When you say you can parallel as many as you want, but then say to limit the 
load on individual units, that does not sound like all the outputs are combined 
to me.  

Do you actually combine the outputs in parallel?  

If so you really cannot limit current to individual units, the load will divide 
across the inverters based on internal and external impedances.  

From: Eric Kuhnke 
Sent: Wednesday, May 9, 2018 8:10 PM
To: af@afmug.com 
Subject: Re: [AFMUG] 48 vdc Inverteres for Data Room 6kw ?

You could also look into individual 1500W meanwell true sine wave inverters, 
running in parallel off your 48vdc battery bus. You can parallel as many as you 
need. Don't load any individual one with more than 1300W constant. Wire up the 
output from each meanwell to 120vac PDUs with amperage meter inline and 
distribute from there. 

On Tue, May 8, 2018, 12:58 PM Gino A. Villarini <g...@aeronetpr.com> wrote:

  Looking for 48 vdc inverters for data room applications in the range of 6-8 kw

  Can be a all in one system ( charger plus Inverter) , must be always online 