Hey Matthias,


for sure I can describe my use case.

In my case I want to write data from a middleware into the OPC UA Server
running on my machine.

Reading with PLC4X workes just fine. As a non maven user (just yet) I
needed the following JARs:


plc4j-driver-opcua-0.6.0.jar

netty-channel-fsm-0.4.jar

strict-machine-0.3.jar

slf4j-api-1.7.25.jar

plc4j-api-0.6.0.jar

commons-lang3-3.7.jar

plc4j-protocol-driver-base-0.6.0.jar

netty-all-4.1.43.Final.jar

slf4j-simple-1.7.26.jar

sdk-client-0.3.6.jar

stack-client-0.3.6.jar

stack-core-0.3.6.jar

bsd-parser-core-0.3.6.jar

jaxb-api-2.3.1.jar



As a OPC Server I used the Prosys OPC Simulation Server. As a client to
check values and so on I used UaExpert.



The thing is that I get an ACCESS_DENIED error when I try to write values
even though my AccessLevel and UserAccessLevel are CurrentRead,
CurrentWrite.

When I’m using a freeopcua Client runnning on Python the writing of the
values works just fine. Any idea why?



Thanks for your help.



Greets

Titus


Am Mo., 4. Mai 2020 um 10:13 Uhr schrieb Strljic, Matthias Milan <
[email protected]>:

> Hi Titus,
>
>
> Nice to hear that it was just a small fix required in the setup 😊
>
> Could you describe the problem that you had, to avoid it for up comming
> users?
>
>
> The accessLevel is a security feature of OPC UA which is only configurable
> over the server configuration or with an admin level user.
>
> So for that you have to contact the server admins. Else you could check
> with tools like UAExplorer or something similiar the accessLevel of the
> item.
>
> Because there was a bug in the past where we did a mistake in the write
> configuration which should be fixed.
>
>
> I hope that helps a bit.
>
>
> Best regards
> Matthias
>
> ________________________________
> Von: Titus Hartmann <[email protected]>
> Gesendet: Montag, 4. Mai 2020 08:29:34
> An: [email protected]
> Betreff: Re: OPC UA communication
>
> Hello Matthias,
>
> Looks like it was again just an error with missing JARs. Reading works
> and with writing the access is currently denied. Do you guys have a
> way to change this accessLevel over the API or do I have to do it on
> the server itself?
>
> Thanks!
> Titus
>
> Am Sa., 2. Mai 2020 um 11:28 Uhr schrieb Titus Hartmann
> <[email protected]>:
> >
> > Hello Matthias,
> >
> >
> > thank you for the response!
> >
> >
> > I tryied with the latest version of Milo 0.4.1 but I got an error with
> that:
> >
> >
> > [main] INFO org.apache.plc4x.java.PlcDriverManager - Instantiating new
> > PLC Driver Manager with class loader
> > jdk.internal.loader.ClassLoaders$AppClassLoader@c387f44
> >
> > [main] INFO org.apache.plc4x.java.PlcDriverManager - Registering
> > available drivers...
> >
> > [main] INFO org.apache.plc4x.java.PlcDriverManager - Registering
> > driver for Protocol opcua (OPC UA (TCP))
> >
> > [main] INFO org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection
> > - Configured OpcuaTcpPlcConnection with: host-name 127.0.0.1
> >
> > [NonceUtilSecureRandom] INFO
> > org.eclipse.milo.opcua.stack.core.util.NonceUtil - SecureRandom seeded
> > in 1ms.
> >
> > [main] INFO org.eclipse.milo.opcua.sdk.client.OpcUaClient - Eclipse
> > Milo OPC UA Stack version: 0.4.0
> >
> > [main] INFO org.eclipse.milo.opcua.sdk.client.OpcUaClient - Eclipse
> > Milo OPC UA Client SDK version: 0.4.0
> >
> > [main] INFO org.titus.plc4x.OpcReader - Verbindung ist aufgebaut...
> >
> > [main] INFO org.titus.plc4x.OpcReader - Anfrage gesendet...
> >
> > [main] ERROR org.titus.plc4x.OpcReader - Konnte keine Verbindung aufbauen
> >
> > java.util.concurrent.ExecutionException: java.lang.ClassCastException:
> > class org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId
> > cannot be cast to class
> > org.eclipse.milo.opcua.stack.core.types.builtin.NodeId
> > (org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId and
> > org.eclipse.milo.opcua.stack.core.types.builtin.NodeId are in unnamed
> > module of loader 'app')
> >
> >              at
> >
> java.base/java.util.concurrent.CompletableFuture.reportGet(CompletableFuture.java:395)
> >
> >              at
> >
> java.base/java.util.concurrent.CompletableFuture.get(CompletableFuture.java:2070)
> >
> >              at org.titus.plc4x.OpcReader.main(OpcReader.java:29)
> >
> > Caused by: java.lang.ClassCastException: class
> > org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId cannot
> > be cast to class
> > org.eclipse.milo.opcua.stack.core.types.builtin.NodeId
> > (org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId and
> > org.eclipse.milo.opcua.stack.core.types.builtin.NodeId are in unnamed
> > module of loader 'app')
> >
> >              at
> >
> org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection.encodeFieldItem(OpcuaTcpPlcConnection.java:115)
> >
> >              at
> >
> org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection.lambda$read$8(OpcuaTcpPlcConnection.java:404)
> >
> >              at
> >
> java.base/java.util.concurrent.CompletableFuture$AsyncSupply.run(CompletableFuture.java:1771)
> >
> >              at
> >
> java.base/java.util.concurrent.CompletableFuture$AsyncSupply.exec(CompletableFuture.java:1763)
> >
> >              at
> > java.base/java.util.concurrent.ForkJoinTask.doExec(ForkJoinTask.java:290)
> >
> >              at
> >
> java.base/java.util.concurrent.ForkJoinPool$WorkQueue.topLevelExec(ForkJoinPool.java:1016)
> >
> >              at
> > java.base/java.util.concurrent.ForkJoinPool.scan(ForkJoinPool.java:1665)
> >
> >              at
> >
> java.base/java.util.concurrent.ForkJoinPool.runWorker(ForkJoinPool.java:1598)
> >
> >              at
> >
> java.base/java.util.concurrent.ForkJoinWorkerThread.run(ForkJoinWorkerThread.java:177)
> >
> >
> >
> > After Debugging I found out that it was a Problem with the Version so
> > I used Milo 0.3.6 and the Problem with the Connection was gone. But
> > another error appeared:
> >
> >
> > [main] INFO org.apache.plc4x.java.PlcDriverManager - Instantiating new
> > PLC Driver Manager with class loader
> > jdk.internal.loader.ClassLoaders$AppClassLoader@c387f44
> >
> > [main] INFO org.apache.plc4x.java.PlcDriverManager - Registering
> > available drivers...
> >
> > [main] INFO org.apache.plc4x.java.PlcDriverManager - Registering
> > driver for Protocol opcua (OPC UA (TCP))
> >
> > [main] INFO org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection
> > - Configured OpcuaTcpPlcConnection with: host-name 127.0.0.1
> >
> > [NonceUtilSecureRandom] INFO
> > org.eclipse.milo.opcua.stack.core.util.NonceUtil - SecureRandom seeded
> > in 1ms.
> >
> > Exception in thread "main" java.lang.NoClassDefFoundError:
> > org/eclipse/milo/opcua/binaryschema/parser/BsdParser
> >
> >              at
> >
> org.eclipse.milo.opcua.sdk.client.api.config.OpcUaClientConfig.builder(OpcUaClientConfig.java:96)
> >
> >              at
> >
> org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection.connect(OpcuaTcpPlcConnection.java:242)
> >
> >              at
> >
> org.apache.plc4x.java.PlcDriverManager.getConnection(PlcDriverManager.java:73)
> >
> >              at org.titus.plc4x.OpcReader.main(OpcReader.java:18)
> >
> > Caused by: java.lang.ClassNotFoundException:
> > org.eclipse.milo.opcua.binaryschema.parser.BsdParser
> >
> >              at
> >
> java.base/jdk.internal.loader.BuiltinClassLoader.loadClass(BuiltinClassLoader.java:602)
> >
> >              at
> >
> java.base/jdk.internal.loader.ClassLoaders$AppClassLoader.loadClass(ClassLoaders.java:178)
> >
> >              at
> java.base/java.lang.ClassLoader.loadClass(ClassLoader.java:521)
> >
> >              ... 4 more
> >
> >
> >
> > My Code is as follows (but the error is the same with the
> > ManualPLC4XOpcua Code):
> >
> >
> > public class OpcReader {
> >
> >              private static final Logger logger =
> > LoggerFactory.getLogger(OpcReader.class);
> >
> >              public static void main(String[] args) {
> >
> >                            try ( OpcuaTcpPlcConnection opcuaConnection
> > = (OpcuaTcpPlcConnection) new
> >
> PlcDriverManager().getConnection("opcua:tcp://localhost:5801/OPC_Simulation_Server?discovery=false"))
> > {
> >
> >                                         logger.info("Verbindung ist
> > aufgebaut...");
> >
> >                                         PlcReadRequest.Builder
> > readBuilder = opcuaConnection.readRequestBuilder();
> >
> >                                         readBuilder.addItem("Menge",
> > "ns=2;i=4");
> >
> >
> >                                         PlcReadRequest request =
> > readBuilder.build();
> >
> >                                         logger.info("Anfrage
> gesendet...");
> >
> >             PlcReadResponse response =
> opcuaConnection.read(request).get();
> >
> >                                         logger.info("Antwort der
> Steuerung:");
> >
> >                                         for (String fieldName :
> > response.getFieldNames()) {
> >
> >                                                      logger.info("{} -
> > {}", fieldName, response.getResponseCode(fieldName));
> >
> >                                                      if
> > (response.getResponseCode(fieldName) == PlcResponseCode.OK) {
> >
> >
> > logger.info("{} - {}", fieldName, response.getObject(fieldName));
> >
> >                                                      }
> >
> >                                         }
> >
> >                            } catch (Exception e) {
> >
> >                                         logger.error("Konnte keine
> > Verbindung aufbauen", e);
> >
> >                            }
> >
> >              }
> >
> > }
> >
> >
> >
> > As a OPC Server I use a Python tool called FreeOpcUa
> > (https://github.com/FreeOpcUa/python-opcua) and just simply set up
> > some variables with:
> >
> >
> > from opcua import Server
> >
> > server = Server()
> >
> > url = "opc.tcp://localhost:5801"
> >
> > server.set_endpoint(url)
> >
> > name = "OPC_Simulation_Server"
> >
> > addspace = server.register_namespace(name)
> > node = server.get_objects_node()
> > Param = node.add_object(addspace, "Parameters")
> > ANr = Param.add_variable(addspace, "Auftragsnummer", 0)
> > Stk = Param.add_variable(addspace, "Stückzahl", 0)
> > Menge = Param.add_variable(addspace, "Menge", 0)
> > ANr.set_writable()
> > Stk.set_writable()
> > Menge.set_writable()
> > server.start()
> >
> > print("Server started at {}".format(url))
> >
> >
> > Thank you for your help and advice.
> >
> > Greets
> >
> > Titus
> >
> > Am Do., 30. Apr. 2020 um 23:33 Uhr schrieb Strljic, Matthias Milan
> > <[email protected]>:
> > >
> > > Hello Titus,
> > >
> > >
> > > the driver supports read, write and subscribe. So you should be able
> to write values to an OPC UA server.
> > >
> > > If you could provide there some meta data to your issue we can perhaps
> help you with that?
> > >
> > > What kind of node type you try to read/write?
> > >
> > >
> > > The ManualPLC4XOpcua test class includes for all request types some
> small examples.
> > >
> > > URL to ManualPLC4XOpcua:
> https://github.com/apache/plc4x/blob/rel/0.6/plc4j/drivers/opcua/src/test/java/org/apache/plc4x/java/opcua/ManualPLC4XOpcua.java
> > >
> > >
> > > To achieve the best results you could build the latest version of the
> 0.6 branch and use that until we publish the 0.6.1 release candidate.
> > >
> > >
> > > Best regards
> > >
> > > Matthias
> > >
> > > ________________________________
> > > Von: Titus Hartmann <[email protected]>
> > > Gesendet: Donnerstag, 30. April 2020 10:01:27
> > > An: [email protected]
> > > Betreff: Re: OPC UA communication
> > >
> > > Hello Matthias,
> > >
> > > thank you for your response! Is there any Option to get around this so
> > > that I can read some nodes for test cases?
> > > The other question that comes to my mind is if there is a write
> > > methode like the one in the S7 Adapter already implemented? Or is
> > > there help needed?
> > >
> > > I started my program this morning and there was another error present.
> > > Could you help me out with this aswell?
> > >
> > > java.util.concurrent.ExecutionException: java.lang.ClassCastException:
> > > class org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId
> > > cannot be cast to class
> > > org.eclipse.milo.opcua.stack.core.types.builtin.NodeId
> > > (org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId and
> > > org.eclipse.milo.opcua.stack.core.types.builtin.NodeId are in unnamed
> > > module of loader 'app')
> > >  at
> java.base/java.util.concurrent.CompletableFuture.reportGet(CompletableFuture.java:395)
> > >  at
> java.base/java.util.concurrent.CompletableFuture.get(CompletableFuture.java:2070)
> > >  at org.titus.plc4x.OpcReader.main(OpcReader.java:44)
> > > Caused by: java.lang.ClassCastException: class
> > > org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId cannot
> > > be cast to class
> > > org.eclipse.milo.opcua.stack.core.types.builtin.NodeId
> > > (org.eclipse.milo.opcua.stack.core.types.builtin.ExpandedNodeId and
> > > org.eclipse.milo.opcua.stack.core.types.builtin.NodeId are in unnamed
> > > module of loader 'app')
> > >  at
> org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection.encodeFieldItem(OpcuaTcpPlcConnection.java:115)
> > >  at
> org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection.lambda$read$8(OpcuaTcpPlcConnection.java:404)
> > >  at
> java.base/java.util.concurrent.CompletableFuture$AsyncSupply.run(CompletableFuture.java:1771)
> > >  at
> java.base/java.util.concurrent.CompletableFuture$AsyncSupply.exec(CompletableFuture.java:1763)
> > >  at
> java.base/java.util.concurrent.ForkJoinTask.doExec(ForkJoinTask.java:290)
> > >  at
> java.base/java.util.concurrent.ForkJoinPool$WorkQueue.topLevelExec(ForkJoinPool.java:1016)
> > >  at
> java.base/java.util.concurrent.ForkJoinPool.scan(ForkJoinPool.java:1665)
> > >  at
> java.base/java.util.concurrent.ForkJoinPool.runWorker(ForkJoinPool.java:1598)
> > >  at
> java.base/java.util.concurrent.ForkJoinWorkerThread.run(ForkJoinWorkerThread.java:177)
> > >
> > > Thank you and greets
> > > Titus
> > >
> > > Am Do., 30. Apr. 2020 um 09:35 Uhr schrieb Strljic, Matthias Milan
> > > <[email protected]>:
> > > >
> > > > Hello, Titus,
> > > >
> > > > the discovery part is an optional parameter. By default the opc ua
> driver uses the discovery endpoint of an opc ua server to get the correct
> endpoint description.
> > > > If the parameter is set to false, it ignores this discovery result
> and forces the specified ip + port combination. We had to implement this
> option because opc ua servers do not always seem to be configured correctly.
> > > > But you are right, the documentation part is missing there. We will
> address this soon to avoid these ambiguities.
> > > >
> > > >
> > > > The bug you mentioned is already fixed in the upcoming versions 7.0
> and 6.1 and should be released soon.
> > > >
> > > > Greetings
> > > > Matthias
> > > >
> > > >
> > > > ________________________________
> > > > Von: Titus Hartmann <[email protected]>
> > > > Gesendet: Mittwoch, 29. April 2020 14:57:35
> > > > An: [email protected]
> > > > Betreff: OPC UA communication
> > > >
> > > > Hello everyone,
> > > >
> > > > following the mail addressed to Julian I have a Question regarding
> the
> > > > communication between Prosys OPC UA and PLC4X.
> > > >
> > > > In the demo Julian used in his Webinar there is this Connection
> String:
> > > >
> > > > "opcua:tcp://
> 10.8.0.2:53530/opcua/SimulationServer?discovery=false&username=tester&password=test1234
> "
> > > >
> > > > I’m wondering what the discovery part does. Can you help me with
> this?
> > > > Using this Code the following error appeared:
> > > >
> > > > org.apache.plc4x.java.api.exceptions.PlcConnectionException: Unable
> to
> > > > discover URL:opc.tcp://
> 192.168.222.27:53530/OPCUA/SimulationServer?discovery=false/discovery
> > > >
> > > >        at
> org.apache.plc4x.java.opcua.connection.OpcuaTcpPlcConnection.connect(OpcuaTcpPlcConnection.java:187)
> > > >
> > > >        at
> org.apache.plc4x.java.PlcDriverManager.getConnection(PlcDriverManager.java:73)
> > > >
> > > >        at org.titus.plc4x.OpcReader.main(OpcReader.java:48)
> > > >
> > > > After Debugging I noticed that the URL is not correctly separated.
> > > > Thats why the discovery part is ignored. Not sure why it worked in
> the
> > > > demo though.
> > > >
> > > > Do you guys have any idea how I could fix this?
> > > >
> > > > Thanks and best regards
> > > >
> > > > Titus
>

Reply via email to