#10 wire is cheap...
Just log the voltage drop and battery voltage for an hour or two and you can 
extrapolate the Ah.  

You can also use a spool of wire in a buck of water as a load.  500 feet of #10 
is a half ohm.  That will give you 24 amps of load on 12 volts and will also 
serve to tell you the current too.  

From: Adam Moffett 
Sent: Thursday, January 25, 2018 9:49 AM
To: af@afmug.com 
Subject: Re: [AFMUG] Watts and VA on DC vs AC

I'll have to get a better meter.

In the mean time I guess I can't say how many Ah I really get out of the 
battery, but I can see how far it depletes in a certain amount of time and say 
it's between x and y Ah.  That should be sufficient for today.


------ Original Message ------
From: "George Skorup" <george.sko...@cbcast.com>
To: af@afmug.com
Sent: 1/25/2018 11:45:24 AM
Subject: Re: [AFMUG] Watts and VA on DC vs AC

  Yeah. I guessed about 33 amps based on 13 volts. Could rise quite a bit as 
the battery drains, and I'd expect the inverter efficiency to drop as the 
battery voltage decreases.

  I like having my handy Craftsman AC/DC clamp-on ammeter to verify my poor 
attempts at math.


  On 1/25/2018 10:12 AM, ch...@wbmfg.com wrote:

    Your inverter is probably 90% efficient if you are lucky.

    355 watts / .9 = perhaps 433 watts input

    433/12 =37 amps input at 12 volts

    So, yeah,  your guess between 30 and 60 amps is pretty accurate.

    You can also insert 1 foot of #10 wire in series with the 12 volt line.
    Measure the voltage from one end of the wire to the other.  
    Millivolts = amps.  

    You should have about 37 milliamps volt drop across that wire.  

    From: Adam Moffett 
    Sent: Thursday, January 25, 2018 8:49 AM
    To: af@afmug.com 
    Subject: [AFMUG] Watts and VA on DC vs AC

    I wanted to rig up a load test for some batteries. 
    I don't have a substantial 12V DC load, so I set up a 1000W inverter, a 
short extension cord, a Kill-a-Watt meter, and a heat gun.

    With the heat gun on low, The kill-a-watt reads 110v, 606 VA, and 355W. 

    The question is how much load is this putting on the battery?  Somewhere 
between 30 and 60amp I guess, and either way my multimeter can't measure more 
than 10A DC current, so I can't measure it directly.  

    My Googling on the topic has failed to enlighten me.  My instinct is to 
think that Watts is Watts, so I should probably use 355W in my calculation of 
battery capacity, but I'm not sure.



Reply via email to