 13 volts. Could rise quite a bit as the 
battery drains, and I'd expect the inverter efficiency to drop as the battery 
voltage decreases.

I like having my handy Craftsman AC/DC clamp-on ammeter to verify my poor 
attempts at math.


On 1/25/2018 10:12 AM, [email protected] wrote:

  Your inverter is probably 90% efficient if you are lucky.

  355 watts / .9 = perhaps 433 watts input

  433/12 =37 amps input at 12 volts

  So, yeah,  your guess between 30 and 60 amps is pretty accurate.

  You can also insert 1 foot of #10 wire in series with the 12 volt line.
  Measure the voltage from one end of the wire to the other.  
  Millivolts = amps.  

  You should have about 37 milliamps volt drop across that wire.  

  From: Adam Moffett 
  Sent: Thursday, January 25, 2018 8:49 AM
  To: [email protected] 
  Subject: [AFMUG] Watts and VA on DC vs AC

  I wanted to rig up a load test for some batteries. 
  I don't have a substantial 12V DC load, so I set up a 1000W inverter, a short 
extension cord, a Kill-a-Watt meter, and a heat gun.

  With the heat gun on low, The kill-a-watt reads 110v, 606 VA, and 355W. 

  The question is how much load is this putting on the battery?  Somewhere 
between 30 and 60amp I guess, and either way my multimeter can't measure more 
than 10A DC current, so I can't measure it directly.  

  My Googling on the topic has failed to enlighten me.  My instinct is to think 
that Watts is Watts, so I should probably use 355W in my calculation of battery 
capacity, but I'm not sure.