Interesting topic considering it does reduce down to connecting three wires
more or less. The executive overview is that hopefully the inverter, circuit 
breaker
panel and GFCI will come with good instructions on how they need to be wired.

At least some of the GFCI are recommended for use in two wire only retrofits.
The requirement is that somewhere at the power source there is a ground.
These units may come with a sticker saying "non grounded outlet". The test
button still works since it jumpers over the sensing circuitry from hot to
neutral, no EGC required.

Maybe this will explain it a lot better:

https://www.nema.org/Products/Documents/NEMA-GFCI-2012-Field-Representative-Presentation.pdf

Check out page 14.

A point I was commenting on was that even with a correctly wired AC system, EGC 
and earth ground
bonded together at the correct location and everything to spec a person can 
still get electrocuted.
It is a safety requirement though more so to help the utility with lightning 
strikes and to ensure the
OCPD ( circuit breaker ) trips if a load shorts out. Tongue in cheek was the 
comment that the ground
path is likely the current return if a person gets a shock. If there is a 
problem with the earth ground
even a GFCI may not help. In a marina or club if all the grounds are correctly 
tied together a persons
safety is dependent on the quality of the worst installation using shore power.

Michael Brown
Windburn
C&C 30-1


From: Josh Muckley <muckl...@gmail.com> 

"So if the inverter is floating and has no ground you cannot get a ground 
fault shock. If there is a ground wired in you could get a shock but the 
GFCI should trip. Maybe having the GFCI in is a good thing in that if there 
was a defect in the load you would never know it without a ground. With 
it the GFCI would keep tripping letting you know something is wrong." 
 
Michael, As you stated the GFCI is comparing the current on both the hot 
and neutral.  When a difference is sensed it trips the GFCI.  You mentioned 
that without a ground the GFCI won't trip.  2 thoughts come to mind. 
First, without a ground, the GFCI won't trip during a "test".  The 
pushbutton connects a high resistance to the ground prong creating a leak 
path for current so in that case you're completely right the GFCI won't 
trip.  Second, the GFCI is still sensitive to a difference in current 
between hot and neutral.  You can wire a GFCI ungrounded and it will still 
trip during a fault.  You need a leak path.  Most GFCI outlets are 
sensitive to 5mA.  The idea that the inverter is using an ungrounded system 
and as a result, you won't trip the GFCI sounds synonymous with the idea 
that since I'm wearing rubber shoes, standing on carpet, in a wood frame 
house I won't get shocked by the hot.  I can tell you from experience, you 
will get shocked! 
 
All of this discussion about floating AC actually gets me thinking about 
whether or not the GFCI outlet has a disconnect on both the hot and neutral 
lines.  Even if the GFCI trips the neutral prong may still be connected to 
the neutral wire which in a home isn't a problem, but with a floating AC 
system you could still be exposed to voltage.  We had problems similar to 
this while on Navy ships.  The crew had bought generic computer surge 
protectors which all needed replaced with high dollar ones since the 
generic ones only protect the hot terminal. 
 
Josh Muckley 
S/V Sea Hawk 
1989 C&C 37+ 
Solomons, MD 
 

 

 

_______________________________________________

This list is supported by the generous donations of our members. If you wish to 
make a contribution to offset our costs, please go to:  
https://www.paypal.me/stumurray

All Contributions are greatly appreciated!