Did you post your code somewhere? I cant find it.. just post it somewhere and I 
will have a look!

Julian

Am 18.02.20, 11:28 schrieb "Etienne Robinet" <[email protected]>:

    Hi Julian,
    thanks for the advice, but where should I change the code to apply your 
modification? Is it in the doStart() methode of de PLC4XConsumer?
    Regards,
    
    Etienne
    
    On 2020/02/18 08:55:22, Julian Feinauer <[email protected]> 
wrote: 
    > Hi Etienne,
    > 
    > thank you for your investigation.
    > I just locked at your log and it seems that connection works fine and 
some messages are exchanged BUT you try to subscribe to a Value which is 
currently not supported.
    > Try to just use the "readRequestBuilder().addItem("", 
"").build().execute().get()" approach to send a single request, that should 
work.
    > 
    > Best
    > Julian
    > 
    > Am 18.02.20, 09:39 schrieb "Etienne Robinet" <[email protected]>:
    > 
    >     Hello,
    >     with the help of some colleague we managed to find how to fix the 
issue so that the DriverManager can find the actual s7 protocol.
    >     All I had to do is to create a maven project (karaf-blueprint) 
archetype and do as follow:
    >     
    >     1. Inside the pom, add the S7PlcDriver under "imports"
    >     2. create a service under 
main/java/resources/META-INF/services/xxx.xxx.PlcDriver containing the 
implementation (S7PlcDriver) and license
    >     3. Create a simple XML blueprint (with a real address this time 
connected to a real PLC)
    >     <blueprint xmlns="http://www.osgi.org/xmlns/blueprint/v1.0.0"; 
default-activation="lazy">
    >     
    >         <camelContext id="PLC-Context" 
xmlns="http://camel.apache.org/schema/blueprint"; streamCache="true">
    >     
    >     
    >             <route id="Route1">
    >     
    >                 <from uri="plc4x:s7://192.168.178.10/1/1"/>
    >                 <log message=" Sending ${body}" loggingLevel="INFO" />
    >                 <to uri="mock:test?retainLast=10" />
    >     
    >             </route>
    >     
    >         </camelContext>
    >     
    >     </blueprint>
    >     
    >     So now I have the next issue, I can see from the log that a 
connection is established but it tells me that the connection doesn't support 
connection. Am I missing a parameter or what could be the issue?
    >     
    >     Here the log:
    >     
    >     https://i.imgur.com/KgWz8DF.png
    >     
    >     On 2020/02/17 12:11:56, Christofer Dutz <[email protected]> 
wrote: 
    >     > Hi all,
    >     > 
    >     > having a more detailed look at the log-trace, it seems the 
DriverManager isn't able to find the S7 driver at all ...
    >     > But I guess if it even was available, as Cesar pointed out, the 
field address is that of the mock driver and not of the S7 so this will not 
work.
    >     > Also are you connecting to localhost, which is also probably not 
what you want. Unless you are running a S7 simulator on your machine.
    >     > 
    >     > Depending of if you're using a released version of the s7 driver 
the connection URL is correct, however if you switch to the new S7 driver it 
would look like this:  s7://{ip or host}
    >     > Not the "/1/1" are now missing.
    >     > 
    >     > Chris
    >     > 
    >     > 
    >     > 
    >     > 
    >     > Am 17.02.20, 13:04 schrieb "Cesar Garcia" 
<[email protected]>:
    >     > 
    >     >     Hi,
    >     >     
    >     >     The PLC address does not look correct, can you confirm that it 
really
    >     >     points to a real PLC or an S7 simulator?
    >     >     
    >     >     <from uri="plc4x:s7:localhost/1/1"/>
    >     >     
    >     >     Best regards,
    >     >     
    >     >     
    >     >     El vie., 14 feb. 2020 a las 18:34, Etienne Robinet 
(<[email protected]>)
    >     >     escribió:
    >     >     
    >     >     > Hello everyone,
    >     >     > I've spent some days trying to figure out how to make PLC4X 
work inside a
    >     >     > karaf container in combination with camel blueprints for 
routing.
    >     >     > I've downloaded the latest release (0.5.0) and built it with 
maven. I then
    >     >     > installed the driver-s7-feature and plc4j-apache-camel bundle 
into my
    >     >     > container and got following bundles running:
    >     >     >
    >     >     > >PLC4J: API
    >     >     > >PLC4J: Driver: S7
    >     >     > >PLC4J: Protocol: Driver-Base: Base
    >     >     > >PLC4J: Protocol: Driver-Base: TCP
    >     >     > >PLC4J: Protocol: ISO on TCP
    >     >     > >PLC4J: Protocol: ISO TP
    >     >     > >PLC4J: Protocol: S7
    >     >     > >PLC4j: Utils: Driver Base: Java
    >     >     > >PLC4J: Integrations: Apache Camel
    >     >     >
    >     >     > After trying a simple route with this consumer component:
    >     >     > <from uri="plc4x:s7:localhost/1/1"/> (the address is for 
testing purpose)
    >     >     > I get the following error:
    >     >     > Error occurred during starting CamelContext: PLC-Context
    >     >     > org.apache.camel.FailedToCreateRouteException: Failed to 
create route
    >     >     > Route1: Route(Route1)[[From[plc4x:s7:localhost/1/1]] -> 
[To[mock:tes...
    >     >     > because of Unable to find driver for protocol 's7'
    >     >     >
    >     >     > I've tested numerous version of PLC4X and got the same 
results, so I think
    >     >     > I might be close to fix it!
    >     >     > Any help would be appreciated!
    >     >     >
    >     >     > Here the full log
    >     >     >
    >     >     > 16:30:45.578 INFO [Blueprint Event Dispatcher: 1] Attempting 
to start
    >     >     > CamelContext: PLC-Context
    >     >     > 16:30:45.579 INFO [Blueprint Event Dispatcher: 1] Apache 
Camel 2.24.2
    >     >     > (CamelContext: PLC-Context) is starting
    >     >     > 16:30:45.580 INFO [Blueprint Event Dispatcher: 1] 
StreamCaching is enabled
    >     >     > on CamelContext: PLC-Context
    >     >     > 16:30:45.580 INFO [Blueprint Event Dispatcher: 1] JMX is 
enabled
    >     >     > 16:30:45.600 INFO [Blueprint Event Dispatcher: 1] 
Instantiating new PLC
    >     >     > Driver Manager with class loader
    >     >     > BundleDelegatingClassLoader(plc4j-route.xml [67])
    >     >     > 16:30:45.600 INFO [Blueprint Event Dispatcher: 1] Registering 
available
    >     >     > drivers...
    >     >     > 16:30:45.601 TRACE [Blueprint Event Dispatcher: 1] 
FindResource:
    >     >     > META-INF/services/org.apache.plc4x.java.spi.PlcDriver
    >     >     > 16:30:45.627 INFO [Blueprint Event Dispatcher: 1] 
StreamCaching in use
    >     >     > with spool directory:
    >     >     > 
C:\karaf\bin\..\data\tmp\camel\camel-tmp-00f849ac-0ccf-4b12-822d-dda62267eb6c
    >     >     > and rules: [Spool > 128K body size]
    >     >     > 16:30:45.629 INFO [Blueprint Event Dispatcher: 1] Apache 
Camel 2.24.2
    >     >     > (CamelContext: PLC-Context) is shutting down
    >     >     > 16:30:45.639 INFO [Blueprint Event Dispatcher: 1] Apache 
Camel 2.24.2
    >     >     > (CamelContext: PLC-Context) uptime 0.060 seconds
    >     >     > 16:30:45.640 INFO [Blueprint Event Dispatcher: 1] Apache 
Camel 2.24.2
    >     >     > (CamelContext: PLC-Context) is shutdown in 0.011 seconds
    >     >     > 16:30:45.640 WARN [Blueprint Event Dispatcher: 1] Changing 
Camel state for
    >     >     > bundle 67 to Failure
    >     >     > 16:30:45.641 ERROR [Blueprint Event Dispatcher: 1] Error 
occurred during
    >     >     > starting CamelContext: PLC-Context
    >     >     > org.apache.camel.FailedToCreateRouteException: Failed to 
create route
    >     >     > Route1: Route(Route1)[[From[plc4x:s7:localhost/1/1]] -> 
[To[mock:tes...
    >     >     > because of Unable to find driver for protocol 's7'
    >     >     >         at
    >     >     > 
org.apache.camel.impl.RouteService.warmUp(RouteService.java:147)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.DefaultCamelContext.doWarmUpRoutes(DefaultCamelContext.java:3954)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.DefaultCamelContext.safelyStartRouteServices(DefaultCamelContext.java:3861)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.DefaultCamelContext.doStartOrResumeRoutes(DefaultCamelContext.java:3647)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.DefaultCamelContext.doStartCamel(DefaultCamelContext.java:3488)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.DefaultCamelContext$4.call(DefaultCamelContext.java:3247)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.DefaultCamelContext$4.call(DefaultCamelContext.java:3243)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.DefaultCamelContext.doWithDefinedClassLoader(DefaultCamelContext.java:3266)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.DefaultCamelContext.doStart(DefaultCamelContext.java:3243)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.support.ServiceSupport.start(ServiceSupport.java:72)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.DefaultCamelContext.start(DefaultCamelContext.java:3159)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.blueprint.BlueprintCamelContext.start(BlueprintCamelContext.java:255)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.blueprint.BlueprintCamelContext.maybeStart(BlueprintCamelContext.java:297)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.blueprint.BlueprintCamelContext.blueprintEvent(BlueprintCamelContext.java:188)
    >     >     > [!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.aries.blueprint.container.BlueprintEventDispatcher$3.call(BlueprintEventDispatcher.java:190)
    >     >     > [!/:1.10.2]
    >     >     >         at
    >     >     > 
org.apache.aries.blueprint.container.BlueprintEventDispatcher$3.call(BlueprintEventDispatcher.java:188)
    >     >     > [!/:1.10.2]
    >     >     >         at 
java.util.concurrent.FutureTask.run(FutureTask.java:264) [?:?]
    >     >     >         at
    >     >     > 
java.util.concurrent.Executors$RunnableAdapter.call(Executors.java:515)
    >     >     > [?:?]
    >     >     >         at 
java.util.concurrent.FutureTask.run(FutureTask.java:264) [?:?]
    >     >     >         at
    >     >     > 
java.util.concurrent.Executors$RunnableAdapter.call(Executors.java:515)
    >     >     > [?:?]
    >     >     >         at 
java.util.concurrent.FutureTask.run(FutureTask.java:264) [?:?]
    >     >     >         at
    >     >     > 
java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.run(ScheduledThreadPoolExecutor.java:304)
    >     >     > [?:?]
    >     >     >         at
    >     >     > 
java.util.concurrent.ThreadPoolExecutor.runWorker(ThreadPoolExecutor.java:1128)
    >     >     > [?:?]
    >     >     >         at
    >     >     > 
java.util.concurrent.ThreadPoolExecutor$Worker.run(ThreadPoolExecutor.java:628)
    >     >     > [?:?]
    >     >     >         at java.lang.Thread.run(Thread.java:834) [?:?]
    >     >     > Caused by: 
org.apache.plc4x.java.api.exceptions.PlcConnectionException:
    >     >     > Unable to find driver for protocol 's7'
    >     >     >         at
    >     >     > 
org.apache.plc4x.java.PlcDriverManager.getDriver(PlcDriverManager.java:98)
    >     >     > ~[?:?]
    >     >     >         at
    >     >     > 
org.apache.plc4x.java.PlcDriverManager.getConnection(PlcDriverManager.java:71)
    >     >     > ~[?:?]
    >     >     >         at
    >     >     > 
org.apache.plc4x.camel.Plc4XConsumer.<init>(Plc4XConsumer.java:57) ~[?:?]
    >     >     >         at
    >     >     > 
org.apache.plc4x.camel.Plc4XEndpoint.createConsumer(Plc4XEndpoint.java:72)
    >     >     > ~[?:?]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.EventDrivenConsumerRoute.addServices(EventDrivenConsumerRoute.java:69)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.DefaultRoute.onStartingServices(DefaultRoute.java:107)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.RouteService.doWarmUp(RouteService.java:172)
    >     >     > ~[!/:2.24.2]
    >     >     >         at
    >     >     > 
org.apache.camel.impl.RouteService.warmUp(RouteService.java:145)
    >     >     > ~[!/:2.24.2]
    >     >     >         ... 24 more
    >     >     >
    >     >     >
    >     >     >
    >     >     
    >     >     -- 
    >     >     *CEOS Automatización, C.A.*
    >     >     *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
    >     >     *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
    >     >     