Hi Greg,

as you seem to have experience with EtherNet/IP ... could you eventually have a 
look at what I'm doing in the feature/etherenet-ip branch?

Here the "ManualPlc4XEtherNetIpTest" class is an example where I connect to a 
eip device with the connection String: 

eip://10.10.64.30:44818 

and try to read the address: 

#4#105#3

Where: #4#105#3 means (Class number 4), (Instance number 105) and (Attribute 
number 3)

The Web-UI of the device tells me the instance numbers and the convention tells 
me #4 is the assembly object. I got the attribute #3 from an EIP Explorer tool 
I used to generally connect to the device in the first place (I used this to 
capture the traffic with Wireshark and compare that to what I've been doing).

Does this Address Format make sense? Is there a publicly accepted convention to 
writing down EIP Addresses?
Is the "attribute # 3" also a convention?

Chris





Am 21.08.18, 02:50 schrieb "Greg Trasuk" <[email protected]>:

    Hi Cris:
    
    It’s been a while, but a long time ago I wrote an Ethernet/IP driver for 
Allen-Bradley’s ControlLogix PLC.  So I might be able to help a little.  I’m 
trying to find the code, so I can donate it or at least let you look at it if 
you’d like (I wrote the code while operating my company which is now 10 years 
defunct).
    
    Some answers below...
    
    > On Aug 20, 2018, at 10:05 AM, Christofer Dutz <[email protected]> 
wrote:
    > 
    > Hi all,
    > 
    > I’m currently working hard on the EtherNet/IP protocol and am pretty 
unfamiliar with it.
    > Especially when it comes to the structure. As I want to build the 
EtherNet/IP support as simple as possible it would be great if someone here 
could eventually answer some of my questions.
    > 
    > Questions like this one:
    > 
    > 
    >  *   There seem to be different ways in which information can be read. 
Which option would be the best for our usecases?
    
    First, be aware that Ethernet/IP is really an encapsulation of the CIP 
(Control and Information) Protocol from DeviceNet that runs over Ethernet.  So 
you want to get familiar with the CIP documentation that is available at ODVA 
(back when I looked into it, I had to join as a personal member; you might want 
to see if they will let Apache join as a foundation).
    
    There are "explicit messaging" and “I/O” connections.  Explicit messaging 
(also called “Unconnected Messages”) is a request/response exchange.  You ask a 
device a question (“What is the value of x”) and it returns an answer.  I/O 
connections are more like subscriptions.  You setup a connection between two 
devices, and then the device sends data at some interval.
    
    On ethernet, the Explicit Messaging runs over TCP/IP, whereas the I/O data 
is sent as UDP once the connection is set up.
    
    In my case, I never bothered to figure out I/O messaging; the unconnected 
messaging was fast enough for what I was trying to do on the ControlLogix.
    
    >  *   Which are the options that exist on every EtherNet/IP compliant 
device?
    
    The spec defines “object types” (46 in my copy of the spec) that may be 
present, but the only ones that are required for all modules are
    - Connection object or connection manager
    - Network specific link object
    - Identity Object Class
    - Message Router Object Class
    
    >  *   Can someone explain why for our test WAGO device I have to read the 
values of the digital input, by reading #4(assembly 
class)#105(instance)#3(attribute)
    
    An assembly is a collection of data.  The device profile can define a 
“static assembly” that is specific to that device.  Assemblies numbered 0-0x63 
are open static, defined by the device profile.  Higher numbers are 
vendor-defined and dynamic assemblies.  So that device must define some meaning 
for that assembly instance.  Not sure what the ‘3’ means offhand.
    
    > 
    > Would be great, if you could help me a little.
    > 
    > Chris
    
    Cheers,
    
    Greg Trasuk
    
    