Hi Cris:

It’s been a while, but a long time ago I wrote an Ethernet/IP driver for 
Allen-Bradley’s ControlLogix PLC.  So I might be able to help a little.  I’m 
trying to find the code, so I can donate it or at least let you look at it if 
you’d like (I wrote the code while operating my company which is now 10 years 
defunct).

Some answers below...

> On Aug 20, 2018, at 10:05 AM, Christofer Dutz <[email protected]> 
> wrote:
> 
> Hi all,
> 
> I’m currently working hard on the EtherNet/IP protocol and am pretty 
> unfamiliar with it.
> Especially when it comes to the structure. As I want to build the EtherNet/IP 
> support as simple as possible it would be great if someone here could 
> eventually answer some of my questions.
> 
> Questions like this one:
> 
> 
>  *   There seem to be different ways in which information can be read. Which 
> option would be the best for our usecases?

First, be aware that Ethernet/IP is really an encapsulation of the CIP (Control 
and Information) Protocol from DeviceNet that runs over Ethernet.  So you want 
to get familiar with the CIP documentation that is available at ODVA (back when 
I looked into it, I had to join as a personal member; you might want to see if 
they will let Apache join as a foundation).

There are "explicit messaging" and “I/O” connections.  Explicit messaging (also 
called “Unconnected Messages”) is a request/response exchange.  You ask a 
device a question (“What is the value of x”) and it returns an answer.  I/O 
connections are more like subscriptions.  You setup a connection between two 
devices, and then the device sends data at some interval.

On ethernet, the Explicit Messaging runs over TCP/IP, whereas the I/O data is 
sent as UDP once the connection is set up.

In my case, I never bothered to figure out I/O messaging; the unconnected 
messaging was fast enough for what I was trying to do on the ControlLogix.

>  *   Which are the options that exist on every EtherNet/IP compliant device?

The spec defines “object types” (46 in my copy of the spec) that may be 
present, but the only ones that are required for all modules are
- Connection object or connection manager
- Network specific link object
- Identity Object Class
- Message Router Object Class

>  *   Can someone explain why for our test WAGO device I have to read the 
> values of the digital input, by reading #4(assembly 
> class)#105(instance)#3(attribute)

An assembly is a collection of data.  The device profile can define a “static 
assembly” that is specific to that device.  Assemblies numbered 0-0x63 are open 
static, defined by the device profile.  Higher numbers are vendor-defined and 
dynamic assemblies.  So that device must define some meaning for that assembly 
instance.  Not sure what the ‘3’ means offhand.

> 
> Would be great, if you could help me a little.
> 
> Chris

Cheers,