Hello Matthias,
thank you for the response!
I tryied with the latest version of Milo 0.4.1 but I got an error with that:
[main] INFO org.apache.plc4x.java.PlcDriverManager - Instantiating new
PLC Driver Manager with class loader
jdk.internal.loader.ClassLoaders$AppClassLoader@c387f44
[main] INFO org.apache.plc4x.java.PlcDriverManager - Registering
available drivers...
[main] INFO org.apache.plc4x.java.PlcDriverManager - Registering
driver for Protocol opcua (OPC UA (TCP))
[main] INFO org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection
- Configured OpcuaTcpPlcConnection with: host-name 127.0.0.1
[NonceUtilSecureRandom] INFO
org.eclipse.milo.opcua.stack.core.util.NonceUtil - SecureRandom seeded
in 1ms.
[main] INFO org.eclipse.milo.opcua.sdk.client.OpcUaClient - Eclipse
Milo OPC UA Stack version: 0.4.0
[main] INFO org.eclipse.milo.opcua.sdk.client.OpcUaClient - Eclipse
Milo OPC UA Client SDK version: 0.4.0
[main] INFO org.titus.plc4x.OpcReader - Verbindung ist aufgebaut...
[main] INFO org.titus.plc4x.OpcReader - Anfrage gesendet...
[main] ERROR org.titus.plc4x.OpcReader - Konnte keine Verbindung aufbauen
java.util.concurrent.ExecutionException: java.lang.ClassCastException:
class org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId
cannot be cast to class
org.eclipse.milo.opcua.stack.core.types.builtin.NodeId
(org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId and
org.eclipse.milo.opcua.stack.core.types.builtin.NodeId are in unnamed
module of loader 'app')
at
java.base/java.util.concurrent.CompletableFuture.reportGet(CompletableFuture.java:395)
at
java.base/java.util.concurrent.CompletableFuture.get(CompletableFuture.java:2070)
at org.titus.plc4x.OpcReader.main(OpcReader.java:29)
Caused by: java.lang.ClassCastException: class
org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId cannot
be cast to class
org.eclipse.milo.opcua.stack.core.types.builtin.NodeId
(org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId and
org.eclipse.milo.opcua.stack.core.types.builtin.NodeId are in unnamed
module of loader 'app')
at
org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection.encodeFieldItem(OpcuaTcpPlcConnection.java:115)
at
org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection.lambda$read$8(OpcuaTcpPlcConnection.java:404)
at
java.base/java.util.concurrent.CompletableFuture$AsyncSupply.run(CompletableFuture.java:1771)
at
java.base/java.util.concurrent.CompletableFuture$AsyncSupply.exec(CompletableFuture.java:1763)
at
java.base/java.util.concurrent.ForkJoinTask.doExec(ForkJoinTask.java:290)
at
java.base/java.util.concurrent.ForkJoinPool$WorkQueue.topLevelExec(ForkJoinPool.java:1016)
at
java.base/java.util.concurrent.ForkJoinPool.scan(ForkJoinPool.java:1665)
at
java.base/java.util.concurrent.ForkJoinPool.runWorker(ForkJoinPool.java:1598)
at
java.base/java.util.concurrent.ForkJoinWorkerThread.run(ForkJoinWorkerThread.java:177)
After Debugging I found out that it was a Problem with the Version so
I used Milo 0.3.6 and the Problem with the Connection was gone. But
another error appeared:
[main] INFO org.apache.plc4x.java.PlcDriverManager - Instantiating new
PLC Driver Manager with class loader
jdk.internal.loader.ClassLoaders$AppClassLoader@c387f44
[main] INFO org.apache.plc4x.java.PlcDriverManager - Registering
available drivers...
[main] INFO org.apache.plc4x.java.PlcDriverManager - Registering
driver for Protocol opcua (OPC UA (TCP))
[main] INFO org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection
- Configured OpcuaTcpPlcConnection with: host-name 127.0.0.1
[NonceUtilSecureRandom] INFO
org.eclipse.milo.opcua.stack.core.util.NonceUtil - SecureRandom seeded
in 1ms.
Exception in thread "main" java.lang.NoClassDefFoundError:
org/eclipse/milo/opcua/binaryschema/parser/BsdParser
at
org.eclipse.milo.opcua.sdk.client.api.config.OpcUaClientConfig.builder(OpcUaClientConfig.java:96)
at
org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection.connect(OpcuaTcpPlcConnection.java:242)
at
org.apache.plc4x.java.PlcDriverManager.getConnection(PlcDriverManager.java:73)
at org.titus.plc4x.OpcReader.main(OpcReader.java:18)
Caused by: java.lang.ClassNotFoundException:
org.eclipse.milo.opcua.binaryschema.parser.BsdParser
at
java.base/jdk.internal.loader.BuiltinClassLoader.loadClass(BuiltinClassLoader.java:602)
at
java.base/jdk.internal.loader.ClassLoaders$AppClassLoader.loadClass(ClassLoaders.java:178)
at java.base/java.lang.ClassLoader.loadClass(ClassLoader.java:521)
... 4 more
My Code is as follows (but the error is the same with the
ManualPLC4XOpcua Code):
public class OpcReader {
private static final Logger logger =
LoggerFactory.getLogger(OpcReader.class);
public static void main(String[] args) {
try ( OpcuaTcpPlcConnection opcuaConnection
= (OpcuaTcpPlcConnection) new
PlcDriverManager().getConnection("opcua:tcp://localhost:5801/OPC_Simulation_Server?discovery=false"))
{
logger.info("Verbindung ist
aufgebaut...");
PlcReadRequest.Builder
readBuilder = opcuaConnection.readRequestBuilder();
readBuilder.addItem("Menge",
"ns=2;i=4");
PlcReadRequest request =
readBuilder.build();
logger.info("Anfrage gesendet...");
PlcReadResponse response = opcuaConnection.read(request).get();
logger.info("Antwort der Steuerung:");
for (String fieldName :
response.getFieldNames()) {
logger.info("{} -
{}", fieldName, response.getResponseCode(fieldName));
if
(response.getResponseCode(fieldName) == PlcResponseCode.OK) {
logger.info("{} - {}", fieldName, response.getObject(fieldName));
}
}
} catch (Exception e) {
logger.error("Konnte keine
Verbindung aufbauen", e);
}
}
}
As a OPC Server I use a Python tool called FreeOpcUa
(https://github.com/FreeOpcUa/python-opcua) and just simply set up
some variables with:
from opcua import Server
server = Server()
url = "opc.tcp://localhost:5801"
server.set_endpoint(url)
name = "OPC_Simulation_Server"
addspace = server.register_namespace(name)
node = server.get_objects_node()
Param = node.add_object(addspace, "Parameters")
ANr = Param.add_variable(addspace, "Auftragsnummer", 0)
Stk = Param.add_variable(addspace, "Stückzahl", 0)
Menge = Param.add_variable(addspace, "Menge", 0)
ANr.set_writable()
Stk.set_writable()
Menge.set_writable()
server.start()
print("Server started at {}".format(url))
Thank you for your help and advice.
Greets
Titus
Am Do., 30. Apr. 2020 um 23:33 Uhr schrieb Strljic, Matthias Milan
<[email protected]>:
>
> Hello Titus,
>
>
> the driver supports read, write and subscribe. So you should be able to write
> values to an OPC UA server.
>
> If you could provide there some meta data to your issue we can perhaps help
> you with that?
>
> What kind of node type you try to read/write?
>
>
> The ManualPLC4XOpcua test class includes for all request types some small
> examples.
>
> URL to ManualPLC4XOpcua:
> https://github.com/apache/plc4x/blob/rel/0.6/plc4j/drivers/opcua/src/test/java/org/apache/plc4x/java/opcua/ManualPLC4XOpcua.java
>
>
> To achieve the best results you could build the latest version of the 0.6
> branch and use that until we publish the 0.6.1 release candidate.
>
>
> Best regards
>
> Matthias
>
> ________________________________
> Von: Titus Hartmann <[email protected]>
> Gesendet: Donnerstag, 30. April 2020 10:01:27
> An: [email protected]
> Betreff: Re: OPC UA communication
>
> Hello Matthias,
>
> thank you for your response! Is there any Option to get around this so
> that I can read some nodes for test cases?
> The other question that comes to my mind is if there is a write
> methode like the one in the S7 Adapter already implemented? Or is
> there help needed?
>
> I started my program this morning and there was another error present.
> Could you help me out with this aswell?
>
> java.util.concurrent.ExecutionException: java.lang.ClassCastException:
> class org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId
> cannot be cast to class
> org.eclipse.milo.opcua.stack.core.types.builtin.NodeId
> (org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId and
> org.eclipse.milo.opcua.stack.core.types.builtin.NodeId are in unnamed
> module of loader 'app')
> at
> java.base/java.util.concurrent.CompletableFuture.reportGet(CompletableFuture.java:395)
> at
> java.base/java.util.concurrent.CompletableFuture.get(CompletableFuture.java:2070)
> at org.titus.plc4x.OpcReader.main(OpcReader.java:44)
> Caused by: java.lang.ClassCastException: class
> org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId cannot
> be cast to class
> org.eclipse.milo.opcua.stack.core.types.builtin.NodeId
> (org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId and
> org.eclipse.milo.opcua.stack.core.types.builtin.NodeId are in unnamed
> module of loader 'app')
> at
> org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection.encodeFieldItem(OpcuaTcpPlcConnection.java:115)
> at
> org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection.lambda$read$8(OpcuaTcpPlcConnection.java:404)
> at
> java.base/java.util.concurrent.CompletableFuture$AsyncSupply.run(CompletableFuture.java:1771)
> at
> java.base/java.util.concurrent.CompletableFuture$AsyncSupply.exec(CompletableFuture.java:1763)
> at java.base/java.util.concurrent.ForkJoinTask.doExec(ForkJoinTask.java:290)
> at
> java.base/java.util.concurrent.ForkJoinPool$WorkQueue.topLevelExec(ForkJoinPool.java:1016)
> at java.base/java.util.concurrent.ForkJoinPool.scan(ForkJoinPool.java:1665)
> at
> java.base/java.util.concurrent.ForkJoinPool.runWorker(ForkJoinPool.java:1598)
> at
> java.base/java.util.concurrent.ForkJoinWorkerThread.run(ForkJoinWorkerThread.java:177)
>
> Thank you and greets
> Titus
>
> Am Do., 30. Apr. 2020 um 09:35 Uhr schrieb Strljic, Matthias Milan
> <[email protected]>:
> >
> > Hello, Titus,
> >
> > the discovery part is an optional parameter. By default the opc ua driver
> > uses the discovery endpoint of an opc ua server to get the correct endpoint
> > description.
> > If the parameter is set to false, it ignores this discovery result and
> > forces the specified ip + port combination. We had to implement this option
> > because opc ua servers do not always seem to be configured correctly.
> > But you are right, the documentation part is missing there. We will address
> > this soon to avoid these ambiguities.
> >
> >
> > The bug you mentioned is already fixed in the upcoming versions 7.0 and 6.1
> > and should be released soon.
> >
> > Greetings
> > Matthias
> >
> >
> > ________________________________
> > Von: Titus Hartmann <[email protected]>
> > Gesendet: Mittwoch, 29. April 2020 14:57:35
> > An: [email protected]
> > Betreff: OPC UA communication
> >
> > Hello everyone,
> >
> > following the mail addressed to Julian I have a Question regarding the
> > communication between Prosys OPC UA and PLC4X.
> >
> > In the demo Julian used in his Webinar there is this Connection String:
> >
> > "opcua:tcp://10.8.0.2:53530/opcua/SimulationServer?discovery=false&username=tester&password=test1234"
> >
> > I’m wondering what the discovery part does. Can you help me with this?
> > Using this Code the following error appeared:
> >
> > org.apache.plc4x.java.api.exceptions.PlcConnectionException: Unable to
> > discover
> > URL:opc.tcp://192.168.222.27:53530/OPCUA/SimulationServer?discovery=false/discovery
> >
> > at
> > org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection.connect(OpcuaTcpPlcConnection.java:187)
> >
> > at
> > org.apache.plc4x.java.PlcDriverManager.getConnection(PlcDriverManager.java:73)
> >
> > at org.titus.plc4x.OpcReader.main(OpcReader.java:48)
> >
> > After Debugging I noticed that the URL is not correctly separated.
> > Thats why the discovery part is ignored. Not sure why it worked in the
> > demo though.
> >
> > Do you guys have any idea how I could fix this?
> >
> > Thanks and best regards
> >
> > Titus