Hi all,
quick update, it worked on Camel inside Karaf with Julian's code. I managed to 
read from output, memento and datablock wit hthe correct adress input:

<from uri="plc4x:s7://192.168.178.10/0/1?address=%25DB1:4.0:STRING"/>
-"%25" gets encoded as "%" in XML
-I fetch in the DB1 at byte 4 starting at his bit 0 and the data I want is a 
STRING.
-To read a memento, this also worked: address+%25MW102:INT

Now I am going to investigate the polling consumer, as I want to fetch the data 
from the PLC at a polling interval.

Etienne
On 2020/02/18 16:49:31, Etienne Robinet <[email protected]> wrote: 
> I managed to get the tool working. By that I mean I got to to a read on my 
> PLC, but seems like the connection is crashing afterwards.
> 17:46:56.556 [main] INFO  o.apache.plc4x.java.PlcDriverManager - 
> Instantiating new PLC Driver Manager with class loader 
> jdk.internal.loader.ClassLoaders$AppClassLoader@78308db1
> 17:46:56.563 [main] INFO  o.apache.plc4x.java.PlcDriverManager - Registering 
> available drivers...
> 17:46:56.579 [main] INFO  o.apache.plc4x.java.PlcDriverManager - Registering 
> driver for Protocol s7 (Siemens S7 (Basic))
> 17:46:56.588 [main] INFO  o.apache.plc4x.java.PlcDriverManager - Registering 
> driver for Protocol ab-eth (Allen Bradley ETH)
> 17:46:56.628 [main] INFO  o.apache.plc4x.java.PlcDriverManager - Registering 
> driver for Protocol ads (Beckhoff Twincat ADS)
> 17:46:56.638 [main] INFO  o.apache.plc4x.java.PlcDriverManager - Registering 
> driver for Protocol eip (EtherNet/IP (TCP))
> 17:46:56.655 [main] INFO  o.apache.plc4x.java.PlcDriverManager - Registering 
> driver for Protocol modbus (Modbus (TCP / Serial))
> 17:46:56.723 [main] INFO  o.apache.plc4x.java.PlcDriverManager - Registering 
> driver for Protocol opcua (OPC UA (TCP))
> 17:46:56.736 [main] INFO  o.apache.plc4x.java.PlcDriverManager - Registering 
> driver for Protocol test (PLC4X Test Protocol)
> 17:46:57.059 [main] INFO  o.a.p.j.s.connection.S7PlcConnection - Setting up 
> S7 Connection with: host-name 192.168.178.10, rack 0, slot 1, pdu-size 1024, 
> max-amq-caller 8, max-amq-callee 8
> 17:46:58.758 [nioEventLoopGroup-2-1] INFO  o.a.plc4x.java.s7.netty.S7Protocol 
> - S7Connection established pdu-size 960, max-amq-caller 3, max-amq-callee 3
> 17:46:58.776 [nioEventLoopGroup-2-1] INFO  o.a.plc4x.java.s7.netty.S7Protocol 
> - Successfully connected to S7: S7_1500 wit PDU 960
> 17:46:58.800 [main] INFO  o.a.p.j.e.helloplc4x.HelloPlc4x - Synchronous 
> request ...
> 17:46:58.836 [main] INFO  o.a.p.j.e.helloplc4x.HelloPlc4x - Value[value-0]: 
> true
> 17:46:58.836 [main] INFO  o.a.p.j.e.helloplc4x.HelloPlc4x - Asynchronous 
> request ...
> 17:46:58.838 [nioEventLoopGroup-2-1] INFO  o.a.p.j.e.helloplc4x.HelloPlc4x - 
> Value[value-0]: true
> 17:46:58.844 [nioEventLoopGroup-2-1] WARN  i.n.channel.DefaultChannelPipeline 
> - An exceptionCaught() event was fired, and it reached at the tail of the 
> pipeline. It usually means the last handler in the pipeline did not handle 
> the exception.
> java.io.IOException: An existing connection was forcibly closed by the remote 
> host
>       at java.base/sun.nio.ch.SocketDispatcher.read0(Native Method)
>       at java.base/sun.nio.ch.SocketDispatcher.read(SocketDispatcher.java:43)
>       at java.base/sun.nio.ch.IOUtil.readIntoNativeBuffer(IOUtil.java:276)
>       at java.base/sun.nio.ch.IOUtil.read(IOUtil.java:233)
>       at java.base/sun.nio.ch.IOUtil.read(IOUtil.java:223)
>       at 
> java.base/sun.nio.ch.SocketChannelImpl.read(SocketChannelImpl.java:358)
>       at io.netty.buffer.PooledByteBuf.setBytes(PooledByteBuf.java:247)
>       at io.netty.buffer.AbstractByteBuf.writeBytes(AbstractByteBuf.java:1140)
>       at 
> io.netty.channel.socket.nio.NioSocketChannel.doReadBytes(NioSocketChannel.java:347)
>       at 
> io.netty.channel.nio.AbstractNioByteChannel$NioByteUnsafe.read(AbstractNioByteChannel.java:148)
>       at 
> io.netty.channel.nio.NioEventLoop.processSelectedKey(NioEventLoop.java:697)
>       at 
> io.netty.channel.nio.NioEventLoop.processSelectedKeysOptimized(NioEventLoop.java:632)
>       at 
> io.netty.channel.nio.NioEventLoop.processSelectedKeys(NioEventLoop.java:549)
>       at io.netty.channel.nio.NioEventLoop.run(NioEventLoop.java:511)
>       at 
> io.netty.util.concurrent.SingleThreadEventExecutor$5.run(SingleThreadEventExecutor.java:918)
>       at 
> io.netty.util.internal.ThreadExecutorMap$2.run(ThreadExecutorMap.java:74)
>       at 
> io.netty.util.concurrent.FastThreadLocalRunnable.run(FastThreadLocalRunnable.java:30)
>       at java.base/java.lang.Thread.run(Thread.java:834)
> Disconnected from the target VM, address: '127.0.0.1:61672', transport: 
> 'socket'
> 
> Process finished with exit code 0
> 
> This did the trick: I had o also enable PUT/GET on my PLC (via TIA Portal).
> Etienne
> On 2020/02/18 14:08:11, Etienne Robinet <[email protected]> wrote: 
> > Hi, I tried the HelloPLC4X Tool, but it seems like he gets stuck. I'm still 
> > not sure about the arguments I am passing, here's the log 
> > 
> > 15:05:42.838 [main] INFO  o.apache.plc4x.java.PlcDriverManager - 
> > Instantiating new PLC Driver Manager with class loader 
> > jdk.internal.loader.ClassLoaders$AppClassLoader@78308db1
> > 15:05:42.874 [main] INFO  o.apache.plc4x.java.PlcDriverManager - 
> > Registering available drivers...
> > 15:05:42.892 [main] INFO  o.apache.plc4x.java.PlcDriverManager - 
> > Registering driver for Protocol s7 (Siemens S7 (Basic))
> > 15:05:42.899 [main] INFO  o.apache.plc4x.java.PlcDriverManager - 
> > Registering driver for Protocol ab-eth (Allen Bradley ETH)
> > 15:05:42.933 [main] INFO  o.apache.plc4x.java.PlcDriverManager - 
> > Registering driver for Protocol ads (Beckhoff Twincat ADS)
> > 15:05:42.941 [main] INFO  o.apache.plc4x.java.PlcDriverManager - 
> > Registering driver for Protocol eip (EtherNet/IP (TCP))
> > 15:05:42.956 [main] INFO  o.apache.plc4x.java.PlcDriverManager - 
> > Registering driver for Protocol modbus (Modbus (TCP / Serial))
> > 15:05:42.980 [main] INFO  o.apache.plc4x.java.PlcDriverManager - 
> > Registering driver for Protocol opcua (OPC UA (TCP))
> > 15:05:43.018 [main] INFO  o.apache.plc4x.java.PlcDriverManager - 
> > Registering driver for Protocol test (PLC4X Test Protocol)
> > 15:05:43.553 [main] INFO  o.a.p.j.s.connection.S7PlcConnection - Setting up 
> > S7 Connection with: host-name 192.168.178.10, rack 0, slot 1, pdu-size 
> > 1024, max-amq-caller 8, max-amq-callee 8
> > 15:05:45.281 [nioEventLoopGroup-2-1] INFO  
> > o.a.plc4x.java.s7.netty.S7Protocol - S7Connection established pdu-size 960, 
> > max-amq-caller 3, max-amq-callee 3
> > 15:05:45.299 [nioEventLoopGroup-2-1] INFO  
> > o.a.plc4x.java.s7.netty.S7Protocol - Successfully connected to S7: S7_1500 
> > wit PDU 960
> > 15:05:45.321 [main] INFO  o.a.p.j.e.helloplc4x.HelloPlc4x - Synchronous 
> > request ... <-----STUCKED
> > 
> > 
> > And here are the arguments I am passing:
> > --connection-string s7://192.168.178.10/0/1 --field-addresses 
> > %DB2:1.0:INT[1]
> > 
> > I also subscribed to the list ;-)
> > 
> > On 2020/02/18 13:28:24, Julian Feinauer <[email protected]> 
> > wrote: 
> > > Hi Etienne,
> > > 
> > > first, you should try to just access it with the HelloPlc4X Tool, just to 
> > > check that everything works.
> > > And Second, please subscribe to the mailing list, otherwise all your 
> > > mails have to go through moderation : )
> > > 
> > > Julian
> > > 
> > > Am 18.02.20, 14:22 schrieb "Etienne Robinet" <[email protected]>:
> > > 
> > >     Hi Julian, thanks for the fast reply!
> > >     
> > >     The route seems to be started, but I try to put the body in log (to 
> > > check) but with no sucess. Here is what I get with your code
> > >     
> > >     https://i.imgur.com/biB9ZpW.png
> > >     
> > >     After checking the code a bit, I tried to adapt my route. I am trying 
> > > to access a DB (number 2) on my PLC which has a String(Hello) and an 
> > > Int(5). I then try to show the body of the component on the log to 
> > > verify. Maybe my syntax of uri is again not correct?
> > >     
> > >     <from 
> > > uri="plc4x:s7://192.168.178.10/0/1?address=%25DB2:2.0:STRING[1]&dataType=java.lang.String"/>
> > >                 <log message=" Sending ${body}" loggingLevel="INFO" />
> > >                 <to uri="mock:test?retainLast=10" />
> > >     
> > >     On 2020/02/18 12:28:53, Julian Feinauer 
> > > <[email protected]> wrote: 
> > >     > Hi Etienne,
> > >     > 
> > >     > fort he sake of easiness... could you do a short test if it works, 
> > > when you Replace the Content of PLC4XConsumer.java with the following:
> > >     > 
> > >     > ```
> > >     > /*
> > >     >  Licensed to the Apache Software Foundation (ASF) under one
> > >     >  or more contributor license agreements.  See the NOTICE file
> > >     >  distributed with this work for additional information
> > >     >  regarding copyright ownership.  The ASF licenses this file
> > >     >  to you under the Apache License, Version 2.0 (the
> > >     >  "License"); you may not use this file except in compliance
> > >     >  with the License.  You may obtain a copy of the License at
> > >     > 
> > >     >    http://www.apache.org/licenses/LICENSE-2.0
> > >     > 
> > >     >  Unless required by applicable law or agreed to in writing,
> > >     >  software distributed under the License is distributed on an
> > >     >  "AS IS" BASIS, WITHOUT WARRANTIES OR CONDITIONS OF ANY
> > >     >  KIND, either express or implied.  See the License for the
> > >     >  specific language governing permissions and limitations
> > >     >  under the License.
> > >     >  */
> > >     > package org.apache.plc4x.camel;
> > >     > 
> > >     > import org.apache.camel.*;
> > >     > import org.apache.camel.spi.ExceptionHandler;
> > >     > import org.apache.camel.support.LoggingExceptionHandler;
> > >     > import org.apache.camel.support.ServiceSupport;
> > >     > import org.apache.camel.util.AsyncProcessorConverterHelper;
> > >     > import org.apache.plc4x.java.api.PlcConnection;
> > >     > import org.apache.plc4x.java.api.exceptions.PlcException;
> > >     > import org.apache.plc4x.java.api.messages.PlcSubscriptionResponse;
> > >     > import org.apache.plc4x.java.api.messages.PlcUnsubscriptionRequest;
> > >     > import org.apache.plc4x.java.api.messages.PlcUnsubscriptionResponse;
> > >     > import org.slf4j.Logger;
> > >     > import org.slf4j.LoggerFactory;
> > >     > 
> > >     > import java.util.Collection;
> > >     > import java.util.concurrent.*;
> > >     > 
> > >     > public class Plc4XConsumer extends ServiceSupport implements 
> > > Consumer {
> > >     >     private static final Logger LOGGER = 
> > > LoggerFactory.getLogger(Plc4XConsumer.class);
> > >     > 
> > >     >     private Plc4XEndpoint endpoint;
> > >     >     private AsyncProcessor processor;
> > >     >     private ExceptionHandler exceptionHandler;
> > >     >     private PlcConnection plcConnection;
> > >     >     private String fieldQuery;
> > >     >     private Class<?> dataType;
> > >     >     private PlcSubscriptionResponse subscriptionResponse;
> > >     > 
> > >     >     private ScheduledExecutorService executorService = 
> > > Executors.newSingleThreadScheduledExecutor();
> > >     >     private ScheduledFuture<?> future;
> > >     > 
> > >     >     public Plc4XConsumer(Plc4XEndpoint endpoint, Processor 
> > > processor) throws PlcException {
> > >     >         this.endpoint = endpoint;
> > >     >         this.dataType = endpoint.getDataType();
> > >     >         this.processor = 
> > > AsyncProcessorConverterHelper.convert(processor);
> > >     >         this.exceptionHandler = new 
> > > LoggingExceptionHandler(endpoint.getCamelContext(), getClass());
> > >     >         String plc4xURI = 
> > > endpoint.getEndpointUri().replaceFirst("plc4x:/?/?", "");
> > >     >         this.plcConnection = 
> > > endpoint.getPlcDriverManager().getConnection(plc4xURI);
> > >     >         this.fieldQuery = endpoint.getAddress();
> > >     >     }
> > >     > 
> > >     >     @Override
> > >     >     public String toString() {
> > >     >         return "Plc4XConsumer[" + endpoint + "]";
> > >     >     }
> > >     > 
> > >     >     @Override
> > >     >     public Endpoint getEndpoint() {
> > >     >         return endpoint;
> > >     >     }
> > >     > 
> > >     >     public ExceptionHandler getExceptionHandler() {
> > >     >         return exceptionHandler;
> > >     >     }
> > >     > 
> > >     >     public void setExceptionHandler(ExceptionHandler 
> > > exceptionHandler) {
> > >     >         this.exceptionHandler = exceptionHandler;
> > >     >     }
> > >     > 
> > >     >     @Override
> > >     >     protected void doStart() throws InterruptedException, 
> > > ExecutionException {
> > >     >         // TODO: Is it correct to only support one field?
> > >     >         future = executorService.schedule(() -> {
> > >     >             plcConnection.readRequestBuilder()
> > >     >                 .addItem("default", fieldQuery)
> > >     >                 .build()
> > >     >                 .execute()
> > >     >                 .thenAccept(response -> {
> > >     >                     LOGGER.debug("Received {}", response);
> > >     >                     try {
> > >     >                         Exchange exchange = 
> > > endpoint.createExchange();
> > >     >                         
> > > exchange.getIn().setBody(unwrapIfSingle(response.getAllObjects("default")));
> > >     >                         processor.process(exchange);
> > >     >                     } catch (Exception e) {
> > >     >                         exceptionHandler.handleException(e);
> > >     >                     }
> > >     >                 });
> > >     >         }, 3, TimeUnit.SECONDS);
> > >     >     }
> > >     > 
> > >     >     @Override
> > >     >     protected void doStop() throws InterruptedException, 
> > > ExecutionException, TimeoutException {
> > >     >         // First stop the polling process
> > >     >         if (future != null) {
> > >     >             future.cancel(true);
> > >     >         }
> > >     >         // TODO: Handle the response ...
> > >     >         try {
> > >     >             plcConnection.close();
> > >     >         } catch (Exception e) {
> > >     >             LOGGER.error("Error closing connection", e);
> > >     >         }
> > >     >     }
> > >     > 
> > >     >     private Object unwrapIfSingle(Collection collection) {
> > >     >         if (collection.isEmpty()) {
> > >     >             return null;
> > >     >         }
> > >     >         if (collection.size() == 1) {
> > >     >             return collection.iterator().next();
> > >     >         }
> > >     >         return collection;
> > >     >     }
> > >     > 
> > >     > }
> > >     > ```
> > >     > 
> > >     > Julian
> > >     > 
> > >     > 
> > >     > Am 18.02.20, 13:22 schrieb "Julian Feinauer" 
> > > <[email protected]>:
> > >     > 
> > >     >     Hi Etienne,
> > >     >     
> > >     >     oh, sorry, indeed. The Code in the Camel module is right, but 
> > > does not work for Siemens S7.
> > >     >     Let me try to write you an updated version in another branch 
> > > ASAP then you can check it.
> > >     >     
> > >     >     Sorry!
> > >     >     Julian
> > >     >     
> > >     >     Am 18.02.20, 12:56 schrieb "Etienne Robinet" 
> > > <[email protected]>:
> > >     >     
> > >     >         I just cloned the rel/0.6 branch from git, until now I 
> > > didn't change anything.
> > >     >         Regards,,
> > >     >         Etienne
> > >     >         
> > >     >         On 2020/02/18 11:10:39, Julian Feinauer 
> > > <[email protected]> wrote: 
> > >     >         > Did you post your code somewhere? I cant find it.. just 
> > > post it somewhere and I will have a look!
> > >     >         > 
> > >     >         > Julian
> > >     >         > 
> > >     >         > Am 18.02.20, 11:28 schrieb "Etienne Robinet" 
> > > <[email protected]>:
> > >     >         > 
> > >     >         >     Hi Julian,
> > >     >         >     thanks for the advice, but where should I change the 
> > > code to apply your modification? Is it in the doStart() methode of de 
> > > PLC4XConsumer?
> > >     >         >     Regards,
> > >     >         >     
> > >     >         >     Etienne
> > >     >         >     
> > >     >         >     On 2020/02/18 08:55:22, Julian Feinauer 
> > > <[email protected]> wrote: 
> > >     >         >     > Hi Etienne,
> > >     >         >     > 
> > >     >         >     > thank you for your investigation.
> > >     >         >     > I just locked at your log and it seems that 
> > > connection works fine and some messages are exchanged BUT you try to 
> > > subscribe to a Value which is currently not supported.
> > >     >         >     > Try to just use the 
> > > "readRequestBuilder().addItem("", "").build().execute().get()" approach 
> > > to send a single request, that should work.
> > >     >         >     > 
> > >     >         >     > Best
> > >     >         >     > Julian
> > >     >         >     > 
> > >     >         >     > Am 18.02.20, 09:39 schrieb "Etienne Robinet" 
> > > <[email protected]>:
> > >     >         >     > 
> > >     >         >     >     Hello,
> > >     >         >     >     with the help of some colleague we managed to 
> > > find how to fix the issue so that the DriverManager can find the actual 
> > > s7 protocol.
> > >     >         >     >     All I had to do is to create a maven project 
> > > (karaf-blueprint) archetype and do as follow:
> > >     >         >     >     
> > >     >         >     >     1. Inside the pom, add the S7PlcDriver under 
> > > "imports"
> > >     >         >     >     2. create a service under 
> > > main/java/resources/META-INF/services/xxx.xxx.PlcDriver containing the 
> > > implementation (S7PlcDriver) and license
> > >     >         >     >     3. Create a simple XML blueprint (with a real 
> > > address this time connected to a real PLC)
> > >     >         >     >     <blueprint 
> > > xmlns="http://www.osgi.org/xmlns/blueprint/v1.0.0"; 
> > > default-activation="lazy">
> > >     >         >     >     
> > >     >         >     >         <camelContext id="PLC-Context" 
> > > xmlns="http://camel.apache.org/schema/blueprint"; streamCache="true">
> > >     >         >     >     
> > >     >         >     >     
> > >     >         >     >             <route id="Route1">
> > >     >         >     >     
> > >     >         >     >                 <from 
> > > uri="plc4x:s7://192.168.178.10/1/1"/>
> > >     >         >     >                 <log message=" Sending ${body}" 
> > > loggingLevel="INFO" />
> > >     >         >     >                 <to uri="mock:test?retainLast=10" />
> > >     >         >     >     
> > >     >         >     >             </route>
> > >     >         >     >     
> > >     >         >     >         </camelContext>
> > >     >         >     >     
> > >     >         >     >     </blueprint>
> > >     >         >     >     
> > >     >         >     >     So now I have the next issue, I can see from 
> > > the log that a connection is established but it tells me that the 
> > > connection doesn't support connection. Am I missing a parameter or what 
> > > could be the issue?
> > >     >         >     >     
> > >     >         >     >     Here the log:
> > >     >         >     >     
> > >     >         >     >     https://i.imgur.com/KgWz8DF.png
> > >     >         >     >     
> > >     >         >     >     On 2020/02/17 12:11:56, Christofer Dutz 
> > > <[email protected]> wrote: 
> > >     >         >     >     > Hi all,
> > >     >         >     >     > 
> > >     >         >     >     > having a more detailed look at the log-trace, 
> > > it seems the DriverManager isn't able to find the S7 driver at all ...
> > >     >         >     >     > But I guess if it even was available, as 
> > > Cesar pointed out, the field address is that of the mock driver and not 
> > > of the S7 so this will not work.
> > >     >         >     >     > Also are you connecting to localhost, which 
> > > is also probably not what you want. Unless you are running a S7 simulator 
> > > on your machine.
> > >     >         >     >     > 
> > >     >         >     >     > Depending of if you're using a released 
> > > version of the s7 driver the connection URL is correct, however if you 
> > > switch to the new S7 driver it would look like this:  s7://{ip or host}
> > >     >         >     >     > Not the "/1/1" are now missing.
> > >     >         >     >     > 
> > >     >         >     >     > Chris
> > >     >         >     >     > 
> > >     >         >     >     > 
> > >     >         >     >     > 
> > >     >         >     >     > 
> > >     >         >     >     > Am 17.02.20, 13:04 schrieb "Cesar Garcia" 
> > > <[email protected]>:
> > >     >         >     >     > 
> > >     >         >     >     >     Hi,
> > >     >         >     >     >     
> > >     >         >     >     >     The PLC address does not look correct, 
> > > can you confirm that it really
> > >     >         >     >     >     points to a real PLC or an S7 simulator?
> > >     >         >     >     >     
> > >     >         >     >     >     <from uri="plc4x:s7:localhost/1/1"/>
> > >     >         >     >     >     
> > >     >         >     >     >     Best regards,
> > >     >         >     >     >     
> > >     >         >     >     >     
> > >     >         >     >     >     El vie., 14 feb. 2020 a las 18:34, 
> > > Etienne Robinet (<[email protected]>)
> > >     >         >     >     >     escribió:
> > >     >         >     >     >     
> > >     >         >     >     >     > Hello everyone,
> > >     >         >     >     >     > I've spent some days trying to figure 
> > > out how to make PLC4X work inside a
> > >     >         >     >     >     > karaf container in combination with 
> > > camel blueprints for routing.
> > >     >         >     >     >     > I've downloaded the latest release 
> > > (0.5.0) and built it with maven. I then
> > >     >         >     >     >     > installed the driver-s7-feature and 
> > > plc4j-apache-camel bundle into my
> > >     >         >     >     >     > container and got following bundles 
> > > running:
> > >     >         >     >     >     >
> > >     >         >     >     >     > >PLC4J: API
> > >     >         >     >     >     > >PLC4J: Driver: S7
> > >     >         >     >     >     > >PLC4J: Protocol: Driver-Base: Base
> > >     >         >     >     >     > >PLC4J: Protocol: Driver-Base: TCP
> > >     >         >     >     >     > >PLC4J: Protocol: ISO on TCP
> > >     >         >     >     >     > >PLC4J: Protocol: ISO TP
> > >     >         >     >     >     > >PLC4J: Protocol: S7
> > >     >         >     >     >     > >PLC4j: Utils: Driver Base: Java
> > >     >         >     >     >     > >PLC4J: Integrations: Apache Camel
> > >     >         >     >     >     >
> > >     >         >     >     >     > After trying a simple route with this 
> > > consumer component:
> > >     >         >     >     >     > <from uri="plc4x:s7:localhost/1/1"/> 
> > > (the address is for testing purpose)
> > >     >         >     >     >     > I get the following error:
> > >     >         >     >     >     > Error occurred during starting 
> > > CamelContext: PLC-Context
> > >     >         >     >     >     > 
> > > org.apache.camel.FailedToCreateRouteException: Failed to create route
> > >     >         >     >     >     > Route1: 
> > > Route(Route1)[[From[plc4x:s7:localhost/1/1]] -> [To[mock:tes...
> > >     >         >     >     >     > because of Unable to find driver for 
> > > protocol 's7'
> > >     >         >     >     >     >
> > >     >         >     >     >     > I've tested numerous version of PLC4X 
> > > and got the same results, so I think
> > >     >         >     >     >     > I might be close to fix it!
> > >     >         >     >     >     > Any help would be appreciated!
> > >     >         >     >     >     >
> > >     >         >     >     >     > Here the full log
> > >     >         >     >     >     >
> > >     >         >     >     >     > 16:30:45.578 INFO [Blueprint Event 
> > > Dispatcher: 1] Attempting to start
> > >     >         >     >     >     > CamelContext: PLC-Context
> > >     >         >     >     >     > 16:30:45.579 INFO [Blueprint Event 
> > > Dispatcher: 1] Apache Camel 2.24.2
> > >     >         >     >     >     > (CamelContext: PLC-Context) is starting
> > >     >         >     >     >     > 16:30:45.580 INFO [Blueprint Event 
> > > Dispatcher: 1] StreamCaching is enabled
> > >     >         >     >     >     > on CamelContext: PLC-Context
> > >     >         >     >     >     > 16:30:45.580 INFO [Blueprint Event 
> > > Dispatcher: 1] JMX is enabled
> > >     >         >     >     >     > 16:30:45.600 INFO [Blueprint Event 
> > > Dispatcher: 1] Instantiating new PLC
> > >     >         >     >     >     > Driver Manager with class loader
> > >     >         >     >     >     > 
> > > BundleDelegatingClassLoader(plc4j-route.xml [67])
> > >     >         >     >     >     > 16:30:45.600 INFO [Blueprint Event 
> > > Dispatcher: 1] Registering available
> > >     >         >     >     >     > drivers...
> > >     >         >     >     >     > 16:30:45.601 TRACE [Blueprint Event 
> > > Dispatcher: 1] FindResource:
> > >     >         >     >     >     > 
> > > META-INF/services/org.apache.plc4x.java.spi.PlcDriver
> > >     >         >     >     >     > 16:30:45.627 INFO [Blueprint Event 
> > > Dispatcher: 1] StreamCaching in use
> > >     >         >     >     >     > with spool directory:
> > >     >         >     >     >     > 
> > > C:\karaf\bin\..\data\tmp\camel\camel-tmp-00f849ac-0ccf-4b12-822d-dda62267eb6c
> > >     >         >     >     >     > and rules: [Spool > 128K body size]
> > >     >         >     >     >     > 16:30:45.629 INFO [Blueprint Event 
> > > Dispatcher: 1] Apache Camel 2.24.2
> > >     >         >     >     >     > (CamelContext: PLC-Context) is shutting 
> > > down
> > >     >         >     >     >     > 16:30:45.639 INFO [Blueprint Event 
> > > Dispatcher: 1] Apache Camel 2.24.2
> > >     >         >     >     >     > (CamelContext: PLC-Context) uptime 
> > > 0.060 seconds
> > >     >         >     >     >     > 16:30:45.640 INFO [Blueprint Event 
> > > Dispatcher: 1] Apache Camel 2.24.2
> > >     >         >     >     >     > (CamelContext: PLC-Context) is shutdown 
> > > in 0.011 seconds
> > >     >         >     >     >     > 16:30:45.640 WARN [Blueprint Event 
> > > Dispatcher: 1] Changing Camel state for
> > >     >         >     >     >     > bundle 67 to Failure
> > >     >         >     >     >     > 16:30:45.641 ERROR [Blueprint Event 
> > > Dispatcher: 1] Error occurred during
> > >     >         >     >     >     > starting CamelContext: PLC-Context
> > >     >         >     >     >     > 
> > > org.apache.camel.FailedToCreateRouteException: Failed to create route
> > >     >         >     >     >     > Route1: 
> > > Route(Route1)[[From[plc4x:s7:localhost/1/1]] -> [To[mock:tes...
> > >     >         >     >     >     > because of Unable to find driver for 
> > > protocol 's7'
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.RouteService.warmUp(RouteService.java:147)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.DefaultCamelContext.doWarmUpRoutes(DefaultCamelContext.java:3954)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.DefaultCamelContext.safelyStartRouteServices(DefaultCamelContext.java:3861)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.DefaultCamelContext.doStartOrResumeRoutes(DefaultCamelContext.java:3647)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.DefaultCamelContext.doStartCamel(DefaultCamelContext.java:3488)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.DefaultCamelContext$4.call(DefaultCamelContext.java:3247)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.DefaultCamelContext$4.call(DefaultCamelContext.java:3243)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.DefaultCamelContext.doWithDefinedClassLoader(DefaultCamelContext.java:3266)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.DefaultCamelContext.doStart(DefaultCamelContext.java:3243)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.support.ServiceSupport.start(ServiceSupport.java:72)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.DefaultCamelContext.start(DefaultCamelContext.java:3159)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.blueprint.BlueprintCamelContext.start(BlueprintCamelContext.java:255)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.blueprint.BlueprintCamelContext.maybeStart(BlueprintCamelContext.java:297)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.blueprint.BlueprintCamelContext.blueprintEvent(BlueprintCamelContext.java:188)
> > >     >         >     >     >     > [!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.aries.blueprint.container.BlueprintEventDispatcher$3.call(BlueprintEventDispatcher.java:190)
> > >     >         >     >     >     > [!/:1.10.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.aries.blueprint.container.BlueprintEventDispatcher$3.call(BlueprintEventDispatcher.java:188)
> > >     >         >     >     >     > [!/:1.10.2]
> > >     >         >     >     >     >         at 
> > > java.util.concurrent.FutureTask.run(FutureTask.java:264) [?:?]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > java.util.concurrent.Executors$RunnableAdapter.call(Executors.java:515)
> > >     >         >     >     >     > [?:?]
> > >     >         >     >     >     >         at 
> > > java.util.concurrent.FutureTask.run(FutureTask.java:264) [?:?]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > java.util.concurrent.Executors$RunnableAdapter.call(Executors.java:515)
> > >     >         >     >     >     > [?:?]
> > >     >         >     >     >     >         at 
> > > java.util.concurrent.FutureTask.run(FutureTask.java:264) [?:?]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.run(ScheduledThreadPoolExecutor.java:304)
> > >     >         >     >     >     > [?:?]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > java.util.concurrent.ThreadPoolExecutor.runWorker(ThreadPoolExecutor.java:1128)
> > >     >         >     >     >     > [?:?]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > java.util.concurrent.ThreadPoolExecutor$Worker.run(ThreadPoolExecutor.java:628)
> > >     >         >     >     >     > [?:?]
> > >     >         >     >     >     >         at 
> > > java.lang.Thread.run(Thread.java:834) [?:?]
> > >     >         >     >     >     > Caused by: 
> > > org.apache.plc4x.java.api.exceptions.PlcConnectionException:
> > >     >         >     >     >     > Unable to find driver for protocol 's7'
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.plc4x.java.PlcDriverManager.getDriver(PlcDriverManager.java:98)
> > >     >         >     >     >     > ~[?:?]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.plc4x.java.PlcDriverManager.getConnection(PlcDriverManager.java:71)
> > >     >         >     >     >     > ~[?:?]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.plc4x.camel.Plc4XConsumer.<init>(Plc4XConsumer.java:57) ~[?:?]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.plc4x.camel.Plc4XEndpoint.createConsumer(Plc4XEndpoint.java:72)
> > >     >         >     >     >     > ~[?:?]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.EventDrivenConsumerRoute.addServices(EventDrivenConsumerRoute.java:69)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.DefaultRoute.onStartingServices(DefaultRoute.java:107)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.RouteService.doWarmUp(RouteService.java:172)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         at
> > >     >         >     >     >     > 
> > > org.apache.camel.impl.RouteService.warmUp(RouteService.java:145)
> > >     >         >     >     >     > ~[!/:2.24.2]
> > >     >         >     >     >     >         ... 24 more
> > >     >         >     >     >     >
> > >     >         >     >     >     >
> > >     >         >     >     >     >
> > >     >         >     >     >     
> > >     >         >     >     >     -- 
> > >     >         >     >     >     *CEOS Automatización, C.A.*
> > >     >         >     >     >     *GALPON SERVICIO INDUSTRIALES Y NAVALES 
> > > FA, C.A.,*
> > >     >         >     >     >     *PISO 1, OFICINA 2, AV. RAUL LEONI, 
> > > SECTOR GUAMACHITO,*
> > >     >         >     >     >     
> > >     >         >     >     >     *FRENTE A LA ASOCIACION DE 
> > > GANADEROS,BARCELONA,EDO. ANZOATEGUI*
> > >     >         >     >     >     *Ing. César García*
> > >     >         >     >     >     *Cel: 0416-681.03.99*
> > >     >         >     >     >     
> > >     >         >     >     >     *Cel: 0414-760.98.95*
> > >     >         >     >     >     
> > >     >         >     >     >     *Hotline Técnica SIEMENS: 0800 1005080*
> > >     >         >     >     >     
> > >     >         >     >     >     *Email: [email protected]
> > >     >         >     >     >     <[email protected]>*
> > >     >         >     >     >     
> > >     >         >     >     > 
> > >     >         >     >     > 
> > >     >         >     >     
> > >     >         >     > 
> > >     >         >     > 
> > >     >         >     
> > >     >         > 
> > >     >         > 
> > >     >         
> > >     >     
> > >     >     
> > >     > 
> > >     > 
> > >     
> > > 
> > > 
> > 
> 

Reply via email to