My post only relates to if in fact you install a ground rod at your ham 
station, that it needs and under the NEC is required to be bonded (connected) 
to your house ground.  Lets assume your house ground rod has a résistance of 22 
ohms. You pound a rod at your shack in the earth that has a resistance   10 
ohms  Lightning strikes  your power line behind your house. This high voltage 
pulse is seeking the least resistance path to earth. The house ground not the 
best, but to the lightning Gods you shack ground looks like a great path, using 
the 3rd prong of your power supply or the neutral side of the power cord, it 
seeks that ground, kind of frying any wiring or equipment in its travels. If 
both ground rods are bonded together, using ohms law, the total resistance is 
6.88 ohms, much better ground, lightning has a low resistance path to earth not 
thru your gear.  Also from a safety aspect (why the NEC requires bonding) if 
you loose a neutral connection at your power drop to your meter, or in your 
breaker box and your house ground is missing or poor, any grounded equipment in 
your house can have up to 120v on its chassis. If you were touching equipment 
in your shack the was connected to your shack ground and something grounded to 
your poor or non-existent house ground. You will be a cooking hot dog. Robert 

 

From: BVARC <bvarc-boun...@bvarc.org> On Behalf Of David Hold via BVARC
Sent: Monday, May 23, 2022 4:58 PM
To: BRAZOS VALLEY AMATEUR RADIO CLUB <bvarc@bvarc.org>
Cc: David Hold <davidh...@gmail.com>
Subject: Re: [BVARC] Ground rod

 

I will bet …. If you ohm out the negative post and chassis you will find out 
they are the same.

 If so just take negative to ground rod or wire under a chassis screw to ground.

 

On Mon, May 23, 2022 at 4:51 PM Mike Knedr via BVARC <bvarc@bvarc.org 
<mailto:bvarc@bvarc.org> > wrote:

Thank you for the information.

I have a semlex sec-1235m power supply.

It doesn't seem to have a chassis ground like the radio and the tuner does.  
Does it need to be grounded?

 

On Mon, May 23, 2022, 1:53 PM Robert Polinski via BVARC <bvarc@bvarc.org 
<mailto:bvarc@bvarc.org> > wrote:

Do not preform any electrical work unless you are comfortable as to what you 
are doing. Do not in any case ground the 3rd prong of an electrical cord to a 
ground rod that is not bonded to your electrical service. You could cause an 
electrical potential difference between ground thru your equipment or thru YOU. 
Remember, an earth ground has resistance. An electrical fault (short to chassis 
or ground) needs a low resistance path back to its source, a metal conductor, 
the earth can be a high resistance path. Low resistance will cause the 
protective device ( Breaker or fuse) to open. Robert KD5YVQ 

 

From: BVARC <bvarc-boun...@bvarc.org <mailto:bvarc-boun...@bvarc.org> > On 
Behalf Of Joseph Benoit via BVARC
Sent: Sunday, May 22, 2022 8:59 AM
To: BRAZOS VALLEY AMATEUR RADIO CLUB <bvarc@bvarc.org <mailto:bvarc@bvarc.org> >
Cc: Joseph Benoit <wa3...@gmail.com <mailto:wa3...@gmail.com> >
Subject: Re: [BVARC] Ground rod

 

Mike.  Not a direct answer to your ground rod issue BUT upon inspection, you 
will find the wire feeding the outlet boxes probably does contain a ground 
wire, just that they didn't have three-prong outlets or continue grounds 
properly

Not sure you want to tackle this BUT it is easy just time-consuming. After 
you've done a couple, maybe 15 minutes each. 

Experiment with one outlet to see if you are up to it.

Look in your breaker panel and you will see a bunch of ground wires connected 
to the ground buss so obviously they go SOMEWHERE (just not terminated at the 
outlets and switches).

Time to replace those old outlets and switches anyway.  Don't buy the cheapest 
outlets, stick to made in USA; Proven to be better connections inside.     

You can fix the issue with the no-grounded outlets throughout the house and 
make things much safer. Buy an outlet tester (a few bucks; three LED's) if you 
don't have one.  Get about 10 feet (jic) #14 solid copper wire green or 
whatever color.; stripping entirely bare if not green. Have a small assortment 
of appropriate wire nuts and electrical tape. Amazing how many three pronged 
outlets don't have any wire to ground screw although the bare ground wire is in 
there (sometimes just balled-up.  Good time to identify what breaker does what 
and to make sure that breaker is OFF before you remove the outlet or light 
switch..  By getting to each and every outlet and switch and make sure the 
ground wires that are there are all connected to each other (may be multiple 
cables in same box) connect them all together  adding a pig tail if it was cut 
too short. Add a short pigtail to the new 3-prong grounded receptacle. Also 
look at any junction boxes hiding in the attic.  Have to be patient since, in 
an older house like ours, one room may feed another room and the problem won't 
resolve until all the grounds are tied together.  One day project does the 
whole house. 

Good idea to take a wrap of tape around the receptacle or switch for safety 
(for safety and to keep that ground wire from touching where it shouldn't.  

 

On Fri, May 20, 2022 at 8:19 PM Mike Knedr via BVARC <bvarc@bvarc.org 
<mailto:bvarc@bvarc.org> > wrote:

The house was built in the 60's.

So there is no ground to the receptacles.

I was planning on building an extension cord with a gfci and running the ground 
to the rod.

I was thinking about flat braid from a ground buss bar to the rod for the 
radio, tuner, and power supply.

 

Any thoughts?

 

Mike KI5UBL 73

 

On Fri, May 20, 2022, 7:57 PM Michael Giannaccio via BVARC <bvarc@bvarc.org 
<mailto:bvarc@bvarc.org> > wrote:

Hi Mike,

When I put mine in I left about 8-12” out of the ground. Plenty of room for 
multiple clamps and coax grounding blocks.

If you’re not already aware make sure you bond your station ground with your 
home’s electrical ground. I have some wire that you’re welcome to for bonding 
if your run isn’t too long. Let me know!

73,

Mike Giannaccio
W5REZ

> On May 20, 2022, at 6:53 PM, Mike Knedr via BVARC <bvarc@bvarc.org 
> <mailto:bvarc@bvarc.org> > wrote:
> 
> 
> I'm am installing an eight foot ground rod for my new shack.
> My question is how much leave above ground to attach the grounds.
> ________________________________________________
> Brazos Valley Amateur Radio Club
> 
> BVARC mailing list
> BVARC@bvarc.org <mailto:BVARC@bvarc.org> 
> http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
> Publicly available archives are available here: 
> https://www.mail-archive.com/bvarc@bvarc.org/ 


________________________________________________
Brazos Valley Amateur Radio Club

BVARC mailing list
BVARC@bvarc.org <mailto:BVARC@bvarc.org> 
http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
Publicly available archives are available here: 
https://www.mail-archive.com/bvarc@bvarc.org/ 

________________________________________________
Brazos Valley Amateur Radio Club

BVARC mailing list
BVARC@bvarc.org <mailto:BVARC@bvarc.org> 
http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
Publicly available archives are available here: 
https://www.mail-archive.com/bvarc@bvarc.org/ 

________________________________________________
Brazos Valley Amateur Radio Club

BVARC mailing list
BVARC@bvarc.org <mailto:BVARC@bvarc.org> 
http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
Publicly available archives are available here: 
https://www.mail-archive.com/bvarc@bvarc.org/ 

________________________________________________
Brazos Valley Amateur Radio Club

BVARC mailing list
BVARC@bvarc.org <mailto:BVARC@bvarc.org> 
http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
Publicly available archives are available here: 
https://www.mail-archive.com/bvarc@bvarc.org/ 

-- 

David Hold david.h...@gmail.com <mailto:david.h...@gmail.com> 

________________________________________________
Brazos Valley Amateur Radio Club

BVARC mailing list
BVARC@bvarc.org
http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
Publicly available archives are available here: 
https://www.mail-archive.com/bvarc@bvarc.org/ 