Hi Etienne, 

I would suggest you create a Pull Request for your changes so we can pull them 
in.
We can then work on finalizing this together.

Chris



Am 17.03.20, 11:22 schrieb "Etienne Robinet" <[email protected]>:

    Hi Chris,
    the problem was the <parameter> tag was a parameter from COTP and not 
propper to XML. Just removed it and it found the right parameters. I pushed the 
test for Parser/Serializer for Read&Write Response/Request. The only little 
issue I have is with the parsing from the Java Object to an XML string (to 
compare). It seems like it still has some difficulties to correctly parse a 
byte[]; for the rest everything should be OK.
    What needs to be done more on the driver? 
    Etienne 
    On 2020/03/17 08:00:49, Christofer Dutz <[email protected]> wrote: 
    > Hi Etienne,
    > 
    > sorry for the late response ... couldn't read the image on my phone, but 
on the computer it's fine.
    > 
    > In your case the root element needs to be EipConnectionRequest and not 
EipRequest.
    > 
    > I have to admit I too haven't completely grasped all the details of how 
Jackson parses and serializes stuff. 
    > But usually I paste an empty xml representation (in your case an empty 
EipPacket element) and put in the bytes.
    > Then I run the test and obviously it fails complaining about what it 
parsed and that it looks different.
    > I manually examine if the xml is correct and replace the empty element 
with the printed out verson.
    > 
    > Chris
    > 
    > 
    > 
    > Am 16.03.20, 17:20 schrieb "Etienne Robinet" <[email protected]>:
    > 
    >     Hi again,
    >     I started also to test serializer and parser. Here is the problem I 
am facing: https://i.imgur.com/stmEqlm.png
    >     On the left you see the testcase, on the right the code in the 
ProtocolLogic. I don't know what I a m doing wrong, but from the log it seems 
it does only look for the parameters I am giving?
    >     
    >     Etienne
    >     On 2020/03/16 15:38:33, Etienne Robinet <[email protected]> wrote: 
    >     > Hi Chris,
    >     > I did a similar test for reading a tag. As I never did such tests 
before, I don't know if the method is correct, but the results are similar to 
the ones I get running the same test for the s7. I also pushed this to my fork. 
Tomorrow I will try to do some tests on the PLC to see if I can perform 
fetching a lot of data (like I did on the s7) and if the writing works.
    >     > 
    >     > Etienne
    >     > 
    >     > On 2020/03/16 13:47:53, Christofer Dutz <[email protected]> 
wrote: 
    >     > > Hi Etienne,
    >     > > 
    >     > > You probably pulled in a SNAPSHOT from our maven repo ... if this 
is newer than yours, Maven usually pulls new versions the first time you build 
on every day. ... yes this can be annoying ;-)
    >     > > 
    >     > > Chris
    >     > > 
    >     > > Am 16.03.20, 14:41 schrieb "Etienne Robinet" <[email protected]>:
    >     > > 
    >     > >     Hi,
    >     > >     Ok I see, seems to be resolved once rebuilt. But how does it 
come that it generates the getLengthInBits() before I updated it?
    >     > >     
    >     > >     Etienne
    >     > >     On 2020/03/16 13:10:24, Christofer Dutz 
<[email protected]> wrote: 
    >     > >     > Hi Etienne,
    >     > >     > 
    >     > >     > it's there ... have a look:
    >     > >     > 
https://github.com/apache/plc4x/blob/develop/plc4j/spi/src/main/java/org/apache/plc4x/java/spi/generation/Message.java
    >     > >     > 
    >     > >     > The problem is that you checked out your fork. That doesn't 
update automatically if someone pushes anything to our repo.
    >     > >     > You manually have to do that.
    >     > >     > 
    >     > >     > Please check "Keeping your fork up to date" on 
https://plc4x.apache.org/developers/contributing.html
    >     > >     > 
    >     > >     > Hope that helps.
    >     > >     > 
    >     > >     > Chris
    >     > >     > 
    >     > >     > 
    >     > >     > 
    >     > >     > Am 16.03.20, 13:50 schrieb "Etienne Robinet" 
<[email protected]>:
    >     > >     > 
    >     > >     >     Hi Chris,
    >     > >     >     
    >     > >     >     buy how do I stop it from generating the error? He 
calls the getLengthInBits on an implmentation of Message so that is where the 
error happens (also the @Override). I checked the Message interface and there 
is no such metho, also checked the pojo-template and couldn't find the method. 
I did not had that before when generating sources (I think since I ran some 
tests on the PLC).
    >     > >     >     Etienne
    >     > >     >     On 2020/03/16 12:46:48, Christofer Dutz 
<[email protected]> wrote: 
    >     > >     >     > Hi Etienne,
    >     > >     >     > 
    >     > >     >     > well the getLengthInBytes is still there ... it just 
calls the getLengthInBits and divides that by 8.
    >     > >     >     > The reason was that with the Firmata driver we first 
had a protocol where the getLengthInBytes returned 0 because one datatype 
didn't have a full multiple of 8 as content. This made getLengthInBytes return 
0 instead of 1.
    >     > >     >     > 
    >     > >     >     > In general nothing should have changed as the 
getLengthInBytes still exists. It's just that there is an additional 
getLengthInBits.
    >     > >     >     > 
    >     > >     >     > Chris
    >     > >     >     > 
    >     > >     >     > 
    >     > >     >     > 
    >     > >     >     > 
    >     > >     >     > Am 16.03.20, 13:19 schrieb "Etienne Robinet" 
<[email protected]>:
    >     > >     >     > 
    >     > >     >     >     Hi Chris,
    >     > >     >     >     
    >     > >     >     >     Thanks for the advice I will try to find a way 
for that.
    >     > >     >     >     I tried executing some tests but I realisedI got 
an error on runtime. After looking at the generated source, this is what I have:
    >     > >     >     >     https://i.imgur.com/LflQvpw.png
    >     > >     >     >     Why does the getLengthInBytes method got swapped 
by getLengthInBits? The error comes that he is looking for the 
gteLengthInBits() on a Message, and the @Override is also wrong.
    >     > >     >     >     
    >     > >     >     >     Etienne 
    >     > >     >     >     On 2020/03/16 11:46:53, Christofer Dutz 
<[email protected]> wrote: 
    >     > >     >     >     > Hi Etienne,
    >     > >     >     >     > 
    >     > >     >     >     > well there must be some way to distinguish the 
two ... perhaps using more than one field to discriminate the types?
    >     > >     >     >     > 
    >     > >     >     >     > Chris
    >     > >     >     >     > 
    >     > >     >     >     > 
    >     > >     >     >     > 
    >     > >     >     >     > Am 16.03.20, 12:01 schrieb "Etienne Robinet" 
<[email protected]>:
    >     > >     >     >     > 
    >     > >     >     >     >     Hi Chris,
    >     > >     >     >     >     I will have a look to build the tests for 
the parser/serializer.
    >     > >     >     >     >     
    >     > >     >     >     >     I have another question. In Cip when data 
is too large and wont fit into a signle packet (>500 bytes), we use 
fragmentedRequest. The problem I'm facing is: ReadFragmentedService and 
UnconnectedRequest have the same service number 0x52.
    >     > >     >     >     >     From the structure, the UnconnectedRequest 
contains the fragmentedServiceRequest; but the responses are at the same 
'level' as the UnconnectedRequest. So I don't know for now how to implement 
this and if we even need it (but I still find a good option);
    >     > >     >     >     >     
    >     > >     >     >     >     Etienne
    >     > >     >     >     >     On 2020/03/16 10:35:34, Christofer Dutz 
<[email protected]> wrote: 
    >     > >     >     >     >     > Hi Etienne,
    >     > >     >     >     >     > 
    >     > >     >     >     >     > I would also suggest you have a look at 
the unit-test framework I built for testing the parsers, serializers and the 
model.
    >     > >     >     >     >     > 
    >     > >     >     >     >     > 
plc4j/drivers/s7/src/test/java/org/apache/plc4x/java/s7/readwrite/S7DriverTestsuite.java
    >     > >     >     >     >     > 
plc4j/drivers/s7/src/test/resources/testsuite/S7DriverTestsuite.xml
    >     > >     >     >     >     > 
    >     > >     >     >     >     > I'm currently still working on an 
integration test-suite that will test the protocol component using pre-defined 
messages:
    >     > >     >     >     >     > 
    >     > >     >     >     >     > 
plc4j/drivers/s7/src/test/java/org/apache/plc4x/java/s7/readwrite/S7ParserSerializerTestsuite.java
    >     > >     >     >     >     > 
plc4j/drivers/s7/src/test/resources/testsuite/S7ParserSerializerTestsuite.xml
    >     > >     >     >     >     > 
    >     > >     >     >     >     > But I wouldn't call that production ready 
yet as I was distracted by other work and have to check where I dropped the 
ball last time.
    >     > >     >     >     >     > 
    >     > >     >     >     >     > Chris
    >     > >     >     >     >     > 
    >     > >     >     >     >     > 
    >     > >     >     >     >     > 
    >     > >     >     >     >     > 
    >     > >     >     >     >     > Am 16.03.20, 11:28 schrieb "Etienne 
Robinet" <[email protected]>:
    >     > >     >     >     >     > 
    >     > >     >     >     >     >     Hi Chris, 
    >     > >     >     >     >     >     this did also the trick and looks far 
more clean, thanks for the help on that!
    >     > >     >     >     >     >     
    >     > >     >     >     >     >     I am now working on the writing, 
might have a look on connected messages afterwards. The fact is that now I'm 
doing home office so it will be a bit trickier to test, but I might get a 
solution in the following days. 
    >     > >     >     >     >     >     Stay safe,
    >     > >     >     >     >     >     
    >     > >     >     >     >     >     Etienne
    >     > >     >     >     >     >     On 2020/03/13 17:09:06, Christofer 
Dutz <[email protected]> wrote: 
    >     > >     >     >     >     >     > Hi Etienne,
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > I just took the version before your 
last commit and applied the pattern how you pass along the arguments.
    >     > >     >     >     >     >     > Please have a look ... I haven't 
compiled the spec, but it should work. As you can see, if you want to use the
    >     > >     >     >     >     >     > arguments inside a sub-type, you 
have to re-declare the variable (identical name and type) in the sub-type.
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > //
    >     > >     >     >     >     >     >  // Licensed to the Apache Software 
Foundation (ASF) under one
    >     > >     >     >     >     >     >  // or more contributor license 
agreements.  See the NOTICE file
    >     > >     >     >     >     >     >  // distributed with this work for 
additional information
    >     > >     >     >     >     >     >  // regarding copyright ownership.  
The ASF licenses this file
    >     > >     >     >     >     >     >  // to you under the Apache 
License, Version 2.0 (the
    >     > >     >     >     >     >     >  // "License"); you may not use 
this file except in compliance
    >     > >     >     >     >     >     >  // with the License.  You may 
obtain a copy of the License at
    >     > >     >     >     >     >     >  //
    >     > >     >     >     >     >     >  //     
http://www.apache.org/licenses/LICENSE-2.0
    >     > >     >     >     >     >     >  //
    >     > >     >     >     >     >     >  // Unless required by applicable 
law or agreed to in writing,
    >     > >     >     >     >     >     >  // software distributed under the 
License is distributed on an
    >     > >     >     >     >     >     >  // "AS IS" BASIS, WITHOUT 
WARRANTIES OR CONDITIONS OF ANY
    >     > >     >     >     >     >     >  // KIND, either express or 
implied.  See the License for the
    >     > >     >     >     >     >     >  // specific language governing 
permissions and limitations
    >     > >     >     >     >     >     >  // under the License.
    >     > >     >     >     >     >     >  //
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     >  
//////////////////////////////////////////////////////////////////
    >     > >     >     >     >     >     >  ///EthernetIP Header of size 24
    >     > >     >     >     >     >     >  
/////////////////////////////////////////////////////////////////
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > [discriminatedType 'EipPacket'
    >     > >     >     >     >     >     >     [discriminator uint 16 
'command']
    >     > >     >     >     >     >     >     [implicit      uint 16 'len' 
'lengthInBytes - 24']
    >     > >     >     >     >     >     >     [simple        uint 32 
'sessionHandle']
    >     > >     >     >     >     >     >     [simple        uint 32 'status']
    >     > >     >     >     >     >     >     [array         uint 8  
'senderContext' count '8']
    >     > >     >     >     >     >     >     [simple        uint 32 
'options']
    >     > >     >     >     >     >     >     [typeSwitch 'command'
    >     > >     >     >     >     >     >             ['0x0065' 
EipConnectionRequest
    >     > >     >     >     >     >     >                 [const  uint    16  
 'protocolVersion'   '0x01']
    >     > >     >     >     >     >     >                 [const  uint    16  
 'flags'             '0x00']
    >     > >     >     >     >     >     >             ]
    >     > >     >     >     >     >     >             ['0x0066' 
EipDisconnectRequest
    >     > >     >     >     >     >     >             ]
    >     > >     >     >     >     >     >             ['0x006F' CipRRData 
[uint  16  'len']
    >     > >     >     >     >     >     >                 [reserved  uint    
32    '0x00000000']
    >     > >     >     >     >     >     >                 [reserved  uint    
16    '0x0000']
    >     > >     >     >     >     >     >                 [simple CipExchange 
'exchange' ['len-6']]
    >     > >     >     >     >     >     >             ]
    >     > >     >     >     >     >     >         ]
    >     > >     >     >     >     >     > ]
    >     > >     >     >     >     >     > [type  'CipExchange' [uint 16 
'exchangeLen']
    >     > >     >     >     >     >     >     [const          uint        16  
    'itemCount'           '0x0002']     //2 items
    >     > >     >     >     >     >     >     [const          uint        32  
    'nullPtr'             '0x0']          //NullPointerAddress
    >     > >     >     >     >     >     >     [const          uint        16  
    'UnconnectedData'     '0x00B2']   //Connection Manager
    >     > >     >     >     >     >     >     [implicit       uint        16  
    'size'                'lengthInBytes - 8 - 2'] //remove fields above and 
routing
    >     > >     >     >     >     >     >     [simple         CipService      
    'service' ['exchangeLen - 10'] ]
    >     > >     >     >     >     >     > ]
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > [discriminatedType  'CipService' 
[uint 16 'serviceLen']
    >     > >     >     >     >     >     >     [discriminator  uint    8   
'service']
    >     > >     >     >     >     >     >     [typeSwitch 'service'
    >     > >     >     >     >     >     >         ['0x4C' CipReadRequest
    >     > >     >     >     >     >     >             [simple     int     8   
'RequestPathSize']
    >     > >     >     >     >     >     >             [array      int     8   
'tag'   length  '(RequestPathSize*2)']
    >     > >     >     >     >     >     >             [simple     uint    16  
'elementNb']
    >     > >     >     >     >     >     >         ]
    >     > >     >     >     >     >     >         ['0xCC' CipReadResponse 
[uint 16 'serviceLen']
    >     > >     >     >     >     >     >               [reserved   uint      
      8   '0x00']
    >     > >     >     >     >     >     >               [simple     uint      
      8   'status']
    >     > >     >     >     >     >     >               [simple     uint      
      8   'extStatus']
    >     > >     >     >     >     >     >               [enum       
CIPDataTypeCode   'dataType']
    >     > >     >     >     >     >     >               [array      int       
      8   'data'  length  'serviceLen-6']
    >     > >     >     >     >     >     >         ]
    >     > >     >     >     >     >     >         ['0x0A' 
MultipleServiceRequest [uint 16 'serviceLen']
    >     > >     >     >     >     >     >                [const  int     8   
'RequestPathSize'   '0x02']
    >     > >     >     >     >     >     >                [const  uint    32  
'RequestPath'       '0x01240220']   //Logical Segment: Class(0x20) 0x02, 
Instance(0x24) 01 (Message Router)
    >     > >     >     >     >     >     >                [simple Services  
'data' ['serviceLen - 6 ']]
    >     > >     >     >     >     >     >         ]
    >     > >     >     >     >     >     >         ['0x8A' 
MultipleServiceResponse [uint 16 'serviceLen']
    >     > >     >     >     >     >     >                [reserved   uint    
8   '0x0']
    >     > >     >     >     >     >     >                [simple     uint    
8   'status']
    >     > >     >     >     >     >     >                [simple     uint    
8   'extStatus']
    >     > >     >     >     >     >     >                [simple Services  
'data' ['serviceLen - 4']]
    >     > >     >     >     >     >     >         ]
    >     > >     >     >     >     >     >         ['0x0052'   
CipUnconnectedRequest
    >     > >     >     >     >     >     >                [reserved   uint    
8   '0x02']
    >     > >     >     >     >     >     >                [reserved   uint    
8   '0x20']   // setRequestPathLogicalClassSegment
    >     > >     >     >     >     >     >                [reserved   uint    
8   '0x06']   // set request class path
    >     > >     >     >     >     >     >                [reserved   uint    
8   '0x24']   // setRequestPathLogicalInstanceSegment
    >     > >     >     >     >     >     >                [reserved   uint    
8   '0x01']   // setRequestPathInstance
    >     > >     >     >     >     >     >                [reserved   uint    
16  '0x9D05']   //Timeout 5s
    >     > >     >     >     >     >     >                [implicit   uint    
16   'messageSize'   'lengthInBytes - 10 - 4']   //substract above and routing
    >     > >     >     >     >     >     >                [simple     
CipService  'service']
    >     > >     >     >     >     >     >                [const      uint    
16  'route' '0x0001']
    >     > >     >     >     >     >     >                [simple     int     
8   'backPlane']
    >     > >     >     >     >     >     >                [simple     int     
8   'slot']
    >     > >     >     >     >     >     >         ]
    >     > >     >     >     >     >     >     ]
    >     > >     >     >     >     >     > ]
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > [type   'Services' [uint   16   
'servicesLen']
    >     > >     >     >     >     >     >     [simple uint    16  'serviceNb']
    >     > >     >     >     >     >     >     [array  uint        16  
'offsets'       count  'serviceNb']
    >     > >     >     >     >     >     >     [array  CipService   'services' 
     count  'serviceNb' ['servicesLen/serviceNb'] ]
    >     > >     >     >     >     >     > ]
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > [enum uint   16   'CIPDataTypeCode' 
[uint 8  'size']
    >     > >     >     >     >     >     >     ['0X00C1'   BOOL            
['1']]
    >     > >     >     >     >     >     >     ['0X00CA'   REAL            
['4']]
    >     > >     >     >     >     >     >     ['0X00C4'   DINT            
['4']]
    >     > >     >     >     >     >     >     ['0X00C3'   INT             
['2']]
    >     > >     >     >     >     >     >     ['0X00C2'   SINT            
['1']]
    >     > >     >     >     >     >     >     ['0X02A0'   STRUCTURED      
['88']]
    >     > >     >     >     >     >     >     ['0X02A0'   STRING          
['88']]
    >     > >     >     >     >     >     >     ['0X02A0'   STRING36        
['40']]
    >     > >     >     >     >     >     >     ['-1'       UNKNOWN         
['-1']]
    >     > >     >     >     >     >     > ]
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > Hope that helps,
    >     > >     >     >     >     >     >        Chris
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > Am 13.03.20, 17:09 schrieb "Etienne 
Robinet" <[email protected]>:
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     >     Hi all,
    >     > >     >     >     >     >     >     sorry for double-posting, but I 
found the fix. For me the code does not look that 'sexy' now but it works. I do 
not know if I can make it better but for now I will stick to this :) I pushed 
it to the 'eip' branch of my fork.
    >     > >     >     >     >     >     >     Have a nice weekend,
    >     > >     >     >     >     >     >     
    >     > >     >     >     >     >     >     Etienne
    >     > >     >     >     >     >     >     On 2020/03/13 14:48:35, Etienne 
Robinet <[email protected]> wrote: 
    >     > >     >     >     >     >     >     > Hi,
    >     > >     >     >     >     >     >     > Thanks for the advice. I am 
trying to pass the length down the subclasses, but I'm stuck. This does not 
work as it seems:
    >     > >     >     >     >     >     >     > 
https://i.imgur.com/77bbdBN.png CipRRData does not know what 'len' is nor its 
value as it seems.
    >     > >     >     >     >     >     >     > 
    >     > >     >     >     >     >     >     > I wanted to inspire mysefl 
from the CotpPayload, but unfortunately, the first byte of the whole packet is 
a discriminator (command).
    >     > >     >     >     >     >     >     > 
    >     > >     >     >     >     >     >     > Etienne
    >     > >     >     >     >     >     >     > On 2020/03/13 13:52:16, 
Christofer Dutz <[email protected]> wrote: 
    >     > >     >     >     >     >     >     > > Hi Etienne,
    >     > >     >     >     >     >     >     > > 
    >     > >     >     >     >     >     >     > > I think you can solve your 
problem in two ways. 
    >     > >     >     >     >     >     >     > > In all you need to pass 
down the length of the packet in total from the root type (which knows the 
length).
    >     > >     >     >     >     >     >     > > 1) You keep on just reading 
bytes and parse in the protocol logic class (Like in the S7 driver or KNX)
    >     > >     >     >     >     >     >     > > 2) You directly parse 
PlcValues (using "dataIo" types) 
    >     > >     >     >     >     >     >     > > 
    >     > >     >     >     >     >     >     > > I would prefer option 2 but 
1 is simpler. The reason I'm doing 1) in S7 and KNX is that I need to know the 
type from the request to decode in the S7 case and in the KNX case I need to 
know the type from an external source in order to decode it.
    >     > >     >     >     >     >     >     > > 
    >     > >     >     >     >     >     >     > > 
    >     > >     >     >     >     >     >     > > Chris
    >     > >     >     >     >     >     >     > > 
    >     > >     >     >     >     >     >     > > Am 13.03.20, 14:45 schrieb 
"Etienne Robinet" <[email protected]>:
    >     > >     >     >     >     >     >     > > 
    >     > >     >     >     >     >     >     > >     Yes this is exactly 
what I need. If I get the remaining bytes, I can know the element numbers as I 
have their type!
    >     > >     >     >     >     >     >     > >     
    >     > >     >     >     >     >     >     > >     Etienne
    >     > >     >     >     >     >     >     > >     
    >     > >     >     >     >     >     >     > >     On 2020/03/13 13:40:09, 
Julian Feinauer <[email protected]> wrote: 
    >     > >     >     >     >     >     >     > >     > Hey,
    >     > >     >     >     >     >     >     > >     > 
    >     > >     >     >     >     >     >     > >     > there ist he 
possibility to get the remaining size oft he bytes of the message. Does that 
help?
    >     > >     >     >     >     >     >     > >     > Otherwise I misread 
your question.
    >     > >     >     >     >     >     >     > >     > 
    >     > >     >     >     >     >     >     > >     > Julian
    >     > >     >     >     >     >     >     > >     > 
    >     > >     >     >     >     >     >     > >     > Am 13.03.20, 14:37 
schrieb "Etienne Robinet" <[email protected]>:
    >     > >     >     >     >     >     >     > >     > 
    >     > >     >     >     >     >     >     > >     >     Hi Julian,
    >     > >     >     >     >     >     >     > >     >     so how should I 
declare this field in the mspec if I can not get its size?
    >     > >     >     >     >     >     >     > >     >     Thank you,
    >     > >     >     >     >     >     >     > >     >     
    >     > >     >     >     >     >     >     > >     >     Etienne
    >     > >     >     >     >     >     >     > >     >     
    >     > >     >     >     >     >     >     > >     >     On 2020/03/13 
13:35:52, Julian Feinauer <[email protected]> wrote: 
    >     > >     >     >     >     >     >     > >     >     > Hi Etienne,
    >     > >     >     >     >     >     >     > >     >     > 
    >     > >     >     >     >     >     >     > >     >     > first, 
Congratulations on your Progress!
    >     > >     >     >     >     >     >     > >     >     > To you question:
    >     > >     >     >     >     >     >     > >     >     > This is a 
common issue with many protocols.
    >     > >     >     >     >     >     >     > >     >     > We solve that 
in the protocol layer by keeping the request until we get the response (see for 
Example how we did it for S7).
    >     > >     >     >     >     >     >     > >     >     > So you cannot 
solve that in mpsec at compile time but have to decode the byte[] you get with 
the Information from the Request.
    >     > >     >     >     >     >     >     > >     >     > 
    >     > >     >     >     >     >     >     > >     >     > Hope that helps!
    >     > >     >     >     >     >     >     > >     >     > Julian
    >     > >     >     >     >     >     >     > >     >     > 
    >     > >     >     >     >     >     >     > >     >     > Am 13.03.20, 
14:02 schrieb "Etienne Robinet" <[email protected]>:
    >     > >     >     >     >     >     >     > >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     Hi Chris,
    >     > >     >     >     >     >     >     > >     >     >     I have yet 
another question. When sending a request for multiple elements (let's say 10 
elements of an array), you get a response from the PLC with all the data at the 
end of the packet. The problem is, in the request there is the number of 
elements we want, but not in the response. So so the protocol knows how many 
elements there are in the response packet, but not the packet itself. This is 
quite a problem as for the parse, we need to know the length of the 'data' 
array containing the response data (for now it was only depending on the type, 
but I would need type*elements).
    >     > >     >     >     >     >     >     > >     >     >     
    >     > >     >     >     >     >     >     > >     >     >     I tested a 
bit by modifying the generated IO, and 1 way to do it is to get the remaining 
bytes and divide this by the datatype size. I just wanted to ask if someone 
would know how to declare this in the mspec, as I don't want to touch at the 
template. I also thought about having an attribute on the response, but I don't 
know how to put an attribute that won't get parsed/serialized. Hope I am clear 
enough, but this is  a code sample that worked (modifying generated sources):
    >     > >     >     >     >     >     >     > >     >     >     
https://i.imgur.com/Xm6DxEZ.png (notice the error but this code works if I 
write it myself)
    >     > >     >     >     >     >     >     > >     >     >     And here is 
how I put it in the mspec: https://i.imgur.com/Ye1Kl9q.png (you can see the 
number of element is not present)
    >     > >     >     >     >     >     >     > >     >     >     
    >     > >     >     >     >     >     >     > >     >     >     Any help is 
welcome of course! :)
    >     > >     >     >     >     >     >     > >     >     >     Etienne
    >     > >     >     >     >     >     >     > >     >     >     
    >     > >     >     >     >     >     >     > >     >     >     
    >     > >     >     >     >     >     >     > >     >     >     
    >     > >     >     >     >     >     >     > >     >     >     
    >     > >     >     >     >     >     >     > >     >     >     
    >     > >     >     >     >     >     >     > >     >     >     On 
2020/03/12 21:34:12, Christofer Dutz <[email protected]> wrote: 
    >     > >     >     >     >     >     >     > >     >     >     > Hi 
Etienne,
    >     > >     >     >     >     >     >     > >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     > that's 
amazing news :-) ... congratulations :-)
    >     > >     >     >     >     >     >     > >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     > Also had 
a look at your mspec and I think you have done a great job with that. I wasn't 
quite sure about the relation between CipRRData and CipExchange, but your 
solution looks rock-solid.
    >     > >     >     >     >     >     >     > >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     > And now 
reading that you even managed to get something working, that makes me very 
happy.
    >     > >     >     >     >     >     >     > >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     > Tomorrow 
I'll be a little consumed with signing the contract with the KNX foundation but 
I'll try to have a look at your fork.
    >     > >     >     >     >     >     >     > >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     > Thanks 
for your great work :)
    >     > >     >     >     >     >     >     > >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     > Chris
    >     > >     >     >     >     >     >     > >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     > Am 
12.03.20, 17:50 schrieb "Etienne Robinet" <[email protected]>:
    >     > >     >     >     >     >     >     > >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     >     Hi 
all,
    >     > >     >     >     >     >     >     > >     >     >     >     again 
a productive day, I pushed to my branch and the driver support reading, 
multiple reading and the camel component works (in karaf) and takes a List of 
strings. Tested it on a different PLC and it also worked! Next I'm going to 
implement the array readings and then maybe writing (tests needs to be done 
too).
    >     > >     >     >     >     >     >     > >     >     >     >     
    >     > >     >     >     >     >     >     > >     >     >     >     
Etienne
    >     > >     >     >     >     >     >     > >     >     >     >     
    >     > >     >     >     >     >     >     > >     >     >     >     On 
2020/03/12 07:18:32, Etienne Robinet <[email protected]> wrote: 
    >     > >     >     >     >     >     >     > >     >     >     >     > Hi 
Chris,
    >     > >     >     >     >     >     >     > >     >     >     >     > yes 
that's what I thought so I managed to work around like this: 
    >     > >     >     >     >     >     >     > >     >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     >     > 
https://github.com/etiennerobinet/plc4x/blob/eip/protocols/eip/src/main/resources/protocols/eip/eip.mspec
    >     > >     >     >     >     >     >     > >     >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     >     > And 
this works for reading! I managed to make a quick test and read via the tag 
name. Now my question is: can I create sub-types that are also discriminated 
with sub-subtypes? That would allow to create the ReadRequest only, as the 
fields before are mainly constant/implicit.
    >     > >     >     >     >     >     >     > >     >     >     >     > 
Etienne
    >     > >     >     >     >     >     >     > >     >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     >     > On 
2020/03/11 20:24:14, Christofer Dutz <[email protected]> wrote: 
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
Hi Etienne,
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
you are defining the type CipRRData twice ... once as one of the sub-types of 
EipPacket and once as a dedicated discriminated type.
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
Chris
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
PS: I have no idea why I didn't finish writing this email and I just noticed 
when closing everything down ... sorry for the late reply.
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
Am 11.03.20, 09:30 schrieb "Etienne Robinet" <[email protected]>:
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  Hi all,
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  I have a quick question. I've been working on the CIP encapsulation but 
hitting a problem with the mspec design. Here is the error I am facing: 
https://i.imgur.com/iCfh59n.png
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  The problem here is that this CipRRData should also be of type EipPacket. 
When the command of an EipPacket is '0x66' this means SendRRData (for 
Read/Write and Request/Response so I have to discriminate it on the sub level). 
The problem is that after generation, CipRRData implements Message but does not 
extend EipPacket. How should I do it? Here is the mspec:
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  [discriminatedType 'EipPacket'
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [discriminator uint 16 'command']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [implicit      uint 16 'len' 'lengthInBytes - 24']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [simple        uint 32 'sessionHandle']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [simple        uint 32 'status']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [array         uint 8  'senderContext' count '8']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [simple        uint 32 'options']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [typeSwitch 'command'
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              ['0x0065' EipConnectionRequest
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
                  [const  uint    16   'protocolVersion'   '0x01']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
                  [const  uint    16   'flags'             '0x00']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              ['0x0066' EipDisconnectRequest
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              ['0x006F' CipRRData
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
                  [const  uint    32  'EipInterface' '0x00000000']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
                  [const  uint    8   'timeout'   '0x0000']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
          ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  [discriminatedType 'CipRRData'
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [simple         uint        8       'itemNb']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [array          CipItem     'items'    length  'itemNb']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [discriminator  uint        8       'CipService']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [typeSwitch 'CipService'
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
          ['0x52' CipUnconnectedRequest
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              [simple CommandData    'data']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
          ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
          ['0xCC' CipReadResponse
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              [reserved   uint            8   '0x0000']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              [simple     uint            8   'status']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              [simple     uint            8   'extStatus']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              [simple     uint            8    'dataType']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              [array      uint            8   'data'  length  'dataType']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
          ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  [type 'CipItem'
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [simple uint    16  'typeID']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [simple uint    16  'size']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  [discriminatedType 'CommandData'
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [reserved         uint    8   '0x02']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [reserved         uint    8   '0x20']   // 
setRequestPathLogicalClassSegment
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [reserved         uint    8   '0x06']   // set request class path
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [reserved         uint    8   '0x24']   // 
setRequestPathLogicalInstanceSegment
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [reserved         uint    8   '0x01']   // setRequestPathInstance
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [discriminator  uint    8   'CipService']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      [typeSwitch 'CipService'
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
          ['0x4C' CipReadRequest
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              [simple     uint    8   'RequestPathSize']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              [reserved   uint    8   '0x91']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              [array      uint    8   'tag'   length  '(RequestPathSize*2) - 1']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
              [reserved   uint    16  '0x0001']  //itemCount set to 1 for now
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
          ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  [enum int   16   'CIPDataTypeCode' [uint 8  'size']
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      ['0X00C1'   BOOL            ['1']]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      ['0X00CA'   REAL            ['4']]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      ['0X00C4'   DINT            ['4']]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      ['0X00C3'   INT             ['2']]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      ['0X00C2'   SINT            ['1']]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      ['0X02A0'   STRUCTURED      ['88']]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      ['0X02A0'   STRING          ['88']]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      ['0X02A0'   STRING36        ['40']]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
      ['-1'       UNKNOWN         ['-1']]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  ]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  Thanks for any help!
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  Etienne 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  On 2020/03/10 15:18:47, Etienne Robinet <[email protected]> wrote: 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > Hi all,
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > I've managed to implement the EIP Session Register/Unregister (used for 
connected message which is best for high frequency fetching). I will push it to 
my branch and create a document explaining my steps.
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > Next I want to do was to to the CIP encapsulation part for accessing tag by 
their name. The thing is, CIP is (from what I heard) proper to Allen Bradley. 
Should I leave it in the EIP driver or modify and adapt the current AB driver 
later on? For now I will continue on eip.
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > Etienne
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > On 2020/03/10 14:41:42, Cesar Garcia <[email protected]> wrote: 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > Hi,
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > You can document the process step by step, you will surely find 
observation
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > points.
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > I am working with the handwritten S7 driver, but in the future I would
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > support the team in migrate to mspec, so the experience you will gain with
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > the Etheret / IP is very important.
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > Best regards,
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > El mar., 10 mar. 2020 a las 9:17, Christofer Dutz (<
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > [email protected]>) escribió:
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > Hi Etienne,
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > I would strongly suggest you install the Antlr plugn for the IDE you 
use.
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > The problem is that ANTLR seems to gobble up a lot of errors and tries 
to
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > be smart in a lot of cases.
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > Whenever I have problems like this I use the ANTLR visual parser to 
parse
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > a block of mspec (one type at a time) and try to narrow down the cause.
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > Chris
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > Am 10.03.20, 13:31 schrieb "Etienne Robinet" <[email protected]>:
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >     Hi all,
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >     I've been struggling with implementing the EIP driver. I started
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > writing the mspec after creating both a module for the protocol and the 
one
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > from the driver. I copied and adapted the pom(s) from the AB-ETH but 
only
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > the enum is generated.
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >     Here is a link to the forked branch:
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > https://github.com/etiennerobinet/plc4x/tree/eip
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >     I've been studying the EIP/CIP protocol and now I am confident what
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > the packages should contain but I can not figure out how to generate 
this
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > > with the templates. Am I missing something?
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >     Etienne
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > >
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > -- 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > *CEOS Automatización, C.A.*
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > *Ing. César García*
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > *Cel: 0416-681.03.99*
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > *Cel: 0414-760.98.95*
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > *Hotline Técnica SIEMENS: 0800 1005080*
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > *Email: [email protected]
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > <[email protected]>*
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  > 
    >     > >     >     >     >     >     >     > >     >     >     >     > >   
  
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > > 
    >     > >     >     >     >     >     >     > >     >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     >     
    >     > >     >     >     >     >     >     > >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     > 
    >     > >     >     >     >     >     >     > >     >     >     
    >     > >     >     >     >     >     >     > >     >     > 
    >     > >     >     >     >     >     >     > >     >     > 
    >     > >     >     >     >     >     >     > >     >     
    >     > >     >     >     >     >     >     > >     > 
    >     > >     >     >     >     >     >     > >     > 
    >     > >     >     >     >     >     >     > >     
    >     > >     >     >     >     >     >     > > 
    >     > >     >     >     >     >     >     > > 
    >     > >     >     >     >     >     >     > 
    >     > >     >     >     >     >     >     
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     > 
    >     > >     >     >     >     >     
    >     > >     >     >     >     > 
    >     > >     >     >     >     > 
    >     > >     >     >     >     
    >     > >     >     >     > 
    >     > >     >     >     > 
    >     > >     >     >     
    >     > >     >     > 
    >     > >     >     > 
    >     > >     >     
    >     > >     > 
    >     > >     > 
    >     > >     
    >     > > 
    >     > > 
    >     > 
    >     
    > 
    > 
    

Reply via email to